GFI outlets problem on Beneteau 40. Help?

In the cabin, I have two GFI protected AC outlets .. 20 amps, Hubbel. Both suddenly show a flashing red LED and leaflet says "lost its GFIC protection, replace immediately". Boat is 2009.
I have power at both outlets (separate circuits) and if I push test button, power goes off, if I push reset, power comes on. This to me seems to say it's working. At least, many other GFIs seem only to have this check and no red flashing light. Are they shot? The marina did have a power failure recently, could that "break" them ... thought they would just flip off with any problem?
Any ideas? If needed can I buy new GFIs from hardware store or is there something special (except price) about going to marine store?
Thanks, JohnB40
JohnB40 is offline  
Quote Quick Reply Share with Facebook
Sponsored Links
Advertisement
 
post #2 of 5 Old 11-30-2011
Freedom 39
 
FarCry's Avatar
 
Join Date: Apr 2007
Location: St Thomas USVI
Posts: 1,062
Thanks: 0
Thanked 30 Times in 28 Posts
Rep Power: 9
 
I wonder if you have lost the ground to your boat that should be coming in on your shore power cord. To have both fail at the same time seems like an odd coincidence. The test button is an internal device test that is really just making contact between the neutral and ground.

Do you have an inverter and if so do your GFIs still flash when that is operating and the boat is unplugged?

To further investigate I would make sure there is nothing plugged in to any outlets including battery chargers, rechargable lights etc.

Then, if you have a tester, or can get one, I would confirm that the ground is still good to the boat. If that is fine then the GFI's should be no different than one at the hardware store. Generally, cheaper GFIs are much more apt to nusance tripping than the more expensive (sophisticated) ones like Hubbel. Good luck. I'd be curious to hear what you find.
FarCry is online now  
Quote Quick Reply Share with Facebook
post #3 of 5 Old 12-03-2011
Senior Member
 
Join Date: Oct 2011
Location: Nanaimo B.C.
Posts: 2,604
Thanks: 3
Thanked 63 Times in 63 Posts
Rep Power: 4
 
Could be a problem with GFIs sharing the same white wire from the source.
Capt Len is offline  
Quote Quick Reply Share with Facebook
post #4 of 5 Old 12-04-2011
Old as Dirt!
 
svHyLyte's Avatar
 
Join Date: Nov 2008
Location: Tampa Bay Area
Posts: 2,937
Thanks: 15
Thanked 130 Times in 123 Posts
Rep Power: 7
 
Quote:
Originally Posted by JohnB40 View Post
In the cabin, I have two GFI protected AC outlets .. 20 amps, Hubbel. Both suddenly show a flashing red LED and leaflet says "lost its GFIC protection, replace immediately". Boat is 2009.
I have power at both outlets (separate circuits) and if I push test button, power goes off, if I push reset, power comes on. This to me seems to say it's working. At least, many other GFIs seem only to have this check and no red flashing light. Are they shot? The marina did have a power failure recently, could that "break" them ... thought they would just flip off with any problem?
Any ideas? If needed can I buy new GFIs from hardware store or is there something special (except price) about going to marine store?
Thanks, JohnB40
John,

Based upon a (admittedly superficial) review of the Hubble literature, it seems that its GFIC units have internal test circuitry that evaluates a unit's ability to break a connection soon enough, and at a low enough amperage, to avoid injury or damage in the even of a short. If the unit test fails, the Red LED Illuminates indicating that the unit needs be replaced tho' it may continue to work in extremis. I am not an electrical guy but I have reasonably good faith in the engineers that design this type of equipment and would trust their judgment in the build. The environment on a yacht is quite different--and more harsh--than that in a house or other building and equipment, particularly electrics suffers accordingly. In the same situation I would replace one of the units with the same type (and ensure the connections were thoroughly) and see if the error LED illuminates. If not, the units do need replacing. If not, there is something else askew and you have a spare (or can simple return the unneeded unit). A electrical equipment--contractors supply--outlet is more likely to carry Hubble units than a Lowes/Home Depot or other general hardware store.

FWIW...

"It is not so much for its beauty that the sea makes a claim upon men's hearts, as for that subtle something, that quality of air, that emanation from the waves, that so wonderfully renews a weary spirit."
svHyLyte is offline  
Quote Quick Reply Share with Facebook
post #5 of 5 Old 12-06-2011 Thread Starter
Junior Member
 
Join Date: Mar 2011
Posts: 19
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 0
 
Thanks to all. I still seem to have ground connection to these circuits fed from marina A.C. For each receptacle: test light in neutral and line gives light. In line and ground gives light. In neutral and ground I get no light. I'm no electrician (got the method from YouTube!!) but think that shows receptacle works but the GFI function is no longer. Was at another marina last few days ... plugged in and ran heater etc just fine but lights still flashed so it's not my current marina's problem.
I was at Running Room last week and heard one runner say he was once electrical contractor. Asked him about this. His view ... a power surge after the power failure would have cooked these GFIs.
Good idea to buy one and try it. I'm in B.C. and don't always get the same variety of bits in Canada as found in the U.S. but I guess can always mail order. I've asked many sailing friends and they haven't seen such a fancy GFI here .. the Beneteau was made in Marion S.C.
JohnB40 is offline  
Quote Quick Reply Share with Facebook
Reply

Quick Reply
Message:
Options

By choosing to post the reply above you agree to the rules you agreed to when joining Sailnet.
Click Here to view those rules.

Register Now



In order to be able to post messages on the SailNet Community forums, you must first register.
Please enter your desired user name, your email address and other required details in the form below.
Please note: After entering 3 characters a list of Usernames already in use will appear and the list will disappear once a valid Username is entered.


User Name:
Password
Please enter a password for your user account. Note that passwords are case-sensitive.

Password:


Confirm Password:
Email Address
Please enter a valid email address for yourself.

Email Address:
OR

Log-in









Human Verification

In order to verify that you are a human and not a spam bot, please enter the answer into the following box below based on the instructions contained in the graphic.




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Show Printable Version Show Printable Version
Email this Page Email this Page



Similar Threads
Thread Thread Starter Forum Replies Last Post
12V DC two pin outlets bobdugan Pacific Seacraft 9 06-01-2011 06:56 PM
GFCI Outlets brokesailor Gear & Maintenance 2 04-09-2011 04:52 PM
where to shop for elect. outlets/boxes ptsbug Electrical Systems 2 06-24-2010 02:33 PM
Why not a Beneteau? Pattyh Boat Review and Purchase Forum 169 04-14-2009 02:43 PM
Peters plc rebrand outlets @ Sea Dreamer NewsReader News Feeds 0 04-14-2006 04:15 AM

Posting Rules  
You may post new threads
You may post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

 
For the best viewing experience please update your browser to Google Chrome