SailNet Community - View Single Post - Battery Fuse Sizing - How, What...?
View Single Post
post #12 of Old 09-12-2011
btrayfors
Senior Member
 
Join Date: Aug 2006
Location: Arlington, VA
Posts: 1,853
Thanks: 0
Thanked 11 Times in 9 Posts
Rep Power: 10
   
Quote:
Originally Posted by Maine Sail View Post
80%..? Jon A. at ABYC says, and we've specifically discussed this, the ampacity chart already accommodates for ANL, Class T etc. and MRBF is really quite similar to an ANL.
Not really. ANL fuses are unlike any other CPDs, in that they blow at a much higher than nominal rating, whereas most other fuses and breakers blow at about 130% of their rating.

ANL blowpoints can exceed their ratings by 140% to as much as 266%. A 100A ANL won't blow until current reaches 175A or more for 500 seconds -- over 8 minutes!

The ampacity tables cannot take the differences between CPDs into account; you must do that yourself, or find a table in which the specific CPD is referenced.

I believe that MRBFs are like most other fuses found in the marine environment -- relatively fast blowing at 130% of their nominal rating. ANLs are very different.

Here are the curves for the MRBFs: http://bluesea.com/productline/specs/379#td

Bill

Last edited by btrayfors; 09-12-2011 at 11:55 PM.
btrayfors is offline  
Quote Share with Facebook
 
 
For the best viewing experience please update your browser to Google Chrome