  #1  
Old 09-29-2013
GrahamO's Avatar
Senior Member
 
Join Date: Apr 2012
Location: Portsmouth NH
Posts: 180
Thanks: 5
Thanked 0 Times in 0 Posts
Rep Power: 3
GrahamO is on a distinguished road
Refrigerator off main breaker?

I am just installing a new fridge system. The old one is tied to the main breaker but I am considering going direct from the battery through its own breaker so we could leave it on with the rest of the boat off. Is this OK?

It is for long term cruising and we have a very well insulated (4 1/2"+) refrigerator and 400w of solar.

Advice appreciated as always.

Thanks

Graham
__________________
Graham and Janaki
Bristol 38.8
Leela
Reply With Quote Share with Facebook
  #2  
Old 09-29-2013
Senior Member
 
Join Date: Feb 2010
Location: Narragansett Bay
Posts: 8,267
Thanks: 6
Thanked 89 Times in 86 Posts
Rep Power: 6
Minnewaska will become famous soon enough Minnewaska will become famous soon enough
Re: Refrigerator off main breaker?

You should have a main breaker that feeds all the sub breakers, for which one could be dedicated to the fridge. Everything else should go through other sub breakers, so that anything can be isolated, but everything can be killed by the one master in the event of an electrical fire.
olson34 and rikhall like this.
__________________

To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.

Jeanneau 54DS

In the harsh marine environment, something is always in need of repair. Margaritas fix everything.
Reply With Quote Share with Facebook
The Following User Says Thank You to Minnewaska For This Useful Post:
Maine Sail (09-29-2013)
  #3  
Old 09-29-2013
deniseO30's Avatar
Move over Joan Rivers!
 
Join Date: Nov 2006
Location: Bristol pa
Posts: 5,480
Thanks: 50
Thanked 55 Times in 47 Posts
Rep Power: 9
deniseO30 will become famous soon enough deniseO30 will become famous soon enough
Re: Refrigerator off main breaker?

Need, more information! Guessing it's only 5 amps but more importantly; use the right size wire!
__________________
Denise, Bristol PA, Oday 30. On Tidal Delaware River, Anchor Yacht Club. New Website!
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.

my current "project"!
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
Reply With Quote Share with Facebook
  #4  
Old 09-29-2013
mitiempo's Avatar
Senior Member
 
Join Date: Sep 2008
Location: Victoria B.C. Canada
Posts: 6,776
Thanks: 0
Thanked 52 Times in 43 Posts
Rep Power: 6
mitiempo will become famous soon enough
Re: Refrigerator off main breaker?

This is DC so a main breaker is not needed - the house bank main fuse takes care of that before feeding the DC panel. It is common to have a few "always on" circuits, bilge pump for one and the refrigeration can also be one. These are best fed from a sub panel that is not main switch dependent. A small panel or a fuse block works well. The feed wire to this panel or fuse block should be appropriately fused for the wire size leading to it. If desired a switch can be installed in this wire so total isolation is possible.
__________________
Brian
Living aboard in Victoria Harbour
Reply With Quote Share with Facebook
  #5  
Old 09-29-2013
GrahamO's Avatar
Senior Member
 
Join Date: Apr 2012
Location: Portsmouth NH
Posts: 180
Thanks: 5
Thanked 0 Times in 0 Posts
Rep Power: 3
GrahamO is on a distinguished road
Refrigerator off main breaker?

Thanks guys,
I am planning battery to 30amp fuse to 30amp+ switch to refrigerator compressor. The wiring is all oversized as the old fridge was a monster. New one is a Seafrost BDXP air/water.

Graham
__________________
Graham and Janaki
Bristol 38.8
Leela
Reply With Quote Share with Facebook
  #6  
Old 09-29-2013
Senior Member
 
Join Date: Feb 2010
Location: Narragansett Bay
Posts: 8,267
Thanks: 6
Thanked 89 Times in 86 Posts
Rep Power: 6
Minnewaska will become famous soon enough Minnewaska will become famous soon enough
Re: Refrigerator off main breaker?

Quote:
Originally Posted by mitiempo View Post
This is DC so a main breaker is not needed......
Not sure what you mean by not needed. If you mean that separate breakers are not absolutely necessary to safely protect a circuit, I agree.

However, in the event of smelling an electrical fire (the most common form of boat fire), wouldn't you want one master switch to kill it all? In addition, if you're up on the hard or away or just need to kill all parasitic loads, a master is very helpful. That may not be a breaker, but often goes through a kill switch of some kind.
__________________

To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.

Jeanneau 54DS

In the harsh marine environment, something is always in need of repair. Margaritas fix everything.
Reply With Quote Share with Facebook
  #7  
Old 09-29-2013
deniseO30's Avatar
Move over Joan Rivers!
 
Join Date: Nov 2006
Location: Bristol pa
Posts: 5,480
Thanks: 50
Thanked 55 Times in 47 Posts
Rep Power: 9
deniseO30 will become famous soon enough deniseO30 will become famous soon enough
Re: Refrigerator off main breaker?

Size the breaker per unit specs.. 15 amp.. guessing again..

why is needed information always a secret with people asking for advice?
__________________
Denise, Bristol PA, Oday 30. On Tidal Delaware River, Anchor Yacht Club. New Website!
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.

my current "project"!
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
Reply With Quote Share with Facebook
  #8  
Old 09-29-2013
mitiempo's Avatar
Senior Member
 
Join Date: Sep 2008
Location: Victoria B.C. Canada
Posts: 6,776
Thanks: 0
Thanked 52 Times in 43 Posts
Rep Power: 6
mitiempo will become famous soon enough
Re: Refrigerator off main breaker?

Quote:
Originally Posted by Minnewaska View Post
Not sure what you mean by not needed. If you mean that separate breakers are not absolutely necessary to safely protect a circuit, I agree.

However, in the event of smelling an electrical fire (the most common form of boat fire), wouldn't you want one master switch to kill it all? In addition, if you're up on the hard or away or just need to kill all parasitic loads, a master is very helpful. That may not be a breaker, but often goes through a kill switch of some kind.
A main breaker is not needed because the house bank should be fused within 7" of the positive post. That fuse will protect the wire to the main switch and from there to the main DC panel, where each circuit has a breaker or fuse which it must have. Whenever the wire size drops a new fuse is required if the main fuse is below the ampacity of the smaller wire.

As I posted a sub panel or fuse block is often used for "always on circuits" like the bilge pump or refrigeration. I also said a switch can be installed to isolate the sub panel or fuse block if desired. It is a good idea but I rarely see it.
__________________
Brian
Living aboard in Victoria Harbour
Reply With Quote Share with Facebook
  #9  
Old 09-30-2013
Bene505's Avatar
Glad I found Sailnet
 
Join Date: Jul 2008
Posts: 3,448
Thanks: 3
Thanked 34 Times in 33 Posts
Rep Power: 7
Bene505 will become famous soon enough Bene505 will become famous soon enough
Re: Refrigerator off main breaker?

We use a dedicated fuse for the fridge, wired directly to the battery. Fuses cause less voltage drop than circuit breakers. Our fridge is always on.

Actually, our compressor is well aft, far from the house bank and right near the shore power charger. I use the (now disconnected) shore power charger's wire. It's 6 gauge. Then I have the fridge fuse coming off that, to a short-ish 14 or 16 gauge wire. 5 amps load. Seafrost says to make sure the compressor gets good power.

Regards,
Brad
__________________
Posts you might like:
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
. .
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
. .
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
. .
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
Reply With Quote Share with Facebook
  #10  
Old 09-30-2013
GrahamO's Avatar
Senior Member
 
Join Date: Apr 2012
Location: Portsmouth NH
Posts: 180
Thanks: 5
Thanked 0 Times in 0 Posts
Rep Power: 3
GrahamO is on a distinguished road
Thanks Brad,
Do you have a switch that allows you to isolate the refrigerator?

Graham

Quote:
Originally Posted by Bene505 View Post
We use a dedicated fuse for the fridge, wired directly to the battery. Fuses cause less voltage drop than circuit breakers. Our fridge is always on.

Actually, our compressor is well aft, far from the house bank and right near the shore power charger. I use the (now disconnected) shore power charger's wire. It's 6 gauge. Then I have the fridge fuse coming off that, to a short-ish 14 or 16 gauge wire. 5 amps load. Seafrost says to make sure the compressor gets good power.

Regards,
Brad
__________________
Graham and Janaki
Bristol 38.8
Leela
Reply With Quote Share with Facebook
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools

 
Posting Rules
You may post new threads
You may post replies
You may post attachments
You may edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On


Similar Threads
Thread Thread Starter Forum Replies Last Post
refrigerator wavedancer38 Provisioning 15 02-03-2012 01:26 PM
Refrigerator billbalme Pacific Seacraft 7 04-11-2010 02:17 PM
Refrigerator jacobitesc Beneteau 4 02-24-2009 03:17 PM
main breaker rating adamtroyg Gear & Maintenance 28 04-13-2008 07:33 PM
Shore power problem! Burned ground wire at main breaker JohnDrake Gear & Maintenance 2 08-20-2002 05:08 AM