Tips for generator diagnosis?

I have a Mase 4001 with 421 hrs / 5 years old. Starter was replaced 5 months ago. It was running fine until this past weekend when 2 minutes after startup it quit with an E-82 message - temperature too high. Checked input water flow before and after the strainer - ok. Checked oil - ok. Tried it again, same result. Let it "rest" overnight and now it won't give any response to starter at all - seems like an internal fuse went out? Any ideas/recommendations ? Thanks
lajimo is offline  
Quote Quick Reply Share with Facebook
Sponsored Links
Advertisement
 
post #2 of 5 Old 07-22-2012
Best Looking MALE Mod
 
Cruisingdad's Avatar
 
Join Date: Jul 2006
Location: Washington State
Posts: 9,917
Thanks: 3
Thanked 124 Times in 57 Posts
Rep Power: 10
     
Re: Tips for generator diagnosis?

Sounds like a sending unit to me. Have u tried bypassing them? Generally this is done by shorting out the connection. For the smarter generators, which run through computers, if they do not see voltage through the temp or oil pressure su within a certain period of time, they shut down. The temp unit maybe turned on with voltage, incidentally, cant remember. If the temp su has failed, it wont bother starting. That is my first guess.

Brian

Sailnet Moderator



1987 Tayana Vancouver 42, Credendo Vides, (Mom and Pops boat, F/T Mobile Live Aboards in Puget Sound)

My Website:
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


Follow My Blog at:
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


Follow me on Facebook:

To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
Cruisingdad is offline  
Quote Quick Reply Share with Facebook
post #3 of 5 Old 07-22-2012 Thread Starter
Senior Member
 
lajimo's Avatar
 
Join Date: Sep 2011
Posts: 187
Thanks: 0
Thanked 1 Time in 1 Post
Rep Power: 4
 
Tips for generator diagnosis?

Good idea -thanks
lajimo is offline  
Quote Quick Reply Share with Facebook
post #4 of 5 Old 07-22-2012
Senior Member
 
Join Date: Feb 2010
Location: Narragansett Bay
Posts: 11,121
Thanks: 46
Thanked 229 Times in 214 Posts
Rep Power: 7
   
Re: Tips for generator diagnosis?

I have an 8k Mase and, once in a while, I need to kill all power to it to let the brains reset or it thinks one of the sensors is showing a fault. Oil and/or temp. Quick reset and she's good to go. Happens about once per year.


To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.

Jeanneau 54DS

In the harsh marine environment, something is always in need of repair. Margaritas fix everything.
Minnewaska is offline  
Quote Quick Reply Share with Facebook
post #5 of 5 Old 07-22-2012 Thread Starter
Senior Member
 
lajimo's Avatar
 
Join Date: Sep 2011
Posts: 187
Thanks: 0
Thanked 1 Time in 1 Post
Rep Power: 4
 
Tips for generator diagnosis?

That's interesting - i will give that a try.
lajimo is offline  
Quote Quick Reply Share with Facebook
Reply

Quick Reply
Message:
Options

By choosing to post the reply above you agree to the rules you agreed to when joining Sailnet.
Click Here to view those rules.

Register Now



In order to be able to post messages on the SailNet Community forums, you must first register.
Please enter your desired user name, your email address and other required details in the form below.
Please note: After entering 3 characters a list of Usernames already in use will appear and the list will disappear once a valid Username is entered.


User Name:
Password
Please enter a password for your user account. Note that passwords are case-sensitive.

Password:


Confirm Password:
Email Address
Please enter a valid email address for yourself.

Email Address:
OR

Log-in









Human Verification

In order to verify that you are a human and not a spam bot, please enter the answer into the following box below based on the instructions contained in the graphic.




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Show Printable Version Show Printable Version
Email this Page Email this Page



Similar Threads
Thread Thread Starter Forum Replies Last Post
Best generator prroots Electrical Systems 12 01-17-2012 11:52 AM
Another Exhaust Smoke Diagnosis DrB Diesel 1 07-06-2010 09:46 AM
Tranny smoking, then slipping - diagnosis process? Pub911 Gear & Maintenance 7 12-02-2008 10:05 PM
Help costing a generator and lots of generator questions... labatt Gear & Maintenance 10 10-16-2008 01:01 AM

Posting Rules  
You may post new threads
You may post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On
Trackbacks are On
Pingbacks are On
Refbacks are On

 
For the best viewing experience please update your browser to Google Chrome