What size AC breaker?

My new to me boat has 30amp shorepower which is wired to 2 15amp breakers. These are household breakers that are located on the cabin deck inside of a standard home metal box! I have a Blue Sea 120v ac panel with burned out 30amp dual breakers. I would like to hook up the Blue Sea and get rid of the household setup. My question is should I go with the original 30amp dual breakers or go with a 15 or 20amp dual breaker to power the onboard electrics. Heater, lights etc when docked? Thank you.
Froggy is offline  
Quote Quick Reply Share with Facebook
Sponsored Links
Advertisement
 
post #2 of 21 Old 09-25-2012
Senior Member
 
poopdeckpappy's Avatar
 
Join Date: Jul 2006
Location: San Diego
Posts: 6,196
Thanks: 35
Thanked 42 Times in 36 Posts
Rep Power: 12
     
Mine has dual 15 on a 30 amp sp

Not being a electrical expert but, I would want to know how or why dual 30 ( 60amp house main ) burned out first

1955 Blanchard 51 Custom ( I got a woody )

1974 Ranger 33


Lord, give me coffee to change the things I can change and Rum to accept the things I can't
poopdeckpappy is offline  
Quote Quick Reply Share with Facebook
post #3 of 21 Old 09-26-2012
Sailboat Reboot
 
svzephyr44's Avatar
 
Join Date: Jun 2000
Location: On Board
Posts: 621
Thanks: 3
Thanked 50 Times in 44 Posts
Rep Power: 16
 
Send a message via Skype™ to svzephyr44
Re: What size AC breaker?

A breaker only protects the circuits beyond the breaker. Thus, if the first breaker in line from the shore power inlet is at the panel any short in the wire from the "house entrance" (where the shore power is plugged into the boat) and the panel will not be protected and could result in a fire. You should have a 30 amp breaker right inside the boat at the house entrance. It should be in a waterproof box.

To see what bad shore power can do at the "house entrance" see Sailing - Reboot (USA 60493): I never saw a thing

If you do not need to leave the boat plugged in to charge the batteries it is a good idea to turn off the power at the marina pedestal and unplug the wire when you leave the boat. Many marinas have stray electrical currents that will eat your zincs alive. By unplugging the boat you reduce these stray currents and your zincs will last a whole lot longer.

CAPT Roger J. Jones USN (ret.)
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


Sailboat Reboot

411 Walnut Street, #9700, Green Cove Springs, FL 32043-3443

Reboot's Agent's Email:
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


Web Site:
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


Blogging:
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


Twitter @Sailboat_Reboot
svzephyr44 is offline  
Quote Quick Reply Share with Facebook
post #4 of 21 Old 09-26-2012
Newbie
 
DannyboyUpstate's Avatar
 
Join Date: Aug 2012
Location: Albany, NY
Posts: 52
Thanks: 1
Thanked 1 Time in 1 Post
Rep Power: 4
 
The maximum breaker size is bound by the type and size of the conductor going to the load.
DannyboyUpstate is offline  
Quote Quick Reply Share with Facebook
post #5 of 21 Old 09-26-2012
Senior Member
 
Join Date: Feb 2010
Posts: 134
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 6
 
Re: What size AC breaker?

Quote:
Originally Posted by svzephyr44 View Post
any short in the wire from the "house entrance" (where the shore power is plugged into the boat) and the panel will not be protected and could result in a fire.
It is protected by the breaker in the shore based distribution panel that feeds the shore power receptacle.

Eric
fairbank56 is offline  
Quote Quick Reply Share with Facebook
post #6 of 21 Old 09-26-2012
Senior Member
 
Capt. Gary Randall's Avatar
 
Join Date: Jun 2012
Location: Mongolia
Posts: 379
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 4
 
Re: What size AC breaker?

Hello there, I don't understand why you have a dual breaker on 120 V. AC 30 amp. This circuit requires only one single 30 amp breaker.you should have a black wire that delivers current, a white wire which is neutral, and a green wire which is ground. The circuit breaker only protects the black wire which is commonly called a hot lead. Normally when you have a double breaker you're dealing with 220 ac which in that case there are four wires. You really need to have someone who is familiar with marine wiring help you with this. You don't know what someone else has done. Attempting to do this yourself without experience, could cause damage to your boat or you. Or someone might be swimming close to your boat..... this is something I really believe you should get help with.....captg


To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
[SIGPIC] The only difference between an ordeal and a adventure is your attitude!
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.

To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
Capt. Gary Randall is offline  
Quote Quick Reply Share with Facebook
post #7 of 21 Old 09-26-2012
Senior Member
 
Join Date: Feb 2010
Posts: 134
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 6
 
Re: What size AC breaker?

A dual simultaneous trip circuit breaker is an ABYC requirement for 120vac single phase shore power feed.

Eric
fairbank56 is offline  
Quote Quick Reply Share with Facebook
post #8 of 21 Old 09-26-2012
Senior Member
 
Maine Sail's Avatar
 
Join Date: Jan 2003
Location: Maine Coast
Posts: 5,890
Thanks: 20
Thanked 223 Times in 170 Posts
Rep Power: 16
       
Re: What size AC breaker?

Quote:
Originally Posted by Capt. Gary Randall View Post
Hello there, I don't understand why you have a dual breaker on 120 V. AC 30 amp. This circuit requires only one single 30 amp breaker.you should have a black wire that delivers current, a white wire which is neutral, and a green wire which is ground. The circuit breaker only protects the black wire which is commonly called a hot lead. Normally when you have a double breaker you're dealing with 220 ac which in that case there are four wires. You really need to have someone who is familiar with marine wiring help you with this. You don't know what someone else has done. Attempting to do this yourself without experience, could cause damage to your boat or you. Or someone might be swimming close to your boat..... this is something I really believe you should get help with.....captg
On boats it is an ABYC requirement to break both white/neutral and black/hot even on a single phase 120V circuit. This is why main breakers for AC on boats are doubles. On branch circuits after the main AC breaker only the black/hot needs to be broken....

Also if the wire run between the AC inlet and the main AC panel breaker is longer than 10' (wire length not as the crow flies) there should be an additional main breaker at the entrance point or close to it.

______
-Maine Sail / CS-36T


To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.




Images In Posts Property of Compass Marine Inc.



Last edited by Maine Sail; 09-26-2012 at 11:05 AM.
Maine Sail is offline  
Quote Quick Reply Share with Facebook
post #9 of 21 Old 09-26-2012
Senior Member
 
Join Date: Feb 2010
Posts: 134
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 6
 
Re: What size AC breaker?

Quote:
Originally Posted by Maine Sail View Post
On branch circuits after the main AC breaker only the black/hot needs to be broken....
Only if the boat is equipped with a reverse polarity indicator or isolation transformer. If not, the branch circuit breakers must be douple pole.

Eric

Last edited by fairbank56; 09-26-2012 at 11:29 AM.
fairbank56 is offline  
Quote Quick Reply Share with Facebook
post #10 of 21 Old 09-26-2012
Senior Member
 
Capt. Gary Randall's Avatar
 
Join Date: Jun 2012
Location: Mongolia
Posts: 379
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 4
 
Re: What size AC breaker?

I'm used to dealing with systems that have polarity protection, however it sounds like this gentleman needs some help. Especially if he has household wiring or distribution. That in itself tells me that it would be very difficult for him to have ground protection in a household distribution panel. I think he needs professional help, maybe you can help him. Eric


To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
[SIGPIC] The only difference between an ordeal and a adventure is your attitude!
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.

To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
Capt. Gary Randall is offline  
Quote Quick Reply Share with Facebook
Reply

Quick Reply
Message:
Options

By choosing to post the reply above you agree to the rules you agreed to when joining Sailnet.
Click Here to view those rules.

Register Now



In order to be able to post messages on the SailNet Community forums, you must first register.
Please enter your desired user name, your email address and other required details in the form below.
Please note: After entering 3 characters a list of Usernames already in use will appear and the list will disappear once a valid Username is entered.


User Name:
Password
Please enter a password for your user account. Note that passwords are case-sensitive.

Password:


Confirm Password:
Email Address
Please enter a valid email address for yourself.

Email Address:
OR

Log-in









Human Verification

In order to verify that you are a human and not a spam bot, please enter the answer into the following box below based on the instructions contained in the graphic.




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Show Printable Version Show Printable Version
Email this Page Email this Page



Similar Threads
Thread Thread Starter Forum Replies Last Post
Breaker for AC mitiempo Electrical Systems 6 04-20-2012 05:25 PM
Testing a breaker. L124C Electrical Systems 28 03-09-2011 11:58 PM
breaker box QuickMick Gear & Maintenance 4 03-26-2010 03:06 PM
breaker box QuickMick Gear & Maintenance 18 12-09-2009 09:03 AM
Tie Breaker km2x Racing 2 07-12-2006 11:35 PM

Posting Rules  
You may post new threads
You may post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On
Trackbacks are On
Pingbacks are On
Refbacks are On

 
For the best viewing experience please update your browser to Google Chrome