heater recommendations

Back in 1992, I fitted a 3 kW Eberspacher forced air diesel heater. It has been reliable.

A long time, somebody warned me that although they will heat the boat, they will not dry the boat. They are right, and I have grown tired of it. You arrive with the boat damp, you start the heater, and 12 hours later you leave with the boat warm and damp, with condensaton just about everywhere. I have tried opening the hatches a wee bit to gain some air circulation, but it made little difference, and there is no point in opening all the hatches as the heat leaks out. I guess the problem is that the Eberspacher just re-cycles the boat's air, and does not draw in "new" air to aid the boat to dry.

So here comes the question. I have been on board a few ships that used a solid fuel heater, using charcoal. They certainly dry the boat, and very quickly. But, will a diesel heater operating on the same idea do the same job, namely, will it dry the boat? I dare not burn wood in a solid fuel heater, as there will be smoke a-plenty and I am not into that. I could go the charcoal route, perhaps even the diesel route with one of these, for example...

Newport Diesel Heater for boats.* Manufacturer: Dickinson Marine

.... but I have got to be sure it will dry the boat before I begin that installation.

This looks like another good one....

Welcome to SigMarine.com - Products - SIG-100


I have not got a great deal of space, but there is one place on the ship where it could go, as long as it will be effective when it does. It really must assist in drying the boat.

Thanks.


Rockter.

Last edited by Rockter; 01-25-2009 at 05:15 PM.
Rockter is offline  
Quote Quick Reply Share with Facebook
Sponsored Links
Advertisement
 
post #2 of 24 Old 01-25-2009
Moderator
 
JohnRPollard's Avatar
 
Join Date: Mar 2007
Location: Chesapeake
Posts: 5,680
Thanks: 0
Thanked 3 Times in 3 Posts
Rep Power: 10
     
Rockter,

That would probably be a pretty good solution, if diesel is what you want. I couldn't tell whether the combustion chamber on that unit is sealed from the boat, or whether it draws air for combustion from the interior of the boat?

We use something similar to what you linked, but ours is Dickinson's propane version of the Newport. What I like about ours is that we can see the flame (ambiance), yet the combustion chamber is sealed from the boat interior. Air for combustion is drawn in from outside the boat via a double-walled chimney. This also has the beneficial effect of insulating/cooling the chimney stack (exhaust is the interior portion), so it does not get quite so hot within the boat.

If you have propane aboard, it is a very clean fuel and is relatively easy to install. These heaters are very dry, because the exhaust from propane combustion does not enter the cabin at all. A little built-in fan helps to circulate the heat better, as do your regular cabin fans.

But I do not know if it will be better than what you have...


Not the best photo, but you can see ours here. We like it a lot:



To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.

Pacific Seacraft Crealock 31 #62

NEVER CALLS CRUISINGDAD BACK....CAN"T TAKE THE ACCENT
JohnRPollard is offline  
Quote Quick Reply Share with Facebook
post #3 of 24 Old 01-25-2009
the pointy end is the bow
 
erps's Avatar
 
Join Date: Aug 2006
Location: La Conner, Washington
Posts: 6,260
Thanks: 2
Thanked 27 Times in 26 Posts
Rep Power: 10
   
I've heard the same thing that John mentioned, is that the solid fuel type stoves, draw warmed moist air from inside the boat and send it up the chimney. We have the Dickinson Antartic stove and it seems to dry out the boat, although it doesn't heat it up very fast.


Ray
S.V. Nikko
1983 Fraser 41
La Conner, WA


To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


Boating for over 25 years, some of them successfully.
erps is offline  
Quote Quick Reply Share with Facebook
post #4 of 24 Old 01-25-2009 Thread Starter
Senior Member
 
Join Date: Sep 2006
Location: Scotland
Posts: 2,364
Thanks: 0
Thanked 11 Times in 11 Posts
Rep Power: 9
 
Guys :

Thanks.

If it doesn't draw cabin air for combustion, then it will, I fear, be little better than the Eberspacher, which has itself, a separate combustion cycle. The exhaust for the Ebespacher is also separate, and does not enter the cabin.

I think the heater must draw on cabin air, or there is no through-put up the chimney, and that boat is not going to dry. With the Eberspacher running, condensation is dripping everywhere, not because the heater is adding water vapour from the combustion, but because the heater simply heats it up and it hits the colder walls.

Given 12 hours of that, the walls and portlights are soaked. It was -5 degC outside, and about +16 degC inside, but still the condensation persisted, and steadily worsened.

Does anyone have a heater that draws on the cabin air? Does it dry the boat? I don't mean just heats the boat, but dries it?
Rockter is offline  
Quote Quick Reply Share with Facebook
post #5 of 24 Old 01-25-2009
Moderator
 
JohnRPollard's Avatar
 
Join Date: Mar 2007
Location: Chesapeake
Posts: 5,680
Thanks: 0
Thanked 3 Times in 3 Posts
Rep Power: 10
     
Rockter,

Drawing air for combustion from the exterior of the boat has always been a desirable feature from my perspective. In fact, the units that don't do this usually are equipped with an oxygen depletion sensor, which to my mind is worrisome.

I do wonder a bit about your scenario. If the ambient air is damp, and the heater unit draws air from within the cabin for combustion, isn't that air going to need to be replaced by more damp ambient air, from outside the cabin? In which case, you will always need to keep a hatch cracked, which in turn will mean a cold draft, which in turn means less efficient heating, and more of the damp ambient air circulating through in the cabin.

Our heater seems to dry the cabin, anyway. Maybe all it's doing is warming the air enough that it can hold more evaporated moisture? But our problem with condensation in cold weather has definitely diminished since we installed the heater.


To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.

Pacific Seacraft Crealock 31 #62

NEVER CALLS CRUISINGDAD BACK....CAN"T TAKE THE ACCENT
JohnRPollard is offline  
Quote Quick Reply Share with Facebook
post #6 of 24 Old 01-25-2009
the pointy end is the bow
 
erps's Avatar
 
Join Date: Aug 2006
Location: La Conner, Washington
Posts: 6,260
Thanks: 2
Thanked 27 Times in 26 Posts
Rep Power: 10
   
Quote:
I do wonder a bit about your scenario. If the ambient air is damp, and the heater unit draws air from within the cabin for combustion, isn't that air going to need to be replaced by more damp ambient air, from outside the cabin?
The colder air outside is supposed to be drier humidity wise than the warm air inside, because cold air holds less moister than warm air. At least that's the way it was explained to me. The Dickinson website actually promotes their heaters as giving off dry heat.

DickinsonMarine.com - Diesel Natural Draft Heaters

Ray
S.V. Nikko
1983 Fraser 41
La Conner, WA


To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


Boating for over 25 years, some of them successfully.
erps is offline  
Quote Quick Reply Share with Facebook
post #7 of 24 Old 01-26-2009 Thread Starter
Senior Member
 
Join Date: Sep 2006
Location: Scotland
Posts: 2,364
Thanks: 0
Thanked 11 Times in 11 Posts
Rep Power: 9
 
erps :

I think what they mean by "dry heat" is that they are not adding water to the cabin air from the combustion. The cooker, for example, creates condensation readily as burning the gas in air produces water vapour a-plenty.

If the Dikenson heater has no cabin air through-put, then all it is doing is what the Eberspacher does and heats the cabin air.

The Taylor heater has a single flue and so must(?) have a cabin air throughput? I think the Dikenson has a single flue as well, so I am encouraged. When the day comes that when I start the heater, and 6 hours later condensation is not dripping down the portlights, then I will be doing beter than at present. I guess I need to find someone with a Taylor or Dickenson heater, or similar.

I know a solid fuel heater will dry a boat... I know someone has one.... but I cannot speak for the diesel heaters with flue, as yet.

Last edited by Rockter; 01-26-2009 at 06:15 AM.
Rockter is offline  
Quote Quick Reply Share with Facebook
post #8 of 24 Old 01-26-2009
Senior Member
 
nk235's Avatar
 
Join Date: Apr 2007
Location: Long Island
Posts: 404
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 9
 
I have the Dickson Newport Deisel heater and it was installed on my boat when I bought it used. The boat has never really had a mositure issue from the start but I can def say that when ever I light the Dickson, it sure feels like it makes the boat extra dry. I used it a lot in the beginning of the season last year and after it has been on for a few hours, everything in the cabin seemed real dry and warm. So I have no scientific proof but just wanted to comment on my experiences incase it may help.

[IMG]Photobucket[/IMG]

Morgan 323

Last edited by nk235; 01-26-2009 at 06:48 AM. Reason: added pic
nk235 is offline  
Quote Quick Reply Share with Facebook
post #9 of 24 Old 01-26-2009
Moderator
 
JohnRPollard's Avatar
 
Join Date: Mar 2007
Location: Chesapeake
Posts: 5,680
Thanks: 0
Thanked 3 Times in 3 Posts
Rep Power: 10
     
Quote:
Originally Posted by Rockter View Post
... The cooker, for example, creates condensation readily as burning the gas in air produces water vapour a-plenty.
Rockter, yeah, that is likely one of the biggest advantages we are seeing. Before we installed the cabin heater, we used to do a lot of extra cooking/baking/pre-heating to help warm the cabin and we would invariably end up in a rainforest below decks. Solid bronze portlights are especially good condensing surfaces!

One of the other variables I seem to remember was that the diesel heaters need a longer flue/chimney for draft purposes. I think that is why we see so many diesel heaters mounted low-down as in erps' and nk's photos. Personally, I like that look, especially when coupled with a tiled- or metal-lined fireplace. But the propane heaters only require about 24" of chimney -- they can often work in tighter spaces. So be sure to measure carefully!


To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.

Pacific Seacraft Crealock 31 #62

NEVER CALLS CRUISINGDAD BACK....CAN"T TAKE THE ACCENT
JohnRPollard is offline  
Quote Quick Reply Share with Facebook
post #10 of 24 Old 01-26-2009 Thread Starter
Senior Member
 
Join Date: Sep 2006
Location: Scotland
Posts: 2,364
Thanks: 0
Thanked 11 Times in 11 Posts
Rep Power: 9
 
Guys :

Thanks.

I just have to be sure they are drawing in cabin air for combustion and so creating a through-put. Some of them draw their air for coubustion down a concentric flue arrangement, and so there is no through-put of cabin air.

I wonder does the flue have to be straight, because I think I can get the necessary length by using a dog-leg in the flue.

nk : do you not fry the cushion material next to it there? It looks very close!

Last edited by Rockter; 02-08-2009 at 04:46 PM.
Rockter is offline  
Quote Quick Reply Share with Facebook
Reply

Quick Reply
Message:
Options

Register Now



In order to be able to post messages on the SailNet Community forums, you must first register.
Please enter your desired user name, your email address and other required details in the form below.
Please note: After entering 3 characters a list of Usernames already in use will appear and the list will disappear once a valid Username is entered.


User Name:
Password
Please enter a password for your user account. Note that passwords are case-sensitive.

Password:


Confirm Password:
Email Address
Please enter a valid email address for yourself.

Email Address:
OR

Log-in









Human Verification

In order to verify that you are a human and not a spam bot, please enter the answer into the following box below based on the instructions contained in the graphic.




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Show Printable Version Show Printable Version
Email this Page Email this Page



Similar Threads
Thread Thread Starter Forum Replies Last Post
Diesel Heater Carboning SV_WholeHeart Living Aboard 8 10-27-2011 07:43 PM
winterize hot water heater? saltypat Gear & Maintenance 6 10-26-2007 11:47 AM
installing duct system for diesel heater and air conditioner levenezia Gear & Maintenance 1 09-25-2004 03:20 AM
Water Heater By Pass Valve MHRitter Gear & Maintenance 2 10-31-2002 09:41 AM
Onboard Heater Sue & Larry Gear and Maintenance Articles 0 10-15-2001 08:00 PM

Posting Rules  
You may post new threads
You may post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On
Trackbacks are On
Pingbacks are On
Refbacks are On

 
For the best viewing experience please update your browser to Google Chrome