shore power

Last time we were at a marina and plugged into the shore power outlet (30amp) got a reverse polarity short. ii wasn't a big concern since we were only there one evening. Never got around to cking the wiring on the boat until today, over a year later

So removed the 120 volt panel and traced out wiring.(this is wiring I know about, not a mystery like some DC stuff) Oh.. what a mess, strands running under bunks, no conduit. staples on the bulkhead to light and outlet boxes, no GFIs. BUT everything checked out. no shorts anywhere that I could detect with the ohm meter. The water heater element (new WH) the 2 outlets and one reading lamp all work.

Questions;
Do marinas have more problems with wet,shorted,and unreliable shore power then I expect in my limited experience?

Options to conceal wiring on bulkheads, cabin ceiling, etc? Stapling stranded house wire is not an option

plastic wire-mold raceways come to mind. whats the word on that? I could make it out of mahogany if there isn't a "code" on such wiring on bulkheads and other areas of the boat.
thanks in advance!

Denise, Bristol PA, Oday 30. On Tidal Delaware River, Anchor Yacht Club.
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.

My last project!
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


My boat is sold!

Last edited by deniseO30; 03-20-2011 at 04:15 PM.
deniseO30 is offline  
Quote Quick Reply Share with Facebook
Sponsored Links
Advertisement
 
post #2 of 20 Old 03-20-2011
Just another Moderator
 
Faster's Avatar
 
Join Date: Sep 2005
Location: New Westminster, BC
Posts: 16,560
Thanks: 109
Thanked 317 Times in 302 Posts
Rep Power: 10
     
I thought the 'rev polarity' indication meant that the marina had the hot and neutral crossed over in their outlets....

As far as containing wires, we use this stuff linked below.. it's nice in that you can open it and add wires to it, or to trace and troubleshoot. It can be applied with hardware or double sided tape (probably not the best choice on a boat). It comes in a variety of sizes, from about 1" square to 6x6 for more industrial applications. Also, unlike tubular conduits you can exit the 'duct' anywhere you like to peel a wire out for a fixture. Raw lengths are about 6 feet.

Product Search

Ron

1984 Fast/Nicholson 345 "FastForward"

".. there is much you could do at sea with common sense.. and very little you could do without it.."
Capt G E Ericson (from "The Cruel Sea" by Nicholas Monsarrat)
Faster is online now  
Quote Quick Reply Share with Facebook
post #3 of 20 Old 03-20-2011
Senior Member
 
mitiempo's Avatar
 
Join Date: Sep 2008
Location: Victoria B.C. Canada
Posts: 7,510
Thanks: 0
Thanked 96 Times in 87 Posts
Rep Power: 8
   
Denise

It would have been the marina's wiring that was wired with the hot and neutral reversed. Your panel reverse polarity light is wired between the incoming neutral and ground connections. These should not show a voltage. But if the hot and neutral incoming are reversed the reverse polarity light is then connected between hot and ground, which would measure 115 volts or so.

Brian
Living aboard in Victoria Harbour
mitiempo is offline  
Quote Quick Reply Share with Facebook
post #4 of 20 Old 03-20-2011
Once known as Hartley18
 
Classic30's Avatar
 
Join Date: Aug 2007
Location: Melbourne, Australia
Posts: 4,847
Thanks: 46
Thanked 65 Times in 65 Posts
Rep Power: 10
   
Dock
Happens all over the world..

The solution: Some boats I've seen have a simple changeover switch to swap the hot and neutral to overcome this problem.

-
"Honestly, I don't know why seamen persist in getting wrecked in some of the outlandish places they do, when they can do it in a nice place like Fiji." -- John Caldwell, "Desperate Voyage"

Last edited by Classic30; 03-20-2011 at 05:34 PM.
Classic30 is offline  
Quote Quick Reply Share with Facebook
post #5 of 20 Old 03-20-2011
Senior Member
 
mitiempo's Avatar
 
Join Date: Sep 2008
Location: Victoria B.C. Canada
Posts: 7,510
Thanks: 0
Thanked 96 Times in 87 Posts
Rep Power: 8
   
I've yet to see that. I think it is better to fix the problem than to install a switch that can be left in the wrong position. As well, the shorepower should go to a breaker before any switches.

Sounds like a crazy Aussie fix.

Brian
Living aboard in Victoria Harbour
mitiempo is offline  
Quote Quick Reply Share with Facebook
post #6 of 20 Old 03-20-2011 Thread Starter
me at 67!
 
deniseO30's Avatar
 
Join Date: Nov 2006
Location: Bristol pa
Posts: 6,970
Thanks: 55
Thanked 126 Times in 115 Posts
Rep Power: 10
   
Thanks gentlemen! I'm sure it was the Marina's power, today I only had the boat connected with the 120 volt outdoor GFI and light duty extension cord "adapted" to the shore power plug. everything worked fine, spent the rest of the day removing the stapled wires and rip.. err.. removing the wiring that was "unacceptable" (re Holmes on homes) LOL I like that polarity reversing switch idea Hartley! woo..zzzzap.. crackle. bzzzt

Basic Electricity Tutorial - Switches

Denise, Bristol PA, Oday 30. On Tidal Delaware River, Anchor Yacht Club.
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.

My last project!
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


My boat is sold!

Last edited by deniseO30; 03-20-2011 at 06:04 PM.
deniseO30 is offline  
Quote Quick Reply Share with Facebook
post #7 of 20 Old 03-20-2011
Once known as Hartley18
 
Classic30's Avatar
 
Join Date: Aug 2007
Location: Melbourne, Australia
Posts: 4,847
Thanks: 46
Thanked 65 Times in 65 Posts
Rep Power: 10
   
Dock
That's the one..

It isn't really possible to leave it in the "wrong" position, since if you connect up shore power and they have it wired the wrong way around, you'll get the reverse polarity light on the AC panel and you simply switch it over.

Yes, it should be wired up after the breaker and before the sub-circuits, so you can switch on the mains, check if polarity is correct, before you turn on the sub-circuits - but there are some (like this one) that are designed to go before the breaker.

To the best of my knowledge, the worst that would happen if polarity is wrong is you'll trip the shore power breaker - probably the dockside one. I certainly don't see how anything could get fried.

The most common instance of reverse polarity I've seen is the use of home-made extension leads for shore power connection. Of course, it'd never happen to me...

-
"Honestly, I don't know why seamen persist in getting wrecked in some of the outlandish places they do, when they can do it in a nice place like Fiji." -- John Caldwell, "Desperate Voyage"

Last edited by Classic30; 03-20-2011 at 08:17 PM.
Classic30 is offline  
Quote Quick Reply Share with Facebook
post #8 of 20 Old 03-20-2011
Senior Member
 
mitiempo's Avatar
 
Join Date: Sep 2008
Location: Victoria B.C. Canada
Posts: 7,510
Thanks: 0
Thanked 96 Times in 87 Posts
Rep Power: 8
   
I don't think reverse polarity would trip the shorepower breaker. It certainly would if the ground was in the wrong place, as ground and neutral are connected on shore if you follow it back far enough.

The switch would work if after the main breaker.

As long as the main is a double breaker that switches both hot and neutral there shouldn't be a problem I don't think. Now if the main only switches the hot as in some older boats that could be a problem. In that case if there is reverse polarity and the switch is turned off every circuit is still hot.

Brian
Living aboard in Victoria Harbour
mitiempo is offline  
Quote Quick Reply Share with Facebook
post #9 of 20 Old 03-21-2011 Thread Starter
me at 67!
 
deniseO30's Avatar
 
Join Date: Nov 2006
Location: Bristol pa
Posts: 6,970
Thanks: 55
Thanked 126 Times in 115 Posts
Rep Power: 10
   
I actually don't like reverse switching.. been around large motors using them... Electric Chain hoists use reverse switches

Denise, Bristol PA, Oday 30. On Tidal Delaware River, Anchor Yacht Club.
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.

My last project!
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


My boat is sold!
deniseO30 is offline  
Quote Quick Reply Share with Facebook
post #10 of 20 Old 03-21-2011
Just another Moderator
 
Faster's Avatar
 
Join Date: Sep 2005
Location: New Westminster, BC
Posts: 16,560
Thanks: 109
Thanked 317 Times in 302 Posts
Rep Power: 10
     
From a practical point of view and given (what ought to be) the rarity of a bad marina source I think a (CLEARLY MARKED) pigtail made up with reversed lines that you could insert if needed would be better... obviously a deliberate act to use that as opposed to forgetting to flip a switch....

Ron

1984 Fast/Nicholson 345 "FastForward"

".. there is much you could do at sea with common sense.. and very little you could do without it.."
Capt G E Ericson (from "The Cruel Sea" by Nicholas Monsarrat)
Faster is online now  
Quote Quick Reply Share with Facebook
Reply

Quick Reply
Message:
Options

By choosing to post the reply above you agree to the rules you agreed to when joining Sailnet.
Click Here to view those rules.

Register Now



In order to be able to post messages on the SailNet Community forums, you must first register.
Please enter your desired user name, your email address and other required details in the form below.
Please note: After entering 3 characters a list of Usernames already in use will appear and the list will disappear once a valid Username is entered.


User Name:
Password
Please enter a password for your user account. Note that passwords are case-sensitive.

Password:


Confirm Password:
Email Address
Please enter a valid email address for yourself.

Email Address:
OR

Log-in









Human Verification

In order to verify that you are a human and not a spam bot, please enter the answer into the following box below based on the instructions contained in the graphic.




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Show Printable Version Show Printable Version
Email this Page Email this Page



Similar Threads
Thread Thread Starter Forum Replies Last Post
Shore Power went dead help! newcruiserP10M Electrical Systems 6 12-06-2010 12:49 PM
shore power with out shore power marcusn Gear & Maintenance 33 06-20-2008 03:55 PM
!@$%!%!! Shore Power! SEMIJim Gear & Maintenance 30 08-17-2007 12:58 PM
Re: shore power NewsReader Mass Bay Sailors 0 02-01-2007 01:15 PM
shore power NewsReader Mass Bay Sailors 0 02-01-2007 10:15 AM

Posting Rules  
You may post new threads
You may post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On
Trackbacks are On
Pingbacks are On
Refbacks are On

 
For the best viewing experience please update your browser to Google Chrome