Battery Term fuses vs wired fuses

Those block fuses that use an stud mounting adapter right on the battery are very appealing. I'm wondering if they are OK rather then doing the "within 7" mounting of line fuses. (I'm about ready to install the bluesea ACR on my boat. )

Denise, Bristol PA, Oday 30. On Tidal Delaware River, Anchor Yacht Club.
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.

My last project!
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


My boat is sold!

Last edited by deniseO30; 07-19-2012 at 07:55 PM.
deniseO30 is offline  
Quote Quick Reply Share with Facebook
Sponsored Links
Advertisement
 
post #2 of 8 Old 07-19-2012
Senior Member
 
Join Date: Jun 2007
Posts: 2,708
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 10
   
Re: Battery Term fuses vs wired fuses

Can't get much closer than right on the battery terminals, Denise I believe Blue Sea designed them for situations where mounting fuses or breakers separately, w/in the seven inch ABYC recommendation, was not practical. I've got two holders and three fuses on-order. If that isn't recommendation enough , Maine Sail uses them

Jim
deniseO30 likes this.
SEMIJim is offline  
Quote Quick Reply Share with Facebook
post #3 of 8 Old 07-19-2012 Thread Starter
me at 67!
 
deniseO30's Avatar
 
Join Date: Nov 2006
Location: Bristol pa
Posts: 6,969
Thanks: 55
Thanked 126 Times in 115 Posts
Rep Power: 10
   
Re: Battery Term fuses vs wired fuses

Thanks Jim! I was hoping so! Now I need to guess what size. the wire is #4 so I'm looking at 80 amps or less? None of the wires are over 20 ft, 2 cylinder kubota too. (need to do some amp draw readings soon)

Denise, Bristol PA, Oday 30. On Tidal Delaware River, Anchor Yacht Club.
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.

My last project!
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


My boat is sold!
deniseO30 is offline  
Quote Quick Reply Share with Facebook
post #4 of 8 Old 07-19-2012
Senior Member
 
Join Date: Aug 2006
Location: Arlington, VA
Posts: 1,854
Thanks: 0
Thanked 11 Times in 9 Posts
Rep Power: 11
   
Re: Battery Term fuses vs wired fuses

Denise,

The MRBF (terminal) fuses are one of only three types of fuses that you CAN connect directly to the house battery bank (the others being Type T and ANL).

They have a high enough AIC rating for this use. They are very convenient.

Keep in mind also that they can be neatly connected to a buss bar....sometimes this is desirable for physical layout reasons, or because you have loads connected to the buss bar which need different value fuses.

Bill
btrayfors is offline  
Quote Quick Reply Share with Facebook
post #5 of 8 Old 07-19-2012
Senior Member
 
Maine Sail's Avatar
 
Join Date: Jan 2003
Location: Maine Coast
Posts: 5,887
Thanks: 20
Thanked 222 Times in 169 Posts
Rep Power: 16
       
Re: Battery Term fuses vs wired fuses

Quote:
Originally Posted by deniseO30 View Post
Thanks Jim! I was hoping so! Now I need to guess what size. the wire is #4 so I'm looking at 80 amps or less? None of the wires are over 20 ft, 2 cylinder kubota too. (need to do some amp draw readings soon)

They are great but do add about 2" in height to the battery and they just won't fit on LOTS of boats. I have been after Blue Sea for a while to put a 90 degree twist in the bar to make them side mount....... I still have to use LOTS of ANL or Class T fuses and just installed an ANL fuse on a bank today ebcause the MRBF was too tall..

The 7" rule is rarely able to be met but so long as that wire between the bank and fuse has no possible way of ever shorting then "as close as possible" is the next best thing. The only draw back to MRBF's are the height and that they only go to 300A, but the amp rating won't affect you.

______
-Maine Sail / CS-36T


To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.




Images In Posts Property of Compass Marine Inc.


Maine Sail is offline  
Quote Quick Reply Share with Facebook
post #6 of 8 Old 07-19-2012
Senior Member
 
Maine Sail's Avatar
 
Join Date: Jan 2003
Location: Maine Coast
Posts: 5,887
Thanks: 20
Thanked 222 Times in 169 Posts
Rep Power: 16
       
Re: Battery Term fuses vs wired fuses

Quote:
Originally Posted by deniseO30 View Post
Thanks Jim! I was hoping so! Now I need to guess what size. the wire is #4 so I'm looking at 80 amps or less? None of the wires are over 20 ft, 2 cylinder kubota too. (need to do some amp draw readings soon)
No need to guess..


______
-Maine Sail / CS-36T


To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.




Images In Posts Property of Compass Marine Inc.


Maine Sail is offline  
Quote Quick Reply Share with Facebook
post #7 of 8 Old 07-20-2012
Senior Member
 
Join Date: Jun 2007
Posts: 2,708
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 10
   
Re: Battery Term fuses vs wired fuses

Quote:
Originally Posted by Maine Sail View Post
No need to guess..
Well, yeah, ya maybe kinda do. Assuming an older boat, like ours, with existing cables: How is one to know what the "temperature rating of conductor insulation" is for their cables? I used the SWAG method for my installation, assuming that the rating on the existing cables is at least as high as the "economy" Seafit cable I bought to jumper the two negative terminals together. (And I had to dig for even that.) But it was only a guess.

Jim
SEMIJim is offline  
Quote Quick Reply Share with Facebook
post #8 of 8 Old 07-20-2012 Thread Starter
me at 67!
 
deniseO30's Avatar
 
Join Date: Nov 2006
Location: Bristol pa
Posts: 6,969
Thanks: 55
Thanked 126 Times in 115 Posts
Rep Power: 10
   
Re: Battery Term fuses vs wired fuses

Well the good news is my new Norcold unit is running off the house bank. Left the boat on the dock with it running want to see how low the bank gets from about 7 last night until about 11 today (7/20)

MS yes .. no need to guess, I do just need to ck the amp draw on the starter.

Denise, Bristol PA, Oday 30. On Tidal Delaware River, Anchor Yacht Club.
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.

My last project!
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


My boat is sold!
deniseO30 is offline  
Quote Quick Reply Share with Facebook
Reply

Quick Reply
Message:
Options

By choosing to post the reply above you agree to the rules you agreed to when joining Sailnet.
Click Here to view those rules.

Register Now



In order to be able to post messages on the SailNet Community forums, you must first register.
Please enter your desired user name, your email address and other required details in the form below.
Please note: After entering 3 characters a list of Usernames already in use will appear and the list will disappear once a valid Username is entered.


User Name:
Password
Please enter a password for your user account. Note that passwords are case-sensitive.

Password:


Confirm Password:
Email Address
Please enter a valid email address for yourself.

Email Address:
OR

Log-in









Human Verification

In order to verify that you are a human and not a spam bot, please enter the answer into the following box below based on the instructions contained in the graphic.




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Show Printable Version Show Printable Version
Email this Page Email this Page



Similar Threads
Thread Thread Starter Forum Replies Last Post
question about fuses Fitz87 Electrical Systems 10 01-12-2011 12:53 PM
Blade or Glass fuses?? SanDiegoChip Electrical Systems 12 10-19-2010 09:56 AM
Fuses for the charging circuit rocinante33 Gear & Maintenance 5 06-17-2009 10:16 AM
The Value of Circuit Breakers and Fuses Chris Brignoli Gear and Maintenance Articles 0 03-24-2003 07:00 PM
breakers and fuses and amps oh my jbarros Gear & Maintenance 6 09-06-2002 11:17 AM

Posting Rules  
You may post new threads
You may post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On
Trackbacks are On
Pingbacks are On
Refbacks are On

 
For the best viewing experience please update your browser to Google Chrome