solar panel wire size (8 awg wont fit) and mounting question

I just bought two Kyocera 135sx-UPU with the junction box and a BlueSky 2512ix MPPT controller. With this set-up I should be making about 18 amps at most (perfect conditions not seen in Michigan), but the wire run will be about 30' round trip. Based on these number the Berkshire wire I ordered was 8 AWG.

Unfortunately, both the junction boxes on the panels and the screw terminals on the BlueSky controller call for 10 AWG max. Is there some way to step down the wire size to work with both items? Should I just get the 10 AWG wire and hook it up that way?

For people that installed panels like these, what size bar stock did you use to make the cross bars for the panels? I was trying to stick with aluminum because it's easily available locally and I wont have to worry about corrosion as much. The thickest I could find was 1/4" by 1" but it still seemed too flexible. Has anyone tried using angle stock and cutting back a small tab for the solar panel frame? By the way, these are getting mounted on the 1" SS davits via Emarine's 1" rail mounts.

Thank you,

Matt

1989 Sabre 34II Targa
mjsailing.com

Last edited by funjohnson; 06-04-2010 at 07:54 PM.
funjohnson is offline  
Quote Quick Reply Share with Facebook
Sponsored Links
Advertisement
 
post #2 of 6 Old 06-04-2010
Senior Member
 
Join Date: Sep 2004
Posts: 176
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 12
 
Matt,
What I did was use 10awg from the panel through the deck to a distribution block. Then 8awg to close to the controller. Then a butt joint from 8 down to 10awg. The large wire size is used to reduce the voltage drop, not because it is required to handle the current level.

Paul L
Paul_L is offline  
Quote Quick Reply Share with Facebook
post #3 of 6 Old 06-04-2010
Senior Member
 
Join Date: Aug 2006
Location: Arlington, VA
Posts: 1,880
Thanks: 0
Thanked 13 Times in 11 Posts
Rep Power: 11
   
Matt,

I'd use the AWG8 that you have. To connect it to the terminals, you can either:

(1) use a short length of AWG10 wire connected to the screw terminals and splice into the AWG8 close by; or

(2) trim a few strands from the AWG8 so it will fit nicely into the screw terminals.

Bill
btrayfors is offline  
Quote Quick Reply Share with Facebook
post #4 of 6 Old 06-04-2010
Senior Member
 
Join Date: Jul 2008
Location: chesapeake bay
Posts: 1,942
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 8
 
you do want to keep as large of a cable as you can, esp if you are using an mppt controller. losing the extra volt is not a big deal on a standard charge controller as they dump the extra anyway, but the mppt can use it. and running 10 gauge for 18 amps looks okay from the voltage drop end but dont do it.

as for the connections, you could use a butt connector to step down to 10 gauge, or a block as mentioned. i personally would very carefully trim a few conductors to make it fit as some one said
scottyt is offline  
Quote Quick Reply Share with Facebook
post #5 of 6 Old 06-04-2010 Thread Starter
A New Adventurer
 
funjohnson's Avatar
 
Join Date: Aug 2008
Location: Grand Rapids MI
Posts: 283
Thanks: 0
Thanked 1 Time in 1 Post
Rep Power: 8
 
Thanks guys.

Should I put anything on the screw in terminals to help prevent corrosion?

1989 Sabre 34II Targa
mjsailing.com
funjohnson is offline  
Quote Quick Reply Share with Facebook
post #6 of 6 Old 06-05-2010
Senior Member
 
Join Date: Apr 2009
Posts: 103
Thanks: 0
Thanked 1 Time in 1 Post
Rep Power: 8
 
Send a message via Skype™ to lshick
You asked "For people that installed panels like these, what size bar stock did you use to make the cross bars for the panels?"

I used 1.5" x 1.5" x .25" aluminum angle for the framing, purchased (next day delivery) from McMaster-Carr, which is a great resource. The actual mount of the solar panel to the radar arch was 1.5" x 1.5" x .125" aluminum box channel. You can see the result at my projects page.

Larry Shick
V42-148 "Moira"
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
lshick is offline  
Quote Quick Reply Share with Facebook
Reply

Quick Reply
Message:
Options

By choosing to post the reply above you agree to the rules you agreed to when joining Sailnet.
Click Here to view those rules.

Register Now



In order to be able to post messages on the SailNet Community forums, you must first register.
Please enter your desired user name, your email address and other required details in the form below.
Please note: After entering 3 characters a list of Usernames already in use will appear and the list will disappear once a valid Username is entered.


User Name:
Password
Please enter a password for your user account. Note that passwords are case-sensitive.

Password:


Confirm Password:
Email Address
Please enter a valid email address for yourself.

Email Address:
OR

Log-in









Human Verification

In order to verify that you are a human and not a spam bot, please enter the answer into the following box below based on the instructions contained in the graphic.




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Show Printable Version Show Printable Version
Email this Page Email this Page



Similar Threads
Thread Thread Starter Forum Replies Last Post
Charging with Solar Power Kevin Jeffrey Gear and Maintenance Articles 0 07-28-2003 08:00 PM

Posting Rules  
You may post new threads
You may post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On
Trackbacks are On
Pingbacks are On
Refbacks are On

 
For the best viewing experience please update your browser to Google Chrome