Galvanic Isolators - SailNet Community

   Search Sailnet:

 forums  store  


Quick Menu
Forums           
Articles          
Galleries        
Boat Reviews  
Classifieds     
Search SailNet 
Boat Search (new)

Shop the
SailNet Store
Anchor Locker
Boatbuilding & Repair
Charts
Clothing
Electrical
Electronics
Engine
Hatches and Portlights
Interior And Galley
Maintenance
Marine Electronics
Navigation
Other Items
Plumbing and Pumps
Rigging
Safety
Sailing Hardware
Trailer & Watersports
Clearance Items

Advertise Here






Go Back   SailNet Community > Contributing Authors > Gear and Maintenance Articles
 Not a Member? 


Closed Thread
 
LinkBack Thread Tools
  #1  
Old 08-06-2002
Contributing Authors
 
Join Date: Jan 2000
Posts: 266
Thanks: 0
Thanked 10 Times in 7 Posts
Rep Power: 15
Tom Wood is on a distinguished road
Galvanic Isolators

My sailboat has two shore power connects, one for regular house, and the other for air conditioner. Can I use just one galvanic isolator or do I need to order two? Do I order a 30 amp for one 20 amp shore and one 50 amp for a 30 amp shore or do you match 30 to 30?

Tom Wood responds:
For full disclosure, let me begin by saying that I am not a big fan of galvanic isolators. They are nothing more than a set of diodes placed in the ground wire of a three-wire AC line as close to the inlet as possible. The theory is that these diodes can open and close the circuit at a preset electrical potential, usually about one volt. This, again in theory, isolates the AC ground from the DC ground, eliminating the possibility of stray electric current from eating up zincs, shafts, props, and thru-hulls unless there is a major need for grounding, in which case the diodes open the ground circuit.

The reality is that many boats have numerous connections between the AC and DC grounds with generator, battery charger, or inverter installations, rendering the galvanic isolator useless. The systems make a proper lightning protection system impossible. And if the diodes fail one of two things happen: if they fail in the closed position, it's as if the galvanic isolator wasn't there at all, but if they fail in the open position, the risk of electrical shock becomes very real.

If you feel that you absolutely have to have them, you must have a separate galvanic isolator on each incoming power inlet. Each must be sized to be at least 25 percent larger than the maximum capacity of the master circuit breaker on the line, so a 30-amp line should have a galvanic isolator rated at a minimum of 37.5 amps—a 40-amp unit would be the best choice but a 50 would do the same thing. A 30-amp unit would work on a circuit with a 20-amp master breaker.

 

Quick reply to this message
Closed Thread

Quick Reply
Message:
Options

By choosing to post the reply above you agree to the rules you agreed to when joining Sailnet.
Click Here to view those rules.

Register Now

In order to be able to post messages on the SailNet Community forums, you must first register.
Please enter your desired user name, your email address and other required details in the form below.
Please note: After entering 3 characters a list of Usernames already in use will appear and the list will disappear once a valid Username is entered.
User Name:
Password
Please enter a password for your user account. Note that passwords are case-sensitive.
Password:
Confirm Password:
Email Address
Please enter a valid email address for yourself.
Email Address:

Log-in

Human Verification

In order to verify that you are a human and not a spam bot, please enter the answer into the following box below based on the instructions contained in the graphic.




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools

 
Posting Rules
You may post new threads
You may post replies
You may post attachments
You may edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On



All times are GMT -4. The time now is 10:43 PM.

Add to My Yahoo!         
Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2014, vBulletin Solutions, Inc.
SEO by vBSEO 3.6.1
(c) Marine.com LLC 2000-2012

The SailNet.com store is owned and operated by a company independent of the SailNet.com forum. You are now leaving the SailNet forum. Click OK to continue or Cancel to return to the SailNet forum.