Refrigeration or AC groundfaults

I was reading BoatUS site today on preventing Electrical Shock Deaths and they alluded to the higher risk of ground faults occurring in marine ac or refrigeration setups....no explanation was given Enquiring Mind wants to Know....

Sent from my SAMSUNG-SGH-I317 using Tapatalk
oysterman23 is offline  
Quote Quick Reply Share with Facebook
Sponsored Links
Advertisement
 
post #2 of 12 Old 12-30-2014
me at 67!
 
deniseO30's Avatar
 
Join Date: Nov 2006
Location: Bristol pa
Posts: 6,925
Thanks: 55
Thanked 125 Times in 114 Posts
Rep Power: 10
   
Re: Refrigeration or AC groundfaults

Refridge & ac compressors are sealed (hermetic) the motor windings are subjected all manner of hazards, acids, heat & cold, hi & lo volts amps, unlike a motor on a air compressor in a shop. So, because of the sealed nature the motor must endure it's very common for transient current to trip gfi breakers as the motor windings get old.

Denise, Bristol PA, Oday 30. On Tidal Delaware River, Anchor Yacht Club.
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.

My last project!
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


My boat is sold!
deniseO30 is offline  
Quote Quick Reply Share with Facebook
post #3 of 12 Old 12-31-2014
islander bahama 24
 
newhaul's Avatar
 
Join Date: Feb 2010
Location: bremerton wa
Posts: 1,711
Thanks: 7
Thanked 53 Times in 53 Posts
Rep Power: 6
 
Re: Refrigeration or AC groundfaults

That is something that sounds interest in to me as well I could see the motor shorting out and on ac systems at high voltages killing someone with a shock however all the refer systems I have worked on on boats are 12v and while it can hurt to get zapped its not usually enough to do any serious damage to your body. Is there a link to the article

Illegitimus Non Tatum Carborundum.

To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
newhaul is online now  
Quote Quick Reply Share with Facebook
post #4 of 12 Old 12-31-2014
me at 67!
 
deniseO30's Avatar
 
Join Date: Nov 2006
Location: Bristol pa
Posts: 6,925
Thanks: 55
Thanked 125 Times in 114 Posts
Rep Power: 10
   
Re: Refrigeration or AC groundfaults

It's more Like low currents that eat anodes NewHaul. not enough to kill but enough to cause problems or unreliable starts. If one knows how motors are made, one would also wonder how any don't short out. Copper wire with varnish on it was the standard since Edison and Tesla started building them.

Denise, Bristol PA, Oday 30. On Tidal Delaware River, Anchor Yacht Club.
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.

My last project!
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


My boat is sold!
deniseO30 is offline  
Quote Quick Reply Share with Facebook
post #5 of 12 Old 12-31-2014
Dirt Free
 
boatpoker's Avatar
 
Join Date: Jul 2008
Location: Toronto
Posts: 1,166
Thanks: 9
Thanked 32 Times in 31 Posts
Rep Power: 8
 
Re: Refrigeration or AC groundfaults

Quote:
Originally Posted by deniseO30 View Post
It's more Like low currents that eat anodes NewHaul. not enough to kill
300 to 500ma DC can be fatal. there's a lot of ma in an 800MCA starter battery.

Dirt People Scare me
boatpoker is offline  
Quote Quick Reply Share with Facebook
post #6 of 12 Old 12-31-2014
Landsman
 
Join Date: Jan 2013
Location: Oregon
Posts: 40
Thanks: 5
Thanked 3 Times in 3 Posts
Rep Power: 0
 
Re: Refrigeration or AC groundfaults

I can't find the article but they may be referring to issues with nuisance tripping on motor starting. These are not actual faults, but the GFCI unit is extremely sensitive and the large starting currents drawn by these motors can look like some type of ground fault to the GFCI.

Just as an aside, 12 V dc does not really present any type of significant shock hazard. Current magnitude (and current path) is important, but there must be sufficient voltage to push the current through the body. This is rarely possible below about 50 V, except in situations where the voltage is applied under the skin, such as things that hospitals stick in your body.

120 V ac can definitely kill you, but with 12 V dc it would be highly unlikely if not impossible.
k7el is offline  
Quote Quick Reply Share with Facebook
post #7 of 12 Old 12-31-2014
me at 67!
 
deniseO30's Avatar
 
Join Date: Nov 2006
Location: Bristol pa
Posts: 6,925
Thanks: 55
Thanked 125 Times in 114 Posts
Rep Power: 10
   
Re: Refrigeration or AC groundfaults

hmmm ok, how? I mean in a practical sense. Don't think I've ever considered it possible so maybe we can all learn what conditions would make it possible

Can a 12v car battery kill - Electronics Forums


Ohm's Law (again!) : Electrical Safety - Electronics Textbook


BODILY EFFECT DIRECT CURRENT (DC) 60 Hz AC 10 kHz AC
---------------------------------------------------------------
Slight sensation Men = 1.0 mA 0.4 mA 7 mA
felt at hand(s) Women = 0.6 mA 0.3 mA 5 mA
---------------------------------------------------------------
Threshold of Men = 5.2 mA 1.1 mA 12 mA
perception Women = 3.5 mA 0.7 mA 8 mA
---------------------------------------------------------------
Painful, but Men = 62 mA 9 mA 55 mA
voluntary muscle Women = 41 mA 6 mA 37 mA
control maintained
---------------------------------------------------------------
Painful, unable Men = 76 mA 16 mA 75 mA
to let go of wires Women = 51 mA 10.5 mA 50 mA
---------------------------------------------------------------
Severe pain, Men = 90 mA 23 mA 94 mA
difficulty Women = 60 mA 15 mA 63 mA
breathing
---------------------------------------------------------------
Possible heart Men = 500 mA 100 mA
fibrillation Women = 500 mA 100 mA
after 3 seconds
---------------------------------------------------------------

Denise, Bristol PA, Oday 30. On Tidal Delaware River, Anchor Yacht Club.
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.

My last project!
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


My boat is sold!
deniseO30 is offline  
Quote Quick Reply Share with Facebook
post #8 of 12 Old 12-31-2014
Dirt Free
 
boatpoker's Avatar
 
Join Date: Jul 2008
Location: Toronto
Posts: 1,166
Thanks: 9
Thanked 32 Times in 31 Posts
Rep Power: 8
 
Re: Refrigeration or AC groundfaults

Quote:
Originally Posted by k7el View Post
I can't find the article but they may be referring to issues with nuisance tripping on motor starting. These are not actual faults, but the GFCI unit is extremely sensitive and the large starting currents drawn by these motors can look like some type of ground fault to the GFCI.

Just as an aside, 12 V dc does not really present any type of significant shock hazard. Current magnitude (and current path) is important, but there must be sufficient voltage to push the current through the body. This is rarely possible below about 50 V, except in situations where the voltage is applied under the skin, such as things that hospitals stick in your body.

120 V ac can definitely kill you, but with 12 V dc it would be highly unlikely if not impossible.
The factor deciding the effects of the AC and DC current is the path the current takes through the body. If it is from the hand to the foot, it does not pass through the heart, and then the effects are not so lethal.

However DC current will make a single continuous contraction of the muscles compared to AC current, which will make a series of contractions depending on the frequency it is supplied at. In terms of fatalities, both kill but more milliamps are required of DC current than AC current at the same voltage.

If the current takes the path from hand to hand thus passing through the heart it can result in fibrillation of the heart. Fibrillation is a condition when all the heart muscles start moving independently in a disorganized manner rather than in a state of coordination. It affects the ability of the heart to pump blood, resulting in brain damage and eventual cardiac arrest.

Either AC or DC currents can cause fibrillation of the heart at high enough levels. This typically takes place at 30 mA of AC (rms, 60 Hz) or 300 500 mA of DC.


This quote From Bright Hub Engineering but there are numerous other sources ...

Effects of an AC or DC Currents on the Human Body
The three basic factors that determine what kind of shock you experience are the amplitude of the current, the duration of the current passing through the body, and the frequency.

Direct Currents actually have zero frequency, as the current is constant. However, there are physiological effects during electrocution no matter what type of current.Though both AC and DC currents and shock are lethal, more DC current is required to have the same effect as AC current. For example, if you are being electrocuted or shocked 0.5 to 1.5 milliamps of AC 60 Hz current is required and up to 4 mA of DC current is required. For the let-go threshold in AC a current of 3 to 22 mA is required against 15 to 88 of DC current.

Dirt People Scare me
boatpoker is offline  
Quote Quick Reply Share with Facebook
post #9 of 12 Old 12-31-2014
me at 67!
 
deniseO30's Avatar
 
Join Date: Nov 2006
Location: Bristol pa
Posts: 6,925
Thanks: 55
Thanked 125 Times in 114 Posts
Rep Power: 10
   
Re: Refrigeration or AC groundfaults

AC and DC Electric Shock Effects Compared
Either AC or DC currents can cause fibrillation of the heart at high enough levels. This typically takes place at 30 mA of AC (rms, 60 Hz) or 300 500 mA of DC.

Though both AC and DC currents and shock are lethal, more DC current is required to have the same effect as AC current. For example, if you are being electrocuted or shocked 0.5 to 1.5 milliamps of AC 60 Hz current is required and up to 4 mA of DC current is required. For the let-go threshold in AC a current of 3 to 22 mA is required against 15 to 88 of DC current.


Now on a 24 volt boat.....But who has actually been killed by boat or auto 12 volt DC? I you were killed by it please speak up!

Denise, Bristol PA, Oday 30. On Tidal Delaware River, Anchor Yacht Club.
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.

My last project!
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


My boat is sold!
deniseO30 is offline  
Quote Quick Reply Share with Facebook
post #10 of 12 Old 12-31-2014 Thread Starter
S/V Wyndwitch - Morgan 24
 
oysterman23's Avatar
 
Join Date: Jul 2011
Location: South Shore LI. NY
Posts: 369
Thanks: 235
Thanked 12 Times in 10 Posts
Rep Power: 5
 
Re: Refrigeration or AC groundfaults

Thanks for your responses. The boats us article related to ac and fresh water environments . I was very surprised the low mili amperage which can be fatal. 1/3 of what it takes to power a 60 watt bulb. It also pointed out many salt water creeks are actually brackish OE fresh near their heads...I can think of all sorts of locations here where swimming should be avoided and of course after heavy rains the effect could be wide spread.

Sent from my SAMSUNG-SGH-I317 using Tapatalk
oysterman23 is offline  
Quote Quick Reply Share with Facebook
Reply

Quick Reply
Message:
Options

By choosing to post the reply above you agree to the rules you agreed to when joining Sailnet.
Click Here to view those rules.

Register Now



In order to be able to post messages on the SailNet Community forums, you must first register.
Please enter your desired user name, your email address and other required details in the form below.
Please note: After entering 3 characters a list of Usernames already in use will appear and the list will disappear once a valid Username is entered.


User Name:
Password
Please enter a password for your user account. Note that passwords are case-sensitive.

Password:


Confirm Password:
Email Address
Please enter a valid email address for yourself.

Email Address:
OR

Log-in









Human Verification

In order to verify that you are a human and not a spam bot, please enter the answer into the following box below based on the instructions contained in the graphic.




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Show Printable Version Show Printable Version
Email this Page Email this Page



Similar Threads
Thread Thread Starter Forum Replies Last Post
refrigeration mickeyrouse Electrical Systems 5 04-06-2013 08:03 AM
Refrigeration Help SailingChance Electrical Systems 3 10-16-2012 10:16 AM
refrigeration pc37howard Pacific Seacraft 10 12-21-2011 12:34 AM
Refrigeration - Old v New rayncyn51 Gear & Maintenance 9 06-16-2011 01:47 PM
Refrigeration on a 34 johnharch Pacific Seacraft 9 02-01-2010 09:46 AM

Posting Rules  
You may post new threads
You may post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On
Trackbacks are On
Pingbacks are On
Refbacks are On

 
For the best viewing experience please update your browser to Google Chrome