How do I determine electrical draw

I have a 12000 BTU Aqua Air Reverse cycle air conditioner. I would like to measure the watts it takes to start it up and then start the compressor. My control switch has a start position and a run position. On start it starts the motor and run starts the compressor. Where should I check the wattage, some where on the unit or at the batteries?
LakePirate is offline  
Quote Quick Reply Share with Facebook
Sponsored Links
Advertisement
 
post #2 of 7 Old 07-31-2009
Best Looking MALE Mod
 
Cruisingdad's Avatar
 
Join Date: Jul 2006
Location: Washington State
Posts: 9,917
Thanks: 3
Thanked 123 Times in 57 Posts
Rep Power: 10
     
Quote:
Originally Posted by LakePirate View Post
I have a 12000 BTU Aqua Air Reverse cycle air conditioner. I would like to measure the watts it takes to start it up and then start the compressor. My control switch has a start position and a run position. On start it starts the motor and run starts the compressor. Where should I check the wattage, some where on the unit or at the batteries?
The unit should have a manual with start up and run amps. It may even be on a sticker attached to the unit. I think they have to have it permantally mounted.

I honestly do not know how to get an exact mesurement without putting in a shunt since it is ac. Maybe Hello could help?

- CD

Sailnet Moderator



1987 Tayana Vancouver 42, Credendo Vides, (Mom and Pops boat, F/T Mobile Live Aboards in Puget Sound)

My Website:
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


Follow My Blog at:
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


Follow me on Facebook:

To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
Cruisingdad is offline  
Quote Quick Reply Share with Facebook
post #3 of 7 Old 07-31-2009
Senior Member
 
Join Date: Aug 2006
Location: Arlington, VA
Posts: 1,853
Thanks: 0
Thanked 11 Times in 9 Posts
Rep Power: 10
   
According to published specifications, the 12K BTU AquaAir S*R-16 models draw 10.4 amps @ 115VAC or 1051 watts. The water pump will draw an additional 1-2 amps, depending on model.

To get inrush current, you'd need a clamp-on ammeter with inrush capability. The min/max setting won't tell you true peak amperage (you'd need something more sophisticated for that), but would give you an idea.

Many modern rotary compressors have a fairly low in-rush current demand, dampened somewhat by start capacitors. For example, my 16,500BTU Flagship Marine A/C draws 14.1 amps at full load, and the starting current requirement is only 21 amps.

Your mileage may vary, however :-)

Bill

Last edited by btrayfors; 07-31-2009 at 01:02 PM.
btrayfors is offline  
Quote Quick Reply Share with Facebook
post #4 of 7 Old 08-01-2009
Senior Member
 
Join Date: Jul 2008
Location: chesapeake bay
Posts: 1,942
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 8
 
call up your local commercial electric company and tell them what you want, and its for a boat and you just want a guy to come buy after work. one of the guys there will have the meter to read it, they wont look at it as a real job hopefully. or go to a local electric supply house and hang out for a while, might cost ya 20 bucks or a case of beer. in real life the inrush is so short on new equipment its only 125 % of the running load. home depot sells clamp on ac amp meters for around 80 bucks, wont be perfect but close enough.

CD was right if the equipment is UL approved it has to have a perminate label with the load info. read a AC unit label is tricky, it will give you a few numbers, one is min circuit size, another max breaker size. the min circuit is normally 125% of running load, the max breaker is normally 125 % of the inrush, you only need to size the wire going to the unit to the min circuit size, its weird electric code thing.

i am a master electrician just so you know
scottyt is offline  
Quote Quick Reply Share with Facebook
post #5 of 7 Old 08-04-2009
Senior Member
 
Join Date: Jun 2006
Posts: 5,006
Thanks: 5
Thanked 18 Times in 18 Posts
Rep Power: 12
     
Quote:
Originally Posted by btrayfors View Post
To get inrush current, you'd need a clamp-on ammeter with inrush capability. The min/max setting won't tell you true peak amperage (you'd need something more sophisticated for that), but would give you an idea.
Could use a hall effects sensor too, but it is non-trivial. If I were doing it I would probably wire a hall effects sensor into the circuit which would provide an analog output that could be hooked to a scope to graph current usage. This has the advantage of being electrically isolated from your test equipment.

What are you pretending not to know ?

Please support my
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
wind_magic is offline  
Quote Quick Reply Share with Facebook
post #6 of 7 Old 08-05-2009
Best Looking MALE Mod
 
Cruisingdad's Avatar
 
Join Date: Jul 2006
Location: Washington State
Posts: 9,917
Thanks: 3
Thanked 123 Times in 57 Posts
Rep Power: 10
     
Quote:
Originally Posted by scottyt View Post

CD was right if the equipment is UL approved it has to have a perminate label with the load info. read a AC unit label is tricky, it will give you a few numbers, one is min circuit size, another max breaker size. the min circuit is normally 125% of running load, the max breaker is normally 125 % of the inrush, you only need to size the wire going to the unit to the min circuit size, its weird electric code thing.

i am a master electrician just so you know
Pfft. I am ALWAYS right!!!! And fyi, I am a Master Sailnetter (which means I know everything about every subject known and unknown to man!!!).

HEHE!

Brian

Sailnet Moderator



1987 Tayana Vancouver 42, Credendo Vides, (Mom and Pops boat, F/T Mobile Live Aboards in Puget Sound)

My Website:
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


Follow My Blog at:
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


Follow me on Facebook:

To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
Cruisingdad is offline  
Quote Quick Reply Share with Facebook
post #7 of 7 Old 08-05-2009 Thread Starter
Senior Member
 
LakePirate's Avatar
 
Join Date: May 2008
Location: Cedar Mills Marina
Posts: 128
Thanks: 0
Thanked 2 Times in 2 Posts
Rep Power: 8
 
Quote:
Originally Posted by Cruisingdad View Post
Pfft. I am ALWAYS right!!!! And fyi, I am a Master Sailnetter (which means I know everything about every subject known and unknown to man!!!).

HEHE!

Brian
Now Y'all put me in spot. I don't know who to believe, a master electrician, a master "Sailnetter" or just some other master BS'er
LakePirate is offline  
Quote Quick Reply Share with Facebook
Reply

Quick Reply
Message:
Options

By choosing to post the reply above you agree to the rules you agreed to when joining Sailnet.
Click Here to view those rules.

Register Now



In order to be able to post messages on the SailNet Community forums, you must first register.
Please enter your desired user name, your email address and other required details in the form below.
Please note: After entering 3 characters a list of Usernames already in use will appear and the list will disappear once a valid Username is entered.


User Name:
Password
Please enter a password for your user account. Note that passwords are case-sensitive.

Password:


Confirm Password:
Email Address
Please enter a valid email address for yourself.

Email Address:
OR

Log-in









Human Verification

In order to verify that you are a human and not a spam bot, please enter the answer into the following box below based on the instructions contained in the graphic.




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Show Printable Version Show Printable Version
Email this Page Email this Page



Similar Threads
Thread Thread Starter Forum Replies Last Post
Calculating Your Electrical Load Kevin Jeffrey Gear and Maintenance Articles 0 03-03-2003 07:00 PM
Electrical Power on Board Kevin Jeffrey Gear and Maintenance Articles 0 02-11-2003 07:00 PM
Electrical Power on Board Kevin Jeffrey Her Sailnet Articles 0 02-11-2003 07:00 PM

Posting Rules  
You may post new threads
You may post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On
Trackbacks are On
Pingbacks are On
Refbacks are On

 
For the best viewing experience please update your browser to Google Chrome