SailNet Community - View Single Post - Battery Fuse Sizing - How, What...?
View Single Post
  #14  
Old 09-13-2011
btrayfors btrayfors is offline
Senior Member
 
Join Date: Aug 2006
Location: Arlington, VA
Posts: 1,807
Thanks: 0
Thanked 4 Times in 4 Posts
Rep Power: 9
btrayfors will become famous soon enough btrayfors will become famous soon enough
Well, yes and no. Although we may be splitting hairs a bit here, please read the following statement from Blue Sea Systems regarding selection of their ANL fuses (bolding mine):

"Because ANL fuses behave differently than all other circuit protection devices, that is, their blow point value ranges from 140 to 266% of nominal value, the 80% rule doesn't work. It is necessary to use a different procedure to select a suitable ANL fuse. To choose a suitable ANL fuse, refer to the ANL Fuse Blow Point table above. According to the table, a 100A ANL fuse has a blow point of 175A. Therefore, a 100A ANL provides suitable protection for the 4 gauge AWG circuit in this example."

This is particularly relevant to the smaller ANL sizes, where the blowpoint -- after 8 minutes -- can be as much as 266% of the nominal rating.

Bill
Reply With Quote Share with Facebook