If you routinely connect/disconnect with the power on, internal arching inevitably can occur causing the burn marks in your picture. As you can imagine, the instantaneous connection/disconnect, particularly if the conenctor pins are dirty, can arch. I don't know if you do this but I've seen many people do it and, correctly or not, I attributed their failed connectors to that process.
It's always a good habit to first shut down the breaker before disconnecting.
Reply With Quote Share with Facebook
  #22  
Old 09-10-2008
JohnRPollard's Avatar
Moderator
 
Join Date: Mar 2007
Location: Chesapeake
Posts: 5,680
Thanks: 0
Thanked 2 Times in 2 Posts
Rep Power: 10
JohnRPollard is a jewel in the rough JohnRPollard is a jewel in the rough JohnRPollard is a jewel in the rough
Quote:
Originally Posted by k1vsk View Post
If you routinely connect/disconnect with the power on, internal arching inevitably can occur causing the burn marks in your picture. As you can imagine, the instantaneous connection/disconnect, particularly if the conenctor pins are dirty, can arch. I don't know if you do this but I've seen many people do it and, correctly or not, I attributed their failed connectors to that process.
It's always a good habit to first shut down the breaker before disconnecting.
K1,

When you say "shut down the breaker", are you referring to the shore power breaker in the boat, or out on the dock? I always shut down the breaker in the boat, but have never shut down the breaker at the dock. In all honestly, it never occurred to me that I should do that...
__________________

To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.

Pacific Seacraft Crealock 31 #62

NEVER CALLS CRUISINGDAD BACK....CAN"T TAKE THE ACCENT
Reply With Quote Share with Facebook
  #23  
Old 09-10-2008
Senior Member
 
Join Date: Jul 2001
Posts: 1,174
Thanks: 0
Thanked 1 Time in 1 Post
Rep Power: 14
k1vsk will become famous soon enough
Quote:
Originally Posted by JohnRPollard View Post
K1,

When you say "shut down the breaker", are you referring to the shore power breaker in the boat, or out on the dock? I always shut down the breaker in the boat, but have never shut down the breaker at the dock. In all honestly, it never occurred to me that I should do that...

I was referring to the breaker on the dock - the supply breaker
Reply With Quote Share with Facebook
  #24  
Old 09-10-2008
JohnRPollard's Avatar
Moderator
 
Join Date: Mar 2007
Location: Chesapeake
Posts: 5,680
Thanks: 0
Thanked 2 Times in 2 Posts
Rep Power: 10
JohnRPollard is a jewel in the rough JohnRPollard is a jewel in the rough JohnRPollard is a jewel in the rough
Quote:
Originally Posted by k1vsk View Post
I was referring to the breaker on the dock - the supply breaker
Roger that. Thanks, I'll add it to our routine.
__________________

To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.

Pacific Seacraft Crealock 31 #62

NEVER CALLS CRUISINGDAD BACK....CAN"T TAKE THE ACCENT
Reply With Quote Share with Facebook
  #25  
Old 09-10-2008
Junior Member
 
Join Date: Sep 2008
Posts: 6
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 0
Sreya is on a distinguished road
Marinco power cables

I too had one go like that and I wondered if I had been neggligent in making sure that the twist-lock was all the way over and then tightened the retainer ring.
It is easy to become non chalant about some of these things
A thought
George
Reply With Quote Share with Facebook
  #26  
Old 09-10-2008
camaraderie's Avatar
moderate?
 
Join Date: May 2002
Location: East Coast
Posts: 13,878
Thanks: 0
Thanked 2 Times in 2 Posts
Rep Power: 15
camaraderie is a jewel in the rough camaraderie is a jewel in the rough camaraderie is a jewel in the rough
Shutting down the dockside breaker is something I always do before plugging in a transient boat. Then I ask the captain if it is ok to turn it on.
Surprising how many look at me like they've never considered that question before!
__________________
No longer posting. Reach me by PM!
Reply With Quote Share with Facebook
  #27  
Old 09-10-2008
Senior Member
 
Join Date: Aug 2006
Location: wherever
Posts: 5,253
Thanks: 8
Thanked 16 Times in 15 Posts
Rep Power: 10
xort has a spectacular aura about xort has a spectacular aura about xort has a spectacular aura about
K1
Does it really matter if the breaker on shore is off... if the breaker at the boat is off and there is no flow of power?

I do think this is a combination of things.
Poor connection due to not twisting the connector on all the way.
Wiggling the cable and causing arcing.
Plugging and unplugging while power is flowing.
Salt & other stuff causing corrosion and poor connection.

This came up on another list and Hubbell was mentioned as using a different method of connecting the lugs to the wires. Sorry I don't recall the differences.

Rings can be forced on to the plugs, I've done it. I don't recall ever seeing a dockside recepticle with threads for screwing the ring to.
Reply With Quote Share with Facebook
  #28  
Old 09-11-2008
Senior Member
 
Join Date: May 2007
Posts: 547
Thanks: 3
Thanked 3 Times in 3 Posts
Rep Power: 8
SteveInMD is on a distinguished road
You are right that if the breaker on the boat is off there will be no current flow in the cord. However, I would turn off the dock side breaker before unplugging, just because working near salt water around a live 30 amp cord seem like a bad idea to me.

If you don't bother with turning off the main breaker on the boat either, you could get some arcing when you connect or disconnect.
Reply With Quote Share with Facebook
  #29  
Old 09-11-2008
Sapperwhite's Avatar
Not So Senior Member
 
Join Date: Oct 2006
Location: Maryland
Posts: 2,504
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 10
Sapperwhite has a spectacular aura about Sapperwhite has a spectacular aura about Sapperwhite has a spectacular aura about
Quote:
Originally Posted by k1vsk View Post
.....
It's always a good habit to first shut down the breaker before disconnecting.
Absolutly (dockside pedestal breaker). Aside from arcing when you plug a live cord into the boats receptical, there are personel safety issues here (as some others have noted). Anyone else ever concider they are holding a live line while standing near a whole lot of water? It is not the voltage that will kill you (well, not 120v), but the amperage. 30 amps, let alone 50 amps, is way more than enough to disrupt your hearts rhythm.

If you are holding the cord while wet or standing in water, and the electricity seeks ground through you, you can be injured or killed as it passes through your heart. Your skin does act like a faraday cage for your internals, but that can be overcome. Otherwise, everyone who ever got zapped with even low amps would go into cardiac arrest (which doesn't happen).

Long story short:
When coming in; breaker at the pedestal off and breaker onboard off, plug in on the boat, then plug in at pedestal, breaker on at the pedestal, then breaker on the boat on.
__________________
Dictated, but not read.
Reply With Quote Share with Facebook
  #30  
Old 09-11-2008
Senior Member
 
Join Date: Jul 2001
Posts: 1,174
Thanks: 0
Thanked 1 Time in 1 Post
Rep Power: 14
k1vsk will become famous soon enough
Quote:
Originally Posted by SteveInMD View Post
You are right that if the breaker on the boat is off there will be no current flow in the cord. .
WRONG!
We're not talking about current flowing on the cable. That has absolutely NOTHING to do with it.

The thread is about the cable ends arching thereby destroying the pins and the cable which occurs every time you connect/disconnect to a live plug..

If you don't believe me, do a simple experiment at home by plugging in a lamp (while shut off) to a socket slowly - you'll see the arch at the junction.

Believe it or not - your choice and I'm sure Marinco thanks you for not believing.
Reply With Quote Share with Facebook
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools

 
Posting Rules
You may post new threads
You may post replies
You may post attachments
You may edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Charging with Solar Power Kevin Jeffrey Gear and Maintenance Articles 0 07-28-2003 08:00 PM
Electrical Power on Board Kevin Jeffrey Gear and Maintenance Articles 0 02-11-2003 07:00 PM
Electrical Power on Board Kevin Jeffrey Her Sailnet Articles 0 02-11-2003 07:00 PM
Boat Battery Power East Penn Manufr. Gear and Maintenance Articles 0 01-18-1999 07:00 PM


All times are GMT -4. The time now is 09:42 AM.

Add to My Yahoo!         
Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2014, vBulletin Solutions, Inc.
SEO by vBSEO 3.6.1
(c) Marine.com LLC 2000-2012