Thirty-amp connectors are a perennial problem in marinas. I've seen many failures and meltdowns over the past couple of decades. Many of these could be traced to "user failure", i.e., overtaxing the connectors by overloading them, not cleaning them, not keeping them dry, etc., etc.

The sad truth, however, is that we're now seeing FAR TOO MANY failures of 30A Marinco connectors to believe that its always "user failure".

First, the design stinks: these things cannot handle anywhere near 30A continuous power, without heating and burning.

Yes, do everything possible to keep contacts clean and dry, and try to limit power draw to not more than 25A or so. That will help.

But, bottom line, IMHO these connectors are real crap. Be very wary of them....i.e., ALL 30A connectors....but, especially, those recently coming out of Marinco. These seem to be substandard in construction.

Is this really the best we can do?

Bill
btrayfors is offline  
Quote Quick Reply Share with Facebook
Sponsored Links
Advertisement
 
post #12 of 91 Old 09-10-2008
Senior Member
 
Join Date: May 2007
Posts: 551
Thanks: 3
Thanked 3 Times in 3 Posts
Rep Power: 9
 
Are you getting a full 120 volts? If the marina is providing less, that could cause the problem too.

The cords may be crap - I have no way of knowing for sure. I'm just trying to mention thing that you have some control over.
SteveInMD is offline  
Quote Quick Reply Share with Facebook
post #13 of 91 Old 09-10-2008
Senior Member
 
ebs001's Avatar
 
Join Date: May 2006
Location: Ottawa, Canada
Posts: 2,205
Thanks: 6
Thanked 21 Times in 19 Posts
Rep Power: 10
 
CD, I have had the same problem. Has it been the same slot on the receptacle end in both your failures? I have a feeling that all the failures are on the same slot and that this is a result of not completely turning the plug before tightening the holding ring and because of the configuration of the blades full contact is not made. If this is the case it is neither corrosion nor poor workmsship that are the cause of the failure.
ebs001 is offline  
Quote Quick Reply Share with Facebook
post #14 of 91 Old 09-10-2008 Thread Starter
Best Looking MALE Mod
 
Cruisingdad's Avatar
 
Join Date: Jul 2006
Location: Washington State
Posts: 9,917
Thanks: 3
Thanked 123 Times in 57 Posts
Rep Power: 10
     
Quote:
Originally Posted by SteveInMD View Post
Are you getting a full 120 volts? If the marina is providing less, that could cause the problem too.

The cords may be crap - I have no way of knowing for sure. I'm just trying to mention thing that you have some control over.
I had already thought of that too.

Yes, on a normal day, we are getting good power. The question is whether it stays good?? That, without putting it on a meter/printout, I cannot know. But the problems associated here are not solely out of my marina which leads me to believe that, unless highly coincidental, it is not the major problem.

- CD

Sailnet Moderator



1987 Tayana Vancouver 42, Credendo Vides, (Mom and Pops boat, F/T Mobile Live Aboards in Puget Sound)

My Website:
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


Follow My Blog at:
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


Follow me on Facebook:

To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
Cruisingdad is offline  
Quote Quick Reply Share with Facebook
post #15 of 91 Old 09-10-2008 Thread Starter
Best Looking MALE Mod
 
Cruisingdad's Avatar
 
Join Date: Jul 2006
Location: Washington State
Posts: 9,917
Thanks: 3
Thanked 123 Times in 57 Posts
Rep Power: 10
     
Quote:
Originally Posted by ebs001 View Post
CD, I have had the same problem. Has it been the same slot on the receptacle end in both your failures? I have a feeling that all the failures are on the same slot and that this is a result of not completely turning the plug before tightening the holding ring and because of the configuration of the blades full contact is not made. If this is the case it is neither corrosion nor poor workmsship that are the cause of the failure.
I am not sure about that. I would have to check.

- CD

Sailnet Moderator



1987 Tayana Vancouver 42, Credendo Vides, (Mom and Pops boat, F/T Mobile Live Aboards in Puget Sound)

My Website:
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


Follow My Blog at:
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


Follow me on Facebook:

To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
Cruisingdad is offline  
Quote Quick Reply Share with Facebook
post #16 of 91 Old 09-10-2008 Thread Starter
Best Looking MALE Mod
 
Cruisingdad's Avatar
 
Join Date: Jul 2006
Location: Washington State
Posts: 9,917
Thanks: 3
Thanked 123 Times in 57 Posts
Rep Power: 10
     
Quote:
Originally Posted by btrayfors View Post
Thirty-amp connectors are a perennial problem in marinas. I've seen many failures and meltdowns over the past couple of decades. Many of these could be traced to "user failure", i.e., overtaxing the connectors by overloading them, not cleaning them, not keeping them dry, etc., etc.

The sad truth, however, is that we're now seeing FAR TOO MANY failures of 30A Marinco connectors to believe that its always "user failure".

First, the design stinks: these things cannot handle anywhere near 30A continuous power, without heating and burning.

Yes, do everything possible to keep contacts clean and dry, and try to limit power draw to not more than 25A or so. That will help.

But, bottom line, IMHO these connectors are real crap. Be very wary of them....i.e., ALL 30A connectors....but, especially, those recently coming out of Marinco. These seem to be substandard in construction.

Is this really the best we can do?

Bill
Hi Bill... how are you?

Thanks for the input. Yes, I think I agree with you. But you would think (using the 20% rule), they would over size their cords/connectors for continuous operation at 30 instead of 80% of 30A. I wonder if that is not the case?

- CD

Sailnet Moderator



1987 Tayana Vancouver 42, Credendo Vides, (Mom and Pops boat, F/T Mobile Live Aboards in Puget Sound)

My Website:
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


Follow My Blog at:
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


Follow me on Facebook:

To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
Cruisingdad is offline  
Quote Quick Reply Share with Facebook
post #17 of 91 Old 09-10-2008
Seinor Member
 
capn_dave's Avatar
 
Join Date: Feb 2000
Location: Green Cove Springs, FL
Posts: 276
Thanks: 0
Thanked 1 Time in 1 Post
Rep Power: 16
 
Cool I have seen it also

On most cases at our marina, the plastic ring that is supposed to hold the connectors tight is broken or was not used. The twist lock function of the plug itself will not hold the plug in.
Insurance companies are checking this when there is a claim.
That plastic ring breaks easily when dropped, and I don't think it can be replaced, so you have to buy a new shore power cable.
Hummmmmm! could this be on purpose?

Fair Winds

Cap'n Dave
capn_dave is offline  
Quote Quick Reply Share with Facebook
post #18 of 91 Old 09-10-2008
Senior Member
 
ebs001's Avatar
 
Join Date: May 2006
Location: Ottawa, Canada
Posts: 2,205
Thanks: 6
Thanked 21 Times in 19 Posts
Rep Power: 10
 
I think you will find that it is always the same slot. It would therefore appear to be a design flaw in their female cap. I do not recall seeing this problem anywhere else, so it may be more of a problem with Marinco. I do know that by insuring to turn the female cap to the lock position and tightening the locking screw ring it doesn't heat up. Note that once heating starts the contacts produce their own resistance furthering the heat build up so periodic cleaning will help. My feeling is that there should be a positve feeling of locking the plug in postion and I certainly don't feel that. Next time I'm in Home Depot I'm going to check other manufacturers male and female cap connections.
ebs001 is offline  
Quote Quick Reply Share with Facebook
post #19 of 91 Old 09-10-2008
moderate?
 
camaraderie's Avatar
 
Join Date: May 2002
Location: East Coast
Posts: 13,877
Thanks: 0
Thanked 3 Times in 3 Posts
Rep Power: 16
     
I am dealing with different cordsets every day...maybe a few hundred each year and would say that the majority of cordsets have similar burning to what is shown. I would guess that 90% of the cordsets are marinco since it is what is generally available and sold at the major boating stores. I rarely see any burning on 50amp sets and I have always attributed it to the much more robust contact and locking mechanism. I think the 30a plug/receptacle design is flawed regardless of the manufacturer...but how do you change a "standard"??

No longer posting. Reach me by PM!
camaraderie is offline  
Quote Quick Reply Share with Facebook
post #20 of 91 Old 09-10-2008
Telstar 28
 
sailingdog's Avatar
 
Join Date: Mar 2006
Location: New England
Posts: 43,290
Thanks: 0
Thanked 14 Times in 12 Posts
Rep Power: 14
         
It is pretty tough to change a standard without overwhelming proof that a newer standard would have significant benefits...
Quote:
Originally Posted by camaraderie View Post
I am dealing with different cordsets every day...maybe a few hundred each year and would say that the majority of cordsets have similar burning to what is shown. I would guess that 90% of the cordsets are marinco since it is what is generally available and sold at the major boating stores. I rarely see any burning on 50amp sets and I have always attributed it to the much more robust contact and locking mechanism. I think the 30a plug/receptacle design is flawed regardless of the manufacturer...but how do you change a "standard"??

Sailingdog

To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.

Telstar 28
New England

You know what the first rule of sailing is? ...Love. You can learn all the math in the 'verse, but you take
a boat to the sea you don't love, she'll shake you off just as sure as the turning of the worlds. Love keeps
her going when she oughta fall down, tells you she's hurting 'fore she keens. Makes her a home.

—Cpt. Mal Reynolds, Serenity (edited)

If you're new to the Sailnet Forums... please read this
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
.

Still—DON'T READ THAT POST AGAIN.
sailingdog is offline  
Quote Quick Reply Share with Facebook
Reply

Quick Reply
Message:
Options

Register Now



In order to be able to post messages on the SailNet Community forums, you must first register.
Please enter your desired user name, your email address and other required details in the form below.
Please note: After entering 3 characters a list of Usernames already in use will appear and the list will disappear once a valid Username is entered.


User Name:
Password
Please enter a password for your user account. Note that passwords are case-sensitive.

Password:


Confirm Password:
Email Address
Please enter a valid email address for yourself.

Email Address:
OR

Log-in









Human Verification

In order to verify that you are a human and not a spam bot, please enter the answer into the following box below based on the instructions contained in the graphic.




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Show Printable Version Show Printable Version
Email this Page Email this Page



Similar Threads
Thread Thread Starter Forum Replies Last Post
Charging with Solar Power Kevin Jeffrey Gear and Maintenance Articles 0 07-28-2003 08:00 PM
Electrical Power on Board Kevin Jeffrey Gear and Maintenance Articles 0 02-11-2003 07:00 PM
Electrical Power on Board Kevin Jeffrey Her Sailnet Articles 0 02-11-2003 07:00 PM
Boat Battery Power East Penn Manufr. Gear and Maintenance Articles 0 01-18-1999 07:00 PM

Posting Rules  
You may post new threads
You may post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On
Trackbacks are On
Pingbacks are On
Refbacks are On

 
For the best viewing experience please update your browser to Google Chrome