Adler Barbour Troubleshooting (LED Flash)

I have an Adler Barbour SuperColdMachine of unknown age in a 1985 model Endeavour Sailboat. As of about a month ago, it's cooling ability greatly diminished and then appeared to be non working at all. I turned the fridge off for about 1 week, then turned it back on. It worked at 100% for a few days, maybe a week, then returned to not working. I attempted to trouble shoot it using the flashing LED(which flashes 3 times). According to the manual, this is a situation where the compressor rotor is physically blocked OR a high pressure condition exists that is preventing the motor from starting up. There is around 12vdc reaching the unit(I checked), so that is not a problem. Do yall think this is fixable or should I start shopping?

By the way, I have installed a portable 14 Q Engel Deep Freeze for my meat products with a min/max thermometer. I LOVE this unit and would highly recommend it.

John Pate
Highport Marina ZD27
aboard S/V Fort Awesome III
"I couldn't do the things the way those people do.
I couldn't live there if you paid me to. "
The Talking Heads
FortAwesomeIII is offline  
Quote Quick Reply Share with Facebook
Sponsored Links
Advertisement
 
post #2 of 17 Old 05-15-2008
moderate?
 
camaraderie's Avatar
 
Join Date: May 2002
Location: East Coast
Posts: 13,877
Thanks: 0
Thanked 3 Times in 3 Posts
Rep Power: 16
     
Probably worth the $100 bucks for a checkout before you spend the bucks for a new one. Have you checked all fuses on the compressor?

No longer posting. Reach me by PM!
camaraderie is offline  
Quote Quick Reply Share with Facebook
post #3 of 17 Old 05-15-2008 Thread Starter
Junior Member
 
FortAwesomeIII's Avatar
 
Join Date: Jul 2007
Location: Pottsboro, Texas
Posts: 20
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 0
 
Yes, I believe I have. However, the unit is mounted in such a way that I can't see(just feel) the terminal connection side of the unit. I really cant even see the LED, just the reflection of it flashing. I will have to remove my sink and some plumbing to extract the unit or gain access to the terminal/fuse side.

What do they do when they check it? Refrigerant test and such?

John Pate
Highport Marina ZD27
aboard S/V Fort Awesome III
"I couldn't do the things the way those people do.
I couldn't live there if you paid me to. "
The Talking Heads
FortAwesomeIII is offline  
Quote Quick Reply Share with Facebook
post #4 of 17 Old 05-15-2008
moderate?
 
camaraderie's Avatar
 
Join Date: May 2002
Location: East Coast
Posts: 13,877
Thanks: 0
Thanked 3 Times in 3 Posts
Rep Power: 16
     
They will generally check refrigerant levels and electrical connections both to the unit and on the terminal block. They may also use a sniffer for leaks. It could be something as simple as a loose wire from vibration over time...or a blown compressor.

No longer posting. Reach me by PM!
camaraderie is offline  
Quote Quick Reply Share with Facebook
post #5 of 17 Old 05-15-2008
Senior Member
 
denby's Avatar
 
Join Date: Feb 2007
Location: Dead Sea, some times called Long Island Sound
Posts: 2,527
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 12
       
Quote:
Originally Posted by camaraderie View Post
They will generally check refrigerant levels and electrical connections both to the unit and on the terminal block. They may also use a sniffer for leaks. It could be something as simple as a loose wire from vibration over time...or a blown compressor.
If he is getting cooling for a day or so the compressor should be ok and the refrigerant level should be ok. What type of condensor is used, air cooled or water cooled? I would look for a bad electrical connection.

Dennis
O'Day 302

To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.

Be careful or i will do what the voices tell me to do
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


To get the most from Sailnet, follow the link in
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
's signature.
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.

Hey stuffit "Get a life"
denby is offline  
Quote Quick Reply Share with Facebook
post #6 of 17 Old 05-15-2008
moderate?
 
camaraderie's Avatar
 
Join Date: May 2002
Location: East Coast
Posts: 13,877
Thanks: 0
Thanked 3 Times in 3 Posts
Rep Power: 16
     
Den...I was thinking more of a compressor that would run till hot then shut down when I said "blown"...more in the not fixable than not running at all category. I am thinking low coolant or slow leak...whether fixable or not...unknown.

No longer posting. Reach me by PM!
camaraderie is offline  
Quote Quick Reply Share with Facebook
post #7 of 17 Old 05-15-2008
Senior Member
 
denby's Avatar
 
Join Date: Feb 2007
Location: Dead Sea, some times called Long Island Sound
Posts: 2,527
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 12
       
Cam,

I'm looking at it's ability to cool back down again for a few days or a week. That leads me to think the refrigerant and compressor are ok. So there may be a problem with a dirty or corroded electrical connection, compressor drawing more amps. Or a condenser problem , a dirty air cooled condenser or if water cooled a corroded, partially blocked condenser or water pump problem. A slim chance of a low side leak that let in some moisture and the capillary tube gets blocked do to ice, but after being off for a week the system should show signs of being short of gas.

Dennis
O'Day 302

To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.

Be careful or i will do what the voices tell me to do
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


To get the most from Sailnet, follow the link in
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
's signature.
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.

Hey stuffit "Get a life"
denby is offline  
Quote Quick Reply Share with Facebook
post #8 of 17 Old 05-15-2008
Senior Member
 
denby's Avatar
 
Join Date: Feb 2007
Location: Dead Sea, some times called Long Island Sound
Posts: 2,527
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 12
       
He did say under the sink, so that should be an air cooled unit, right?

Dennis
O'Day 302

To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.

Be careful or i will do what the voices tell me to do
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


To get the most from Sailnet, follow the link in
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
's signature.
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.

Hey stuffit "Get a life"
denby is offline  
Quote Quick Reply Share with Facebook
post #9 of 17 Old 05-15-2008
Junior Member
 
Join Date: Nov 2007
Location: Katy, TX
Posts: 9
Thanks: 0
Thanked 1 Time in 1 Post
Rep Power: 0
 
Check the condenser coils

I have had similer problems with one that was installed in a boat I bought about 3 years ago and it was due to lack of ventilation. You may want to check that the condenser coils aren't clogged with dust or dirt, which could overheat the compressor after contunuous running.
donhallmon is offline  
Quote Quick Reply Share with Facebook
post #10 of 17 Old 05-16-2008
Senior Member
 
trantor12020's Avatar
 
Join Date: Mar 2006
Location: Singapore
Posts: 699
Thanks: 4
Thanked 10 Times in 10 Posts
Rep Power: 10
 
you have a supercold machine, is that raw water cool ?
if yes, any fouling of the cooling circuit ?

Ken
2002 Hunter 326, SV Millennium 2
1999 Macgregor 26X, SV Millennium
trantor12020 is offline  
Quote Quick Reply Share with Facebook
Reply

Quick Reply
Message:
Options

Register Now



In order to be able to post messages on the SailNet Community forums, you must first register.
Please enter your desired user name, your email address and other required details in the form below.
Please note: After entering 3 characters a list of Usernames already in use will appear and the list will disappear once a valid Username is entered.


User Name:
Password
Please enter a password for your user account. Note that passwords are case-sensitive.

Password:


Confirm Password:
Email Address
Please enter a valid email address for yourself.

Email Address:
OR

Log-in









Human Verification

In order to verify that you are a human and not a spam bot, please enter the answer into the following box below based on the instructions contained in the graphic.




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Show Printable Version Show Printable Version
Email this Page Email this Page



Similar Threads
Thread Thread Starter Forum Replies Last Post
LEDs afloat GoodOldBoat Good Old Boat 56 12-19-2014 01:23 PM
Adler Barbour refrigeration Fro36 Catalina 10 08-13-2010 08:42 AM
Adler Barbour maintenance ZapataII Gear & Maintenance 5 05-07-2008 12:01 PM
Charging an Adler Barbour Refrigerator maxheadspace Gear & Maintenance 6 10-16-2007 07:46 PM

Posting Rules  
You may post new threads
You may post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On
Trackbacks are On
Pingbacks are On
Refbacks are On

 
For the best viewing experience please update your browser to Google Chrome