Fusing to the size of the wire....

I know that you're supposed to choose your fuses to the size of your wire, not the device amperage draw. What I'm suddenly having trouble with though, is finding a good chart that shows which fuses for which size wire.

All the tables I can find are voltage drop tables, which aren't helpful I assume. Don't I need to know at what amperage 6 gauge wire spontaneously combusts? My specific project is a 20A 12V engine heater that I would like to fuse. I'll likely be using 6 or 8 gauge wire and the round trip run will probably be around 20-30ft.

My Google-fu is weak, please help me find what I need.

Medsailor.

I have a sauna on my boat, therefore I win.
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
MedSailor is offline  
Quote Quick Reply Share with Facebook
Sponsored Links
Advertisement
 
post #2 of 7 Old 10-05-2012
Just another Moderator
 
Faster's Avatar
 
Join Date: Sep 2005
Location: New Westminster, BC
Posts: 16,577
Thanks: 110
Thanked 321 Times in 306 Posts
Rep Power: 10
     
Re: Fusing to the size of the wire....

You're looking for the 'ampacity' of the various AWG ratings. Try this...

Wire-Gauge Ampacity - Transwiki

Ron

1984 Fast/Nicholson 345 "FastForward"

".. there is much you could do at sea with common sense.. and very little you could do without it.."
Capt G E Ericson (from "The Cruel Sea" by Nicholas Monsarrat)
Faster is offline  
Quote Quick Reply Share with Facebook
post #3 of 7 Old 10-05-2012 Thread Starter
Closet Powerboater
 
MedSailor's Avatar
 
Join Date: Mar 2008
Location: Anacortes PNW
Posts: 3,579
Thanks: 258
Thanked 112 Times in 101 Posts
Rep Power: 8
 
Re: Fusing to the size of the wire....

Quote:
Originally Posted by Faster View Post
You're looking for the 'ampacity' of the various AWG ratings. Try this...

Wire-Gauge Ampacity - Transwiki
Hmmm..... I'm not exactly sure how to use that table. It looks though like they're talking about house wiring though which would be 120v or 220v which, I believe, makes a big difference because the lower voltage of the 12v is creating more heat.

It also says that the values of the table might not apply for stranded wire, which is what I would be using.

MedSailor

I have a sauna on my boat, therefore I win.
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
MedSailor is offline  
Quote Quick Reply Share with Facebook
post #4 of 7 Old 10-05-2012
Senior Member
 
Join Date: Feb 2010
Posts: 134
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 6
 
Re: Fusing to the size of the wire....

Quote:
Originally Posted by MedSailor View Post
I know that you're supposed to choose your fuses to the size of your wire, not the device amperage draw.
Not necessarily. It can be either way depending on the situation. Because of the wire sizing requirements of 12 volt circuits, the wire can typically handle way more current than the load requires.

How much current a wire can safely handle depends on the physical size of the wire, the temperature rating of its insulation, whether its run with other wires and how many, and whether its in an engine space.

In your case, if this circuit is soley for the heater, I would size the fuse for the load of the heater which is far less than #8 or #6 wire can safely handle.

Eric
fairbank56 is offline  
Quote Quick Reply Share with Facebook
post #5 of 7 Old 10-05-2012
Senior Member
 
mitiempo's Avatar
 
Join Date: Sep 2008
Location: Victoria B.C. Canada
Posts: 7,512
Thanks: 0
Thanked 96 Times in 87 Posts
Rep Power: 8
   
Re: Fusing to the size of the wire....

Here's another ampacity chart that applies to marine under 50 volts from Blue Seas
Attached Thumbnails
wire ampacity.jpg  

Brian
Living aboard in Victoria Harbour
mitiempo is offline  
Quote Quick Reply Share with Facebook
post #6 of 7 Old 10-05-2012
Senior Member
 
Join Date: Aug 2006
Location: Arlington, VA
Posts: 1,854
Thanks: 0
Thanked 11 Times in 9 Posts
Rep Power: 11
   
Re: Fusing to the size of the wire....

MedSailor,

Fusing to the size of the wire is a good overall concept, but it should not be applied slavishly. As Eric intimated, there are times when you would want to use a smaller -- even much smaller -- fuse than the wire size itself would otherwise dictate.

For example, I routinely install SSB radios having a maximum peak draw of 30A using AWG6 cable for runs up to 20' and AWG4 cable for runs over 20'. These cables have an ampacity of 120 and 160 amps, respectively (outside engine spaces). But, as these are cables dedicated to the SSB and it's maximum draw is 30A it would be foolish to use a big fuse or breaker for this purpose. I use 40A ANL and, sometimes, 30A or 40A MRBF (terminal) fuses.

Nothing wrong with using fuses or breakers rated LESS THAN the wire's ampacity, so long as you have definitive knowledge of the anticipated load(s) to be placed on that cable.

Never use fuses or breakers rated HIGHER than the ampacity of the cable they are to protect.

Bill
btrayfors is offline  
Quote Quick Reply Share with Facebook
post #7 of 7 Old 10-05-2012
Senior Member
 
asdf38's Avatar
 
Join Date: Jul 2010
Posts: 780
Thanks: 1
Thanked 12 Times in 11 Posts
Rep Power: 6
 
Re: Fusing to the size of the wire....

Quote:
Originally Posted by MedSailor View Post
It looks though like they're talking about house wiring though which would be 120v or 220v which, I believe, makes a big difference because the lower voltage of the 12v is creating more heat.
Just chiming in on this (which I actually remember talking with you about before):

The voltage of the bus has nothing to do with ampacity or heat. The voltage drop (and heat generated) is the same for 10A at 120V as it is for 10A at 12V over the same wire.

Differences in specification result from the marine environment, and because you just can't tolerate voltage drop when you only have 12 volts to start with. When you have 120V you can drop a couple of them without your load caring.
Kajungizmo likes this.

Last edited by asdf38; 10-05-2012 at 03:07 PM.
asdf38 is offline  
Quote Quick Reply Share with Facebook
Reply

Quick Reply
Message:
Options

By choosing to post the reply above you agree to the rules you agreed to when joining Sailnet.
Click Here to view those rules.

Register Now



In order to be able to post messages on the SailNet Community forums, you must first register.
Please enter your desired user name, your email address and other required details in the form below.
Please note: After entering 3 characters a list of Usernames already in use will appear and the list will disappear once a valid Username is entered.


User Name:
Password
Please enter a password for your user account. Note that passwords are case-sensitive.

Password:


Confirm Password:
Email Address
Please enter a valid email address for yourself.

Email Address:
OR

Log-in









Human Verification

In order to verify that you are a human and not a spam bot, please enter the answer into the following box below based on the instructions contained in the graphic.




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Show Printable Version Show Printable Version
Email this Page Email this Page



Similar Threads
Thread Thread Starter Forum Replies Last Post
Q: Standing rig wire size ulferlingsson Gear & Maintenance 1 06-11-2010 10:17 AM
Fusing the wire or the object? SanDiegoChip Electrical Systems 6 06-08-2010 08:48 PM
Bonding wire size? sunfishin Electrical Systems 7 01-18-2009 09:25 AM
Lifeline wire size BreakingWind2 Gear & Maintenance 4 10-06-2008 08:15 PM
Windlass Wire Size 1970Columbia34 Gear & Maintenance 3 01-01-2007 08:05 AM

Posting Rules  
You may post new threads
You may post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On
Trackbacks are On
Pingbacks are On
Refbacks are On

 
For the best viewing experience please update your browser to Google Chrome