A/C freezing up

My air conditioner froze up last weekend. It is a Mermaid 16,500 BTU unit with reverse cycle heat. The thermostat was replaced in February by the PO and they used a household type thermostat from Home Depot. They claimed the local A/C repair guy suggested this as a fix. I should mention here that the thermostat was replaced because the heat would not cycle on during the survey so this thermostat was installed and the heat worked. I was on the boat last October and the A/C worked great.

Is it possible that the new thermostat was connected incorrectly and that is the causing the unit to run until it freezes? I don't have the instructions so I am unable to double check the connections that way. Are there some other troubleshooting steps that I can complete before getting the HVAC guy to come out and take a look at it? The closest one is in Austin and charges mileage to come out to our lake.

Again, thanks for your assistance in advance
Bill

s/v Lucky
Catalina 36
Texas
wfahey is offline  
Quote Quick Reply Share with Facebook
Sponsored Links
Advertisement
 
post #2 of 11 Old 04-08-2008
Senior Member
 
pigslo's Avatar
 
Join Date: Nov 2004
Posts: 804
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 11
 
My recolection is that when an a/c freezes up, the system is low on freon.
pigslo
pigslo is offline  
Quote Quick Reply Share with Facebook
post #3 of 11 Old 04-09-2008
Telstar 28
 
sailingdog's Avatar
 
Join Date: Mar 2006
Location: New England
Posts: 43,290
Thanks: 0
Thanked 15 Times in 12 Posts
Rep Power: 14
         
Believe Pigslo may be correct. Basically, there are two reasons an A/C unit will freeze up. One is low on refrigerant--technically not Freon any more, but what do you expect from a pig. The other is if the air flow over the coils isn't sufficient...which is usually caused by a bad fan. I doubt it is caused by the thermostat installation, unless the thermostat is responsible for controlling the fan in the A/C system (which is very unlikely).

BTW, have you checked the duct work and filters to see if they're clear? Obstructions in the duct work or filters can reduce the airflow enough to cause the freezing problem, especially in a very humid environment of a boat.

Two websites you might want to read LINK LINK2

Sailingdog

To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.

Telstar 28
New England

You know what the first rule of sailing is? ...Love. You can learn all the math in the 'verse, but you take
a boat to the sea you don't love, she'll shake you off just as sure as the turning of the worlds. Love keeps
her going when she oughta fall down, tells you she's hurting 'fore she keens. Makes her a home.

—Cpt. Mal Reynolds, Serenity (edited)

If you're new to the Sailnet Forums... please read this
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
.

Still—DON'T READ THAT POST AGAIN.
sailingdog is offline  
Quote Quick Reply Share with Facebook
post #4 of 11 Old 04-09-2008
Best Looking MALE Mod
 
Cruisingdad's Avatar
 
Join Date: Jul 2006
Location: Washington State
Posts: 9,917
Thanks: 3
Thanked 124 Times in 57 Posts
Rep Power: 10
     
As has been said before, low freon (99% chance) or low fan speed.

Steps:

1) When you turn it on, do you hear the compressor kick on? Note, this is the compressor... not fan. The compressor kicks on and makes a deep hum... If so...

2) Are you making water? If so...

3) Are you moving good air? If so...

4) (assuming it is defrosted), are you making COLD air? Not cool, COLD? The answer to this is most likely no. If it is low on freon it will move cool air and slowly freeze up at the coils, or will not move any cool air, or the compressor will not kick on at all. Most compressors will not run if they are real low on freon, but will run if moderately low on freon.

Honestly, I have only had a unit shut down because of not moving enough air once. If it is a low fan speed issue, you will make very cold air... just not move enough across the coils and it takes a while for it to shut down. Any time I have ever seen or heard of a unit shutting down outside of that it was because of low freon... and have NEVER EVEN HEARD of a unit freezing up because of a bad thermostat. Either you were sold a bag of goods or I learnerd that a thermostat can freeze up your coils??? I don't see how, honestly. Most units have a max 55 degree low setting and that is a long way from 32 (assuming you could ever even hit 55).

Refilling with refrigerant will require a tech that is licensed. Sorry. I am not sure you could do it yourself. I do not think you can even buy refrigerant unless licenesed.

Another point... why are you low on refrigerant? Have a leak (most likely)? As such, you will have to track that down. Most techs will not keep filling refrigerant. The first time assumes it might be a very slow leak and you will probably get it filled. The second time, they will want to track it down, IMO.

- CD

PS My disclaimer: I am NOT a licensesd marine ac mechanic. I have done a lot of my own work. My father in law is licensed (home) so I do a lot of work with him. THis is what I have learned, so take my advice as such.

Sailnet Moderator



1987 Tayana Vancouver 42, Credendo Vides, (Mom and Pops boat, F/T Mobile Live Aboards in Puget Sound)

My Website:
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


Follow My Blog at:
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


Follow me on Facebook:

To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
Cruisingdad is offline  
Quote Quick Reply Share with Facebook
post #5 of 11 Old 04-09-2008
Member
 
Join Date: Feb 2008
Posts: 30
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 0
 
Not knowing a whole lot on this issue, but once at a motel, the window unit was freezing up. We noticed that 80% of the radiator fins had been bent over thus restricting air flow. We spent quite a while straightening these out and were able to improve the cooling ability.
Stu01 is offline  
Quote Quick Reply Share with Facebook
post #6 of 11 Old 04-09-2008
Best Looking MALE Mod
 
Cruisingdad's Avatar
 
Join Date: Jul 2006
Location: Washington State
Posts: 9,917
Thanks: 3
Thanked 124 Times in 57 Posts
Rep Power: 10
     
Quote:
Originally Posted by Stu01 View Post
Not knowing a whole lot on this issue, but once at a motel, the window unit was freezing up. We noticed that 80% of the radiator fins had been bent over thus restricting air flow. We spent quite a while straightening these out and were able to improve the cooling ability.
These units use water to remove the heat, not air. Without water movement, you will get a high head pressure within moments. THis is often shown as a PS (looks like P5) on the display for Cruiseair. I would assume Mermaid has a similar readout for high head pressure. Different animal than air exchanged units (window units).

- CD

Sailnet Moderator



1987 Tayana Vancouver 42, Credendo Vides, (Mom and Pops boat, F/T Mobile Live Aboards in Puget Sound)

My Website:
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


Follow My Blog at:
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


Follow me on Facebook:

To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
Cruisingdad is offline  
Quote Quick Reply Share with Facebook
post #7 of 11 Old 04-09-2008
Member
 
Join Date: Feb 2008
Posts: 30
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 0
 
CD,
I would PM you to thank you for the clarification/education but I need some more posts. One less now!
Stu
Stu01 is offline  
Quote Quick Reply Share with Facebook
post #8 of 11 Old 04-09-2008
Junior Member
 
Join Date: Aug 2006
Posts: 8
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 0
 
Let me add my two cents. I have noticed that the systems can become less efficient which can lead to freeze up when the coils get dirty. Living in FL, the high humidity will make your boat damp if you are not running the AC all the time or have a dehumidifier. I clean my coils twice a year with a spray solvent I get from local AC suppliers. After flushing I spray the coils with an anti-fungus spray. I also get that from local AC suppliers. With the growing popularity of people cleaning their home ductwork, these products may be obtainable from Lowe’s or Home Depot.

Another test for Freon is to check the temp across the coil when running. You can get the thermometers at Home Depot or where ever. From what I understand, a home system will pull about 10 degrees difference between the intake and the exhaust side of the coil. I have been told a boat AC will pull between 15 and 20 degrees difference. Going either side can mean either to little or too much Freon. I was also told that Freon will be phased out of marine AC units in the next 10 years. I just replace a 16k BTU Cruise Air and was told that by the tech. I defer to anyone with more knowledge to add or subtract form this.
nightwatch is offline  
Quote Quick Reply Share with Facebook
post #9 of 11 Old 04-09-2008
Member
 
Join Date: May 2005
Posts: 46
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 0
 
I occasionally have a freeze up problem with my Mermaid A/C. But it's not due to any of the above described problems. I replaced my old unit with a slightly larger one by Mermaid. If you read the owners manual, it describes the amount of vents you need to properly ventilate the area. If you don't have enough vents, then the cold air can't get out and thus backs up causing the unit to freeze. So the answer from Mermaid is to set the thermostat a couple of degrees warmer so the compressor won't run as long and thus get rid of the cold air it needs to function correctly. Sounds corny, but it's in the owners manual how many vents you should have.
Another solution depends on the vents you have. On the unit with the freezing problem, the vent blows straight up. Someday, I'll replace it with a 45 degree vent that blows outward. That should help air flow blow away from the vent and dissipate better.
Scott


Below is what the Mermaid site says. Look at the last section:

Air Conditioners Evaporator is Freezing

While the marine air conditioner is running, the evaporator is freezing. This device looks like a radiator or a car.

Supply air vents closed or insufficient number of vents. Open and/or add additional vents.
Fan not running or intermittent.
Return air blocked. Clean air filter and/or remove any blockage.
Thermostat set too low and is not allowing unit to cycle and remove icing. Set thermostat at a higher setting.
Thermostat improperly located in a position not giving "true" cabin temperature. Examples would be in a sunny spot near glass, or near the hatch. Relocate thermostat.
Low freon due to leak. Unit will require professional service.
NOTE: The most common of this problem is insufficient ventilation coming off the unit. Additional vents are needed or "cleaning" the existing ducting scheme to ensure better airflow off the system. Remember, the more vents the better on ANY unit. Each unit has minumum vent requirements, review your product under Marine Air Conditioners if needed.

Last edited by Schuckerman; 04-09-2008 at 02:52 PM.
Schuckerman is offline  
Quote Quick Reply Share with Facebook
post #10 of 11 Old 04-10-2008
Senior Member
 
HerbDB's Avatar
 
Join Date: Sep 2000
Location: Eastern Pennsylvania
Posts: 203
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 15
 
I just had a similar problem. If you do not have sufficient water flow, and are using the unit for heat, the compressor will ice up because it cannot disperse the cold it is collecting. My unit does not auto shut down in this situation.

It will auto shut down if it is overheating because I am asking it to cool down and it is collecting heat that it can not disperse.

Overheat = shutdown, Overcold = Iced up

My pump had an air block (they are not self priming) and once cleared all was well. Check the unit for adequate water flow ie. pump, thru hull, raw water filter, etc. May save you a service call.

Herb DuBois
Beneteau 36CC
Split Decision
HerbDB is offline  
Quote Quick Reply Share with Facebook
Reply

Quick Reply
Message:
Options

By choosing to post the reply above you agree to the rules you agreed to when joining Sailnet.
Click Here to view those rules.

Register Now



In order to be able to post messages on the SailNet Community forums, you must first register.
Please enter your desired user name, your email address and other required details in the form below.
Please note: After entering 3 characters a list of Usernames already in use will appear and the list will disappear once a valid Username is entered.


User Name:
Password
Please enter a password for your user account. Note that passwords are case-sensitive.

Password:


Confirm Password:
Email Address
Please enter a valid email address for yourself.

Email Address:
OR

Log-in









Human Verification

In order to verify that you are a human and not a spam bot, please enter the answer into the following box below based on the instructions contained in the graphic.




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Show Printable Version Show Printable Version
Email this Page Email this Page



Similar Threads
Thread Thread Starter Forum Replies Last Post
Lost my A/C Power mathislaw1 Gear & Maintenance 12 07-17-2007 11:28 AM
Need to run a/c mooring, no gen? acmecoyote Gear & Maintenance 4 11-19-2002 03:21 PM
A/C on the high seas acmecoyote General Discussion (sailing related) 4 10-26-2002 03:28 PM
Inboard motors in Freezing Weather hunter87 Gear & Maintenance 0 12-31-2000 04:37 PM

Posting Rules  
You may post new threads
You may post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On
Trackbacks are On
Pingbacks are On
Refbacks are On

 
For the best viewing experience please update your browser to Google Chrome