Quote:
Originally Posted by mitiempo
I try not to combine circuits whenever possible. On my own boat I have the Blue Seas 8027 AC panel - double breaker main with 6 circuits. Every outlet is on its own circuit (4) and the charger and 120 volt heater (built-in) are each on their own circuit as well. I have to be concerned about the total usage relative to dock amperage but don't have to worry about individual circuits.
|
Exactly. If I had a 30 amp breaker, but tied all of the outlets to a 15amp branch breaker, then I'd never be able to use all 30 amps available. Sure, you could run wire capable of 30 amps to the outlets, but the outlets themselves are still only rated for 15 or maybe 20 amps max (depending on which you buy).
Here's my hypothetical energy budget:
Small dehumidifier: 4.35 amps
1000w microwave: 8.30 amps
Dorm fridge: 3amps startup/2amps running
1500w electric heater: 12.5 amps
_______________________________
If all outlets are tied to a single, 15a branch breaker, then the heater alone exceeds 80% of the max load of the 15amp branch breaker. No matter where the appliances are plugged in, if I turn them on, I'll pop the breaker.
If I install
two 15a branch breakers, and plug the heater into one outlet, and the other appliances into the other outlet, then I'm at no more than 80%
per breaker, per outlet and I get to use all 30 amps available.
I took my measurements last night, and for me, the 8099 is really the only way to go. I still had to pick a slightly different spot to install it, but it should all work out. Going to be a lot of cutting...