  #1  
Old 06-25-2009
JMan
 
Join Date: Jul 2003
Location: Virginia
Posts: 25
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 0
JohnManzano is on a distinguished road
Switching shore power from 220 to 110

I've searched this forum and can't find anything on converting a boat's electrical system from 220 volts to 110. As I consider purchasing a boat built in Europe its shore power system is European 220 volts. Can that be converted or are all the systems, i.e. battery charger only compatible with 220 volts?
Thanks for any help you can offer,
John
Reply With Quote Quick reply to this message Share with Facebook
  #2  
Old 06-25-2009
Senior Member
 
Join Date: Apr 2008
Posts: 476
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 7
negrini is on a distinguished road
Send a message via AIM to negrini Send a message via Yahoo to negrini Send a message via Skype™ to negrini
John, it depends on things you have installed on boat. If you're purchasing new, just ask for a 110V system. If it's already built on 220V you should consider many factors. I personally dislike the input transformer (a bulky transformer input 110V - output 220V). Besides the size/weight/etc you never know how many things you'll install in the future, requiring upgrades and lost of investment, and not all systems accept 50HZ vs 60Hz. Look to wich appliances are connected to AC, like freezers, microwave, airconditioning, batt charger, inverter, genset, etc ... some of them would take both 110/220 50/60Hz simply changing a switch, and some are automatic. But majority of heavy load (microwaves/aircon/etc) doesn't have such double power input. Then plan a replacement for others. The more you have installed, the more costly will be your project and certaily will ruin a good deal. Think twice ....
__________________
Nave Rara
Beneteau Oceanis 43
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
Reply With Quote Quick reply to this message Share with Facebook
  #3  
Old 06-25-2009
Senior Member
 
Join Date: Aug 2006
Location: Arlington, VA
Posts: 1,813
Thanks: 0
Thanked 4 Times in 4 Posts
Rep Power: 10
btrayfors will become famous soon enough btrayfors will become famous soon enough
Good advice!

Also, remember that wire size needed to carry 220V is smaller than that required for 110V. In some cases, you could find that the wiring and/or the fittings are undersized for 110VAC service.

For example, we just found that a new high-end Victron MultiPlus inverter/charger -- intended for the 220V European market -- won't really take the AWG6 wire needed for 50amp 110VAC service without some adapting. It's set up for much smaller wire (equivalent of AWG10).

Bill
Reply With Quote Quick reply to this message Share with Facebook
  #4  
Old 06-25-2009
JMan
 
Join Date: Jul 2003
Location: Virginia
Posts: 25
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 0
JohnManzano is on a distinguished road
Thanks your comments have been very helpful. I have thought twice and have nixed the idea.
Reply With Quote Quick reply to this message Share with Facebook
  #5  
Old 06-25-2009
imagine2frolic's Avatar
Senior Member
 
Join Date: Aug 2008
Posts: 1,830
Thanks: 0
Thanked 1 Time in 1 Post
Rep Power: 7
imagine2frolic is on a distinguished road
I had the same problem, and used adaptors for the outlets. Be cautious in doing this. As mentioned above the wire size difference could lead to a fire. I also used a transformer to change the wiring, but have slowly replaced to the correct wire size.....i2f
__________________
20 MPH ain't fast unless, you do it in a 1000sq 3/2 house on 10foot waves
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


BORROWED, No single one of us is as smart as all of us!
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.



To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
Reply With Quote Quick reply to this message Share with Facebook
Reply

Quick Reply
Message:
Options

By choosing to post the reply above you agree to the rules you agreed to when joining Sailnet.
Click Here to view those rules.

Register Now

In order to be able to post messages on the SailNet Community forums, you must first register.
Please enter your desired user name, your email address and other required details in the form below.
Please note: After entering 3 characters a list of Usernames already in use will appear and the list will disappear once a valid Username is entered.
User Name:
Password
Please enter a password for your user account. Note that passwords are case-sensitive.
Password:
Confirm Password:
Email Address
Please enter a valid email address for yourself.
Email Address:

Log-in

Human Verification

In order to verify that you are a human and not a spam bot, please enter the answer into the following box below based on the instructions contained in the graphic.




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools

 
Posting Rules
You may post new threads
You may post replies
You may post attachments
You may edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Shore Power Connecter Hawkwind Gear & Maintenance 6 06-07-2006 12:19 PM
Charging with Solar Power Kevin Jeffrey Gear and Maintenance Articles 0 07-28-2003 09:00 PM
european shore power plugs kimberlite Gear & Maintenance 2 03-05-2003 07:02 PM
Shore power problem! Burned ground wire at main breaker JohnDrake Gear & Maintenance 2 08-20-2002 06:08 AM
Adapting Power Sue & Larry Gear and Maintenance Articles 0 12-20-2001 08:00 PM


All times are GMT -4. The time now is 04:50 PM.

Add to My Yahoo!         
Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2014, vBulletin Solutions, Inc.
SEO by vBSEO 3.6.1
(c) Marine.com LLC 2000-2012

The SailNet.com store is owned and operated by a company independent of the SailNet.com forum. You are now leaving the SailNet forum. Click OK to continue or Cancel to return to the SailNet forum.