  #221  
Old 03-31-2010
Senior Member
 
Join Date: Jul 2008
Location: chesapeake bay
Posts: 1,942
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 7
scottyt is on a distinguished road
Quote:
Originally Posted by fairbank56 View Post
... instant Internet "experts" ...
did he just call maine sail an internet expert?.... sure sounds like it to me
Reply With Quote Share with Facebook
  #222  
Old 03-31-2010
Maine Sail's Avatar
Senior Member
 
Join Date: Jan 2003
Location: Maine Coast
Posts: 5,274
Thanks: 9
Thanked 114 Times in 83 Posts
Rep Power: 15
Maine Sail is just really nice Maine Sail is just really nice Maine Sail is just really nice Maine Sail is just really nice
Quote:
Originally Posted by fairbank56 View Post
This thread is about "Crimping versus Soldering". You seemed to bring up CFR rules in defense of ABYC rules regarding this subject when you stated "The ABYC standards are partly derived from the CFR".
No, I brought it up simply to explain where and how the ABYC comes to present its standards, partly from the CFR and partly from evidence and other sources.



Quote:
Originally Posted by fairbank56 View Post
CFR rules do not say a soldered wire termination must have a "mechanical connection, then solder" as you stated.
Eric, please read very carefully I NEVER stated that the CFR said that. I said the ABYC says that but never said the CFR stated that.

Quote:
Originally Posted by fairbank56 View Post
CFR rules say you can have EITHER a pressure type connector or a solder lug, EITHER a pressure type splice connector or a soldered splice.
Yes that is what CFR 46 says never disputed that.

Quote:
Originally Posted by fairbank56 View Post
The point is, soldering is fine when done properly just as crimping is fine when done properly just as crimping and then soldering is fine when done properly.

Yes, I think I said most of that too.

Quote:
Originally Posted by fairbank56 View Post
Iv'e seen PLENTY of improperly installed terminations done either way.
Yes I too have seen all type of connections done incorrectly but more bad solder than anything, mostly due to incorrect practices.

Quote:
Originally Posted by fairbank56 View Post
The debate goes on because of all the instant Internet "experts" who have little experience and don't know what the heck they are talking about.

Eric
Are you calling me an "internet expert" who does not know anything? Not very becoming behavior when we agree on the vast majority of what we are discussing. You take me out of context, make up stuff that I never said and then insult me? Cool, welcome to the forum..
__________________
______
-Maine Sail / CS-36T


To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.




© Images In Posts Property of Compass Marine Inc.



Last edited by Maine Sail; 03-31-2010 at 08:28 PM.
Reply With Quote Share with Facebook
  #223  
Old 03-31-2010
Senior Member
 
Join Date: Feb 2010
Posts: 134
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 5
fairbank56 is on a distinguished road
Quote:
Originally Posted by Maine Sail View Post
Are you calling me an "internet expert" who does not know anything?
Absolutely not. You are obviously quite knowledgable about the subject and the rules. I am talking about those who jump in here and make claims about this and that when they obviously don't have a clue but think they do because they just "googled it" and are now "experts". People misstate ABYC rules ALL THE TIME. It can be quite frustrating, and comical, for an experienced pro to deal with the inexperienced DIY's who think they know it all.

Eric
Reply With Quote Share with Facebook
  #224  
Old 03-31-2010
Maine Sail's Avatar
Senior Member
 
Join Date: Jan 2003
Location: Maine Coast
Posts: 5,274
Thanks: 9
Thanked 114 Times in 83 Posts
Rep Power: 15
Maine Sail is just really nice Maine Sail is just really nice Maine Sail is just really nice Maine Sail is just really nice
Quote:
Originally Posted by fairbank56 View Post
Absolutely not. You are obviously quite knowledgable about the subject and the rules. I am talking about those who jump in here and make claims about this and that when they obviously don't have a clue but think they do because they just "googled it" and are now "experts". People misstate ABYC rules ALL THE TIME. It can be quite frustrating, and comical, for an experienced pro to deal with the inexperienced DIY's who think they know it all.

Eric

People often think the ABYC is mandatory for them when it is not. You and I are in strong agreement on that. Still not a bad idea for a DIY to try and do projects that would comply if only for insurace surveys and re-sale surveys.

That being said, as you and I know, the ABYC standards are not perfect. There are parts I don't agree with and some points I am working with them on to get into committee, reviewed and added/changed, but for the most part it is an excellent standard and one I always try to work by because it is good and partly based in evidence, something many standards are not.

Give folks a chance here there are lots of very knowlegeable DIY's on this site as well as many industry professionals who do this day in day out...
__________________
______
-Maine Sail / CS-36T


To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.




© Images In Posts Property of Compass Marine Inc.


Reply With Quote Share with Facebook
  #225  
Old 04-01-2010
KeelHaulin's Avatar
STARBOARD!!
 
Join Date: Mar 2006
Posts: 1,662
Thanks: 0
Thanked 2 Times in 2 Posts
Rep Power: 10
KeelHaulin will become famous soon enough KeelHaulin will become famous soon enough
Well; despite 23 pages of diatribe over crimping v. soldering, I feel compelled to make one more addition. I wanted to point out that on the ABYC code it says that a soldered connection would be acceptable if it is made secure from flexing at the ends of the solder joint (where wires would be bent sharply).

I am going to make the point that if you use a long enough length of adhesive lined heat shrink tubing on the solder joint; the ends of the solder joint become supported by the heat shrink tubing as it is less flexible than just the wire with it's sheath. If you are connecting two hot/ground wires with solder and you cover both individually with heat shrink; then cover both together with a larger/longer piece of heat shrink you will not only protect the connection from flexing you will protect them from chafe, moisture and corrosion.

For end point connections I would use crimp connectors with heat shrink (which are damn expensive to buy in small quantity).

What I don't understand about ABYC's protocol regarding minimizing flex of solder joints is that it does not also apply to crimped connections; as they also create a "hard/solid joint" where the wire is joined to the connector.
Reply With Quote Share with Facebook
  #226  
Old 04-01-2010
Senior Member
 
Join Date: Feb 2010
Posts: 134
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 5
fairbank56 is on a distinguished road
Quote:
Originally Posted by Maine Sail View Post
There are parts I don't agree with and some points I am working with them on to get into committee, reviewed and added/changed,...
Have them check into sections 11.17.4, .5, and .6 and their associated wiring diagrams. The diagrams are incorrect and Iv'e been seeing incorrectly wired isolation transformers because of this. Installers are going strictly by the diagrams and not reading the text. As an example, they wire an isolation xformer as an isolation system but connect the shore ground to the shield AND the xformer case (according to the diagram). This wiring is done inside the xformer enclosure. Then somebody comes along and connects an external bond wire to one of the xformer's mounting bolts. They have just bypassed the purpose of the isolation system. The shore ground should ONLY be connected to the xformer shield in an isolation system. Sorry, way off topic but this thread is about finished anyway.

Eric
Reply With Quote Share with Facebook
  #227  
Old 04-01-2010
Maine Sail's Avatar
Senior Member
 
Join Date: Jan 2003
Location: Maine Coast
Posts: 5,274
Thanks: 9
Thanked 114 Times in 83 Posts
Rep Power: 15
Maine Sail is just really nice Maine Sail is just really nice Maine Sail is just really nice Maine Sail is just really nice
Quote:
Originally Posted by KeelHaulin View Post
What I don't understand about ABYC's protocol regarding minimizing flex of solder joints is that it does not also apply to crimped connections; as they also create a "hard/solid joint" where the wire is joined to the connector.
Properly executed crimps, using the correct crimping tool, provide strain relief by design. An insulated crimp of good quality for the marine environment will consist of three pieces and two crimps will be made, one for strain relief clamping down on the jacket, and one on the bare stripped wire.

As a point of interest I have cycled both double crimps and heat shrink crimps over 100 times a full 180 degrees, side to side, with UL 1426 wire, and seen no detrimental effects..



__________________
______
-Maine Sail / CS-36T


To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.




© Images In Posts Property of Compass Marine Inc.


Reply With Quote Share with Facebook
  #228  
Old 06-16-2010
Member
 
Join Date: Jun 2010
Location: Miami, Florida
Posts: 97
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 5
ulferlingsson is on a distinguished road
This thread is a little bit odd because it does not discuss when, where, why. I mean, it is like asking, "Is it better to weld or to use bolts?" It depends, doesn't it?

Soldering is excellent for small things, light things, and if done in a well controlled manner. Most bad soldering joints are probably the result of working with inferior equipment, in the field, and without proper training. Dirty connectors, cold solder, etc.

For heavy gauge wire, soldering should not be used. For AWG 20 or finer, with a temperature controlled iron, it is excellent - if heat shrink tubing is applied well outside the joint on both sides, for strain relief. Or use two layers, it's not that expensive!
__________________
Ensenada 20, 1972
Reply With Quote Share with Facebook
  #229  
Old 06-16-2010
Senior Member
 
Join Date: Apr 2003
Posts: 4,192
Thanks: 50
Thanked 37 Times in 36 Posts
Rep Power: 14
knothead has a spectacular aura about knothead has a spectacular aura about knothead has a spectacular aura about
Quote:
Originally Posted by ulferlingsson View Post
This thread is a little bit odd because it does not discuss when, where, why. I mean, it is like asking, "Is it better to weld or to use bolts?" It depends, doesn't it?

Soldering is excellent for small things, light things, and if done in a well controlled manner. Most bad soldering joints are probably the result of working with inferior equipment, in the field, and without proper training. Dirty connectors, cold solder, etc.

For heavy gauge wire, soldering should not be used. For AWG 20 or finer, with a temperature controlled iron, it is excellent - if heat shrink tubing is applied well outside the joint on both sides, for strain relief. Or use two layers, it's not that expensive!

My God Man!! Do you have any idea what you've just done?
Reply With Quote Share with Facebook
  #230  
Old 06-16-2010
Member
 
Join Date: Jun 2010
Location: Miami, Florida
Posts: 97
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 5
ulferlingsson is on a distinguished road
Yes, expressed my opinion. But why do you call me God?
__________________
Ensenada 20, 1972

Last edited by ulferlingsson; 06-16-2010 at 07:12 PM. Reason: forgot smiley ;)
Reply With Quote Share with Facebook
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools

 
Posting Rules
You may post new threads
You may post replies
You may post attachments
You may edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Advice, please on crimping wire connections... FrankLanger Gear & Maintenance 67 10-09-2012 07:22 AM
Rope Cutting Tip for Weller 8200 Soldering Gun? SEMIJim Gear & Maintenance 6 11-18-2007 10:17 AM
Turnbuckles - Stainless versus Aluminum Finallybuyingaboat Gear & Maintenance 9 10-05-2007 09:47 PM
da versus high tech sailon2win Racing 5 10-05-2004 04:07 AM
Power versus Sail Tom Wood Cruising Articles 0 12-23-2000 07:00 PM