Trozden: There's a few ways this is done. First, you can add a simple charge controller that pulses input as voltage approaches a maximum, then cuts the turbine loose -- just opens the circuit. The danger is that small turbines spin pretty fast and need a load to keep their RPMs in check. Left to freewheel, they can tear themselves to bits. Dunno if the KISS is made to survive unloaded operation or not.
Second means is mechanical braking. Fancy turbines may pitch their blades; some manually or automatically turn the rotor at right angles to the tail; but a few have tried actual friction devices to slow or stop the rotor (disc or drum brakes, basically). These last tend to wear out, but they can give you a positive shutdown until they do.
Third means is alternator braking. Basically the controller shorts the turbine leads together, either in pulses (SWWP AirX) or continuously (Bergey XL1). It'll spare the batteries for sure, and it may slow the turbine in medium or light winds. High winds can overpower the braking force of the coils, alas, and the turbine can begin revving up anyhow. Then you are likely in for a fried stator or rectifier. The electrons got nowhere to go, and oooh do those coil get hot!
Final (and best) means is to get yerself a slightly smarter controller ( or a second, dumb one like the Trace C40) that can manage a diversion load. You set it so upon reaching full battery charge, the turbine's power gets shunted to a mighty resistor. Turby's always kept under load, batteries are spared. I use an Outback MX60 as a solar controller, because the Bergey turbine controller's dump load is too stupid for words. When the Outback senses battery bus voltage is about 28.8VDC for a set period of time, a small current is sent to a solid-state relay, which diverts the wind turbine input to parallel water-heater elements. The MX60 is so smart, it knows hysteresis -- that is, it'll keep the diversion load on until battery voltage falls below a value you select.
Some folks use banks of lightbulbs, or air-heating elements, or similar for their dump loads. I don't like the hazard they present, and I find water can soak up a whole lot more watts than air. Plus hot water is always welcome!
ETA: You can't use hardware-store water heater elements for low-voltage DC, by the way. You can buy special DC elements (ouchouchouch, $80 each); or, if you have an inverter that can handle the strain, use cheapo household elements wired for 110V on a dedicated AC circuit switched by the solid-state relay. That's how mine works. My neighbor actually uses a dedicated (manky Harbor Freight) inverter upstream of his water heating element.