Here's some advice for those with solar controllers that have auto equalize...


As for GEL batteries (most are Sonnenschein or Deka/East Penn) absorption should be about 14.1V. Deka has recently upped this "allowable" voltage on their GEL batteries but when I see properly charged GEL batteries going 8 to 12 years I have to assume that they really like 14.1V and the people who invented the technology, Sonnenschein, knew what they were talking about when they advised 14.1V...

My concern with this new Deka charging voltage allowance is that is to "accommodate" potential buyers with "dumb" chargers and not in the best interest of longevity, which is where GEL's really win..

On your float voltage gels actually float (Sonnenschein & Deka) at higher than one would assume. They like to be floated at 13.6V to 13.8V with 13.8V being preferred...

I would highly recommend the IPN ProRemote especially with GEL or AGM batteries...