  #1  
Old 07-12-2013
tdw's Avatar
tdw tdw is offline
Super Fuzzy Moderator
 
Join Date: Oct 2006
Location: Sydney Australia
Posts: 14,394
Thanks: 5
Thanked 67 Times in 62 Posts
Rep Power: 10
tdw is a jewel in the rough tdw is a jewel in the rough tdw is a jewel in the rough
Not so Gas lines

Having been involved in repairing and replacing pretty much all the electrical systems on the Womboat since our little lightning strike it came as something of a surprise to find that our LPG lines were not up to scratch.

Gas inspector came on board to fit new solanoid and re certify installation. Much to our surprise, no go because current Australian regulations require gas lines to be coated copper, not just copper as is the case.

I knew that new instalations require coated copper but I confess it was something of a shock , an AUD1000 shock at that, to find we had to renew all lines before certification.

Sooooo ..... today me and the Wombet head on down to run new line ourselves. Shite. Cost of new coated copper tube AUD150 plus AUD50 for a pipe bender and tube cutter. Something of a saving in exchange for a day lost. To their credit the gas fitters did suggest this. We run the lines which is the time consuming tedious bit and they come in, attach the fittings, solonoid etc and then certify.

Nonetheless it should be fun (insert sarcastic emoticon) pulling the aft cabin and cockpit lockers apart to get at and remove old line. Fun indeed.

Question .... what are the regs in America and/or Europe ?

Andrew B
jimgo likes this.
__________________
Andrew B

"Do you think God gets stoned? I think so... Look at the platypus." Robin Williams.
Reply With Quote Share with Facebook
  #2  
Old 07-12-2013
chef2sail's Avatar
Senior Member
 
Join Date: Nov 2007
Location: Maryland
Posts: 6,963
Thanks: 29
Thanked 54 Times in 50 Posts
Rep Power: 7
chef2sail will become famous soon enough
Send a message via AIM to chef2sail
Re: Not so Gas lines

It appears that it has to be either annealed copper tubing or approved hose. You will need hose in the gimbal area regardless

https://law.resource.org/pub/us/cfr/....A-22.1993.pdf

A-22 MARINE COMPRESSED NATURAL GAS (CNG) SYSTEMS
Based on ABYC's assessment of the state of existing
technology and the problems associated with achieving
the requirements of the standard, ABYC recommends
compliance with this standard by August I, 1994.
22.1 PURPOSE
These voluntary teclmical practices and engineering
standards are guides for the design, construction and
installation of compressed natural gas (CNG) systems on
boats.
22.2 SCOPE
These voluntary technical practices and engineering
standards apply to all compressed natural gas (CNG)
systems used for cooking, heating and refrigeration on all
boats.
NOTES: 1. Attelltioll is directed to tlte U.S. Coast
Gllard Reglliatiolls wlticlt prohibit tlte lise of
Compressed Natllral Gas (CNG) 011 certaill
vessels alld set dif/erellt stalldards for Small
Passel/ger Vessels.
2. A,wt/,er gaseous flleillsed ill boats is
Liquefied Petrolellm Gas, (LPG). See ABYC
A-I, "Marb,e - Liquefied Petroleum Gas
(LPG) Systems".
3. Reqlliremellts for CNG galley stoves
are covered by ABYC A-3, "Galley Stoves".
22.3 DEFINITIONS
Accessible - Capable of being reached for inspection,
removal or maintenance without removal of permanent
boat structure.
Attended Appliance ~ An attended appliance is one which
is intended for use when the occupants are in the
accommodation space in which the appliance is installed,
and requires frequent attention by an operator, such as
cooking stoves and ovens and demand type water heaters
with piezo electric ignition.
Compressed Natural Gas - Consists principally of methane
in gaseous form and includes naturally occurring mixtures
of hydrocarbon gases. CNG is a natural gas that is
normally supplied as a fuel by a gas utility and is stored
under pressure in portable cylinders. Certain physical
properties of CNG are listed in the Appendix.
Cylinder - Any vessel or container used to transport or
store CNG.
Locker - An enclosure intended for storage of one or more
cylinders.
Readily Accessible ~ Capable of being reached quickly and
safely for effective use under emergency conditions
without the use of tools.
System - The arrangement of cylinders, safety devices,
regulators, connections, valves, piping, tubing, hose,
fittings, and devices intended to store, supply, monitor or
control the flow of fuel gas up to but not including the
appliance.
Unattended Appliance - Unattended appliances are those
which are intended to function without frequent attention
by an operator and may cycle on and off automatically,
such as storage type water heaters, refrigerators, or
thermostatically controlled cabin heaters.
22.4 REFERENCED ORGANIZATIONS
ABYC - American Boat & Yacht Council, Inc., 3069
Solomon's Island Road, Edgewater, MD 21037-1416.
(410)956-1050.
AGA - American Gas Association, 1515 Wilson Blvd.,
Arlington, VA 22209. (703)841-8400.
ASME - American Society of Mechanical Engineers, 345
E. 47th Street, New York, NY 10017. (212)705-7722.
ASTM·· American Society for Testing and Materials, 1916
Race Street, Philadelphia, PA 19103. (215)299-5400.
DOT· Department of Transportation, 400 Seventh Street,
Sw., Washington, DC 20590. (202)366-4000.
NFPA National Fire Protection Association,
Batterymarch Park, Quincy, MA 02269 (617)770-3000.
SAE Society of Automotive Engineers, 400
Commonwealth Drive, Warrendale, PA 15096-0001.
(412 )776-4841.
UL - Underwriters Laboratories, Inc., 12 Laboratory Drive
PO. Box 13995, Research Triangle Park, NC 27709.
(919)549-1565.
22.5 REQUIREMENTS - IN GENERAL
22.5.1 Comprehensive printed instructions and a
labeled diagram(s) covering details of proper installation,
maintenance, and operation shall be provided with each
CNG system installed in a boat. These instructions shall
include that a test be made every time the cylinder supply
valve is opened for use.
© 1993 American Boat & Yacht Council, Inc.
I
A-22 (2)
8/19/93
22.5.2 Components of this system, subject to cylinder
pressure, shall have a working pressure that is at least 133
percent of the maximum fill pressure of the cylinder.
22.5.3 With each CNG system installed on a boat a sign
shall be provided. It shall be located in the immediate
vicinity of the cylinder and shall be plainly visible. The
sign shall withstand the effects of exposure to water, oil,
saIt spray, direct sunlight, heat, cold and wear expected in
normal operation of a boat without loss of legibility, and
shall include the following informational elements:
(1) ~ CAUTION
THIS SYSTEM IS DESIGNED FOR USE WITH
COMPRESSED NATURAL GAS (CNG) ONLY.
DO NOT CONNECT LIQUEFIED PETROLEUM
GAS (LPG)
TO THIS SYSTEM.
(2) Keep cylinder valve(s) and solenoid valve(s)
closed when boat is unattended. Close them immediately
in any emergency. When on board, cylinder valve(s) or
solenoid valve(s) shall be closed when appliances are not
in use. Keep empty cylinders tightly closed.
(3) Close all appliance valves before opening
cylinder valve.
(4) Test for system leakage each time the cylinder
supply valve is opened for appliance use. Close all
appliance valves. Open solenoid shut-off valve, if
installed. Open, then close cylinder supply valve.
Observe pressure gauge at the regulating device and see
that it remains constant for not less than three minutes
before any appliance is used. If any leakage is evidenced
by a pressure drop check system with a leak detection
fluid or detergent solution, which does not contain
ammonia, and repair before operating system.
(5) NEVER USE FLAME TO CHECK FOR
LEAKS!
NOTE: Tltis sign sit all be illstalled ill tlte vicillity of
tlte cylillder alld sltall be plaillly visible.
22.5.4 On boats with a gasoline engine, the sign shall
also contain at least the following:
~WARNING
GASOLINE VAPORS ARE EXPLOSIVE.
OPEN FLAME APPLIANCES CAN IGNITE
GASOLINE VAPOR CAUSING FIRE OR
EXPLOSION.
TURN OFF ALL OPEN FLAME APPLIANCES
WHEN FUELING!
© 1993 American Boat & Yacht Council, Inc.
2
22.5.5 The system and all its components, as installed,
shall be suitable for operation within an ambient
temperature range of _18°C (O°F) to 60°C (140°F).
22.5.6 All devices and appliances using CNG shall be
secured so as to prevent upset or displacement that will
place strain upon fuel distribution system or appliance
connections.
22.6 ELECTRlL'AL DEVIL"ES IGNITION
PROTECTION
22.6.1 If CNG is provided on a boat, unattended
electrical potential sources of ignition shall be ignition
protected in accordance with UL 1500 "Ignition Protection
Test for Marine Products" or SAE Jl171, "External
Ignition Protection of Marine Electrical Devices", if:
located in compartments containing CNG appliances,
cylinders, fittings, valves, regulators, and the unattended
electrical devices located within one meter of or located
above the level of the cylinder valve.
EXCEPTIONS: 1. Accomlllodatioll spaces.
2. Opell compartmellts:
Itavillg at least 15 square iI/cites of
opell area per cubic foot of
compartmellt voillme exposed to the
opell atmospltere olltside of the craft.
22.7 CYLINDERS
22.7.1 Cylinders used in CNG systems shall meet tile
applicable DOT and AGA Regulations and standards.
22.8 CYLINDER VALVES AND SAFETY
DEVIL"ES
22.8.1 A readily accessible manual or electrically
operated (solenoid) shut-off valve(s) shall be installed in
the low pressure line to each attended appliance(s). The
valve(s) or its control shall be operable from within the
vicinity of the appliance( s) in tile event of a fire at the
appliance(s). If the cylinder valve(s) is readily accessible
from the vicinity of the attended appliance(s), the above
shut-off valve(s) on the supply line is not required.
22.9 PRESSURE REGULATOR
22.9.1 Each CNG system shall be provided with
pressure regulators specifically designed for use with
CNG, made of materials that are compatible with CNG.
22.9.2 The CNG pressure regulator system shall be
adjusted to deliver gas at any or each appliance, under
varying appliance loads, at a pressure not in excess of 16
mbar (six inches water colulJ1J1, approximately 0.22 psig).
22.9.3 The CNG pressure regulators shall be connected
directly to the cylinder shut-off valve, using one CGA
series 350 connection.
22.9.4 Each regulating system shall include a pressure
gauge. The gauge shall read the cylinder pressure side of
the pressure regulatoL
NOTES: Tlte purpose of tit is gauge is hj,ofold:
1. To mo"itor tlte amOllllt of CNG fuel
remai"i"g ill tlte storage cyli"der, a"d
2. to provide a quick a"d easy way to test tlte
systemfor leakage. (ReJ. A-22.13)
22.9.5 The pressure regulation system shall include a
high flow restrictor located on the cylinder pressure side of
the regulator which shalt
22.9.5.1 actuate and control gas flow through the vent
system to the open atmosphere in the event of regulator
malfunction, and
22.9.5.2 The vent system shall be designed to contain the
gas flow at the pressure present when the high flow
restrictor is activated.
22.9.6 The high flow restrictor vent system shall be
designed to contain the gas flow at the pressure which
actuates the high flow restrictoL
22.9.6.1 Relief vent outJet(s) shall not discharge to the
interior of the vessel.
22.9.7 The vent discharge system shall be located and
designed to prevent water from entering the regulation
system. The vent hole shall be protected against entry of
other foreign material.
22.10 FUEL SUPPLY LINES
22.10.\ The fuel supply line system and its components,
as installed, shall be designed to be compatible with CNG
and to withstand the stresses and exposure to the marine
environment
22.10.2 Copper tubing, unless internally tinned, is
prohibited.
22.10.3 CNG hose shall meet the applicable
requirements ofNFPA 52.
22.10.4 CNG supply hose shall be equipped with
pennanently attached end fittings such as swaged sleeve or
sleeve and threaded insert or other fittings specifically
designed for use with that hose.
A-22 (2)
811 9/93
22.10.5 Metal tubing shall be cOimected by means of
flare fittings. Metal to metal compression sleeve type
fittings shall not be used
22.11 LOCATION AND INSTALlATION - FUEL
LINE
22.11.1 Fuel supply lines shall be protected from
physical damage and shall be accessible for inspection.
22.11.2 A flexible section shall be used to allow the free
swing of gimbaled stoves.
22.11.3 Fuel supply lines shall be supported by clips,
straps or other suitable means, such as a conduit or tray,
to prevent vibration damage. The clips, straps or otller
means shall be corrosion resistant and shall be designed to
prevent cutting, abrading or damage to the lines and shall
be compatible with fuel supply line material
22.11.4 Fuel supply lines shall be protected by closefitting
grommets, sleeves or sealants of non-abrasive
material wherever they pass through decks and bulkheads.
Fuel supply lines passing through bulkheads that need not
be watertight shall be installed so that the bulkheads will
not cut, abrade or damage the line.
22.11.5 Fuel supply lines shall be continuous lengths of
tubing, piping or hose from the regUlating appliance or to
the flexible section at the appliance. Each appliance shall
be served by a separate supply line.
22.11.6 CNG fuel supply lines shall not be used for an
electrical ground.
22.12 LOCATION - CYLINDER AND CONNECTED
DEVICES
22.12.1 CNG systems with cOimected capacity greater
than 100 cubic feet shall provide for storage lockers (see
A-22.13S2).
22.12.2 CNG cylinders and regulation equipment shall
be located in a well ventilated area The area shall
provide protection from water or mechanical damage.
22.12.3 CNG cylinders and regulating equipment shall
be readily accessible and secured (in a vertical or
horizontal position).
22.12.4 CNG cylinders shall not be installed in
compartments containing an internal combustion engine.
22.12.5 CNG cylinder storage compartments shall not
have openings which communicate with the engine space
above the level of the pressure regulator.
(\2) 1993 American Boat & Yacht Council, Inc
3
A-22 (2)
8/19/93
22.12.6 CNG cylinders shall be located at least one
meter (three feet) from any attended open flame device, in
the same compartment.
22.13 INSTALLATION CYLINDER AND
CONNECTED DEVICES
22.13.1 CNG cylinder location shall be readily
accessible such that the cylinder valve hand wheel can be
conveniently and quickly operated and the system pressure
gauge dial is fully visible.
22 .. 13.2 If CNG cylinders are installed in a space other
than a dedicated locker, the regulators, valves and fittings
shall be protected from the weather and against
mechanical damage ..
22.133 Storage provisions for unconnected reserve
cylinders, filled or empty, shall be the same as the
provisions for the cylinder in use.
22.13.4 Compartments and lockers in which CNG
cylinders are stored shall have a ventilation opening
located above the cylinder.
22.13.5 If the CNG installation includes attached
cylinders of greater than 2.8 cubic meters (100 cubic feet)
combined capacity, the cylinders shall be:
22.13 S I located on the exterior of the boat where
escaping gases can directly escape into the open air, or
22.13.5.2 installed in a locker which shall be:
a vapor tight to the hull interior,
b. vented to the open atmosphere outside the boat,
c. constructed of or lined with corrosion resistant
materials,
d.. equipped with a means to discharge incidental
accumulated water,
e. equipped with a cover which
i. opens directly to the atmosphere,
ii. latches tightly,
111. is capable of being quickly and conveniently
opened without tools and for operating the cylinder
valves, testing the system for leakage and viewing the
pressure gauge.
© 1993

Here are the Canadian standards
http://www.pcmarinesurveys.com/Safe%...stallation.htm
__________________

To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
___________________________
S/V Haleakala (Hawaiian for" House of the Sun")
C&C 35 MKIII Hull # 76
Parkville, Maryland
(photos by Joe McCary)
Charter member of the Chesapeake Lion posse

Our blog-
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


“Sailing is just the bottom line, like adding up the score in bridge. My real interest is in the tremendous game of life.”- Dennis Conner

Last edited by chef2sail; 07-12-2013 at 10:48 PM.
Reply With Quote Share with Facebook
  #3  
Old 07-12-2013
Member
 
Join Date: Nov 2012
Location: Southern Mississippi
Posts: 33
Thanks: 1
Thanked 0 Times in 0 Posts
Rep Power: 0
Johnnycatt is on a distinguished road
Re: Not so Gas lines

ok, I was in maritime law enforcement in the US Coast Guard for 4 years back in the 90's and I don't rememeber enforcing ANY laws like what is published above me... BUT they could have added some crap - we don;t really like "freedom" here anymore.... umm. I think our regulations in the US are: if you blow-up and you damage someone else's property, you are liable for the damages...

thanks for the warning about Australiia, though.. I fully plan to sail to Australia one day.. I'm going to Durras. I'm going to lay on the beach the entire month of January and drink myself BACK to sanity.. then find a job...

Last edited by Johnnycatt; 07-12-2013 at 10:50 PM.
Reply With Quote Share with Facebook
  #4  
Old 07-12-2013
fryewe's Avatar
Senior Member
 
Join Date: Dec 2004
Location: Gulf Coast.
Posts: 1,156
Thanks: 22
Thanked 45 Times in 45 Posts
Rep Power: 10
fryewe is on a distinguished road
Re: Not so Gas lines

Damn, c2s!!! Thats a lot of ABYC regs! I am SO glad that I am happy with my low energy density/takes longer to cook/inconvenient/smelly unpressurized alcohol...
chef2sail likes this.
__________________
“Sailors, with their built in sense of order, service and discipline, should really be running the world.” – Nicholas Monsarrat
Reply With Quote Share with Facebook
  #5  
Old 07-12-2013
Senior Member
 
Join Date: Feb 2007
Location: New Jersey
Posts: 1,928
Thanks: 4
Thanked 34 Times in 34 Posts
Rep Power: 8
Tempest is on a distinguished road
Re: Not so Gas lines

They look like they are CNG specs and not LPG specs...

found this on West advisor

http://www.westmarine.com/webapp/wcs...ropane-Systems
__________________
Tempest
Sabre 34
Morgan, NJ

Last edited by Tempest; 07-12-2013 at 11:19 PM.
Reply With Quote Share with Facebook
  #6  
Old 07-12-2013
fryewe's Avatar
Senior Member
 
Join Date: Dec 2004
Location: Gulf Coast.
Posts: 1,156
Thanks: 22
Thanked 45 Times in 45 Posts
Rep Power: 10
fryewe is on a distinguished road
Re: Not so Gas lines

Quote:
Originally Posted by Tempest View Post
They look like they are CNG specs and not LPG specs...
Good catch!
__________________
“Sailors, with their built in sense of order, service and discipline, should really be running the world.” – Nicholas Monsarrat
Reply With Quote Share with Facebook
  #7  
Old 07-12-2013
Senior Member
 
Join Date: Feb 2007
Location: New Jersey
Posts: 1,928
Thanks: 4
Thanked 34 Times in 34 Posts
Rep Power: 8
Tempest is on a distinguished road
Re: Not so Gas lines

The west advisor is not a complete list of specs..I'm sure there's a more detailed code..for LPG similar to what Dave posted.
__________________
Tempest
Sabre 34
Morgan, NJ
Reply With Quote Share with Facebook
  #8  
Old 07-13-2013
Senior Member
 
Join Date: Feb 2011
Location: San Francisco Bay area
Posts: 2,219
Thanks: 2
Thanked 36 Times in 36 Posts
Rep Power: 4
MarkSF is on a distinguished road
Re: Not so Gas lines

"NOTES: 1. Attelltioll is directed to tlte U.S. Coast
Gllard Reglliatiolls wlticlt prohibit tlte lise of
Compressed Natllral Gas (CNG) 011 certaill
vessels alld set dif/erellt stalldards for Small
Passel/ger Vessels.
2. A,wt/,er gaseous flleillsed ill boats is
Liquefied Petrolellm Gas, (LPG). See ABYC
A-I, "Marb,e - Liquefied Petroleum Gas
(LPG) Systems"."

That makes it all clear then.
chef2sail likes this.
__________________
1984 Bristol 31.1
Alameda, California, USA
Reply With Quote Share with Facebook
  #9  
Old 07-13-2013
SlowButSteady's Avatar
Senior Slacker
 
Join Date: Feb 2010
Location: SoCal
Posts: 4,223
Thanks: 0
Thanked 17 Times in 15 Posts
Rep Power: 5
SlowButSteady is on a distinguished road
Re: Not so Gas lines

This thread just re-enforces my love of non-pressured alcohol stoves.
__________________
Never forget them. Do something to prevent it from happening again.
Charlotte Bacon, Daniel Barden, Rachel Davino, Olivia Josephine Gay, Ana M. Marquez-Greene, Dylan Hockley, Dawn Hochsprung, Madeleine F. Hsu, Catherine V. Hubbard, Chase Kowalski, Jesse Lewis, James Mattioli , Grace McDonnell, Anne Marie Murphy, Emilie Parker, Jack Pinto, Noah Pozner, Caroline Previdi, Jessica Rekos, Avielle Richman, Lauren Rousseau, Mary Sherlach, Victoria Soto, Benjamin Wheeler, Allison N. Wyatt
Reply With Quote Share with Facebook
  #10  
Old 07-13-2013
Senior Member
 
Join Date: Nov 2010
Location: Baltimore
Posts: 411
Thanks: 8
Thanked 5 Times in 5 Posts
Rep Power: 4
MastUndSchotbruch is on a distinguished road
Re: Not so Gas lines

Quote:
Originally Posted by SlowButSteady View Post
This thread just re-enforces my love of non-pressured alcohol stoves.
Good, but you dont' go far enough!

Long live kerosene!

Kerosene is the saltiest fuel!
Reply With Quote Share with Facebook
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools

 
Posting Rules
You may post new threads
You may post replies
You may post attachments
You may edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Size & Type: Dock lines vs. Mooring lines JordanH Gear & Maintenance 23 05-19-2011 10:29 PM
Off her lines? L124C Sailboat Design and Construction 0 08-14-2009 06:24 PM
lines xort Gear & Maintenance 22 08-05-2008 04:40 PM
Lines aft - what''s best? raybies Gear & Maintenance 6 01-01-2004 11:27 AM
Lines aft sneuman Gear & Maintenance 6 09-29-2003 09:10 AM


All times are GMT -4. The time now is 12:54 AM.

Add to My Yahoo!         
Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2014, vBulletin Solutions, Inc.
SEO by vBSEO 3.6.1
(c) Marine.com LLC 2000-2012

The SailNet.com store is owned and operated by a company independent of the SailNet.com forum. You are now leaving the SailNet forum. Click OK to continue or Cancel to return to the SailNet forum.