Shore power outlets, even if correctly wired, can be a BIG problem.
If there is ANY sign of discoloration around the prongs to your shore cord or the receptacles where these prongs fit on the shore power post, replace them. Otherwise, just be sure everything is absolutely clean and that the power cord fits snugly into the outlet.
Have the marina (not you) check that the wires are very tightly attached to the outlets. "Copper creep" happens over time, and it is necessary to periodically tighten things. Spray a bit of DeOxIt on the plugs and inlets.
Do the same on your shore cord (when it's disconnected) if you have access to the prongs or sockets. Ditto on your receptacle(s) on the boat.
Just a bit of surface corrosion can cause high resistances and even intermittents such as you seemed to have been experiencing.
If you're using a splitter with 2 30-amp connections plugged into a single 50A outlet on the dock, be especially careful and prudent. A dropped or intermittent neutral can be devastating: depending on load, it can put up to 240V on one of the cords and can cause fires.
Bill