Combining 110v & 12v charging systems - SailNet Community
 
LinkBack Thread Tools
post #1 of 6 Old 08-22-2004 Thread Starter
Member
 
Join Date: Jun 2004
Posts: 92
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 12
 
Combining 110v & 12v charging systems

I''m looking to add a solar panel/controller to my boat. I already have a Xantrex Trace 20 110v (shorepower) charger.

Everything I read discusses how to hook up 110v charging or 12v charging but not both together.

The question is, how do you add another charger circuit (of a different voltage) to an existing system?
mmccoy is offline  
Quote Quick Reply Share with Facebook
Sponsored Links
Advertisement
 
post #2 of 6 Old 08-23-2004
Junior Member
 
Join Date: Mar 2002
Posts: 4
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 0
 
Combining 110v & 12v charging systems

Hi mmcoy,
Your 110v shore power charger converts the 110v AC to a charging current of 12-14 volts DC. Once the shore power is unplugged, the charging stops and your solar panel can kick in to trickle charge your batteries. If your solar panel doesn''t already have an isolating circuit, you can isolate your solar panel from your shore power by simply installing a diode in-line between your solar panel and the battery. This will limit current flow to one direction only. Many panels already have this protection built-in and a quick check of the manufacturer''s specs should tell your whether yours does or not. Hope this helps.
SCSeaside is offline  
Quote Quick Reply Share with Facebook
post #3 of 6 Old 08-24-2004
Senior Member
 
Join Date: Dec 2002
Posts: 552
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 13
 
Combining 110v & 12v charging systems

A solar Panel puts out an unregulated charge, so long as there is sunlight, regardless of battery voltage (state of charge). A Solar Charge Controller could provide "Regulated" output.
Your Xantrax 110V Battery Charger senses the battery voltage, and varies it’s output accordingly (so long as 110V is applied).
Hence, you don’t want your Solar Panels connected at the same time as your AC Charger - the Voltage output from the Solar Panel would “fool” the AC Charger, and reduce it’s output.
Put a disconnect switch in series with the positive output of the Solar Panel (& Blocking Diode, if equipped).
GordMay is offline  
Quote Quick Reply Share with Facebook
post #4 of 6 Old 08-24-2004 Thread Starter
Member
 
Join Date: Jun 2004
Posts: 92
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 12
 
Combining 110v & 12v charging systems

Ahh... I just knew you couldn''t simultaneously connect the solar panels/controller to the batts with a 110v charger wired to the batts as well without one charger ''interfering'' with the other.

Makes sense to disconnect the solar charging circuit when attached to shore power (and using the Xantrex).

It''s a shame to ''waste'' the power being generated by the solar panel(s) even when connected to shore power though. hmmm... maybe in addition to the disconnect I could have an extra switch position that would shunt it to a seperate, dedicated 12v outlet as well.

mmccoy is offline  
Quote Quick Reply Share with Facebook
post #5 of 6 Old 08-24-2004
Junior Member
 
Join Date: Aug 2004
Posts: 3
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 0
 
Combining 110v & 12v charging systems

How about diode isolation?

Ed
bobsquarepants is offline  
Quote Quick Reply Share with Facebook
post #6 of 6 Old 08-25-2004
Senior Member
 
Join Date: Dec 2002
Posts: 552
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 13
 
Combining 110v & 12v charging systems

Your (proposed) “dedicated” 12V outlet wouldn’t need to be shunt switched - just connect it in parallel with the Blocking Diode (Ed’s “isolation”) ahead of the disconnect (which is effectively, a permanent “shunt” connection). The outlet will always get it’s power from the Solar Cell, but will only be able to power devices rated less than the Solar output.
This is tough to put into words, when a very simple sketch would be so illuminating. Have I made it clear as mud?
Gord
GordMay is offline  
Quote Quick Reply Share with Facebook
Reply

Quick Reply
Message:
Options

Register Now



In order to be able to post messages on the SailNet Community forums, you must first register.
Please enter your desired user name, your email address and other required details in the form below.
Please note: After entering 3 characters a list of Usernames already in use will appear and the list will disappear once a valid Username is entered.


User Name:
Password
Please enter a password for your user account. Note that passwords are case-sensitive.

Password:


Confirm Password:
Email Address
Please enter a valid email address for yourself.

Email Address:
OR

Log-in









Human Verification

In order to verify that you are a human and not a spam bot, please enter the answer into the following box below based on the instructions contained in the graphic.




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Show Printable Version Show Printable Version
Email this Page Email this Page



Similar Threads
Thread Thread Starter Forum Replies Last Post
Mainsail slide systems psotis Gear & Maintenance 11 09-10-2006 10:10 PM
Mainsail Furling/Reefing Systems camaraderie Gear & Maintenance 10 06-27-2003 02:52 PM
Charging Regulators davealves Gear & Maintenance 3 03-30-2002 11:31 PM

Posting Rules  
You may post new threads
You may post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On
Trackbacks are On
Pingbacks are On
Refbacks are On

 
For the best viewing experience please update your browser to Google Chrome