You cant connect the outputs of two portable generators together and expect them to syncronise.

It is essential to disconnect the mains as well.

If you need more capacity, either get a bigger generator or split the loads running half the load on one generator and the other half on a different generator.

It does take more generator capacity to start some electric motors than just the current to run the motor.