Unhappy CruisAir system freezing up on heat cycle

I have a 2009 Beneteau with two CruisAir air conditioning/heating systems. My problem is they are freezing up in the heat cycle. The sea water temperature is around 55 degrees. I cleaned the intake strainer. Both units definitely have water flowing through them and out the through hull. They will not give me more than 60 degrees Fahrenheit. The salon unit is getting a thick layer of ice on the compressor unit. Air is flowing out of the vents at full speed. Help!

Big.Moe1@verizon.net

Thanks, Big Moe
BigMoe is offline  
Quote Quick Reply Share with Facebook
Sponsored Links
Advertisement
 
post #2 of 6 Old 04-14-2009
October Moon B43
 
Join Date: Mar 2009
Location: SE Pennsylvania
Posts: 400
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 7
 
Moe, the icing is normal in the heat mode. In your house the unit has a sensor that detects the ice and puts the heat pump into a reverse cycle, thereby melting the ice. The units on boats do not have an auto defrost mode for when they ice up. The only fix is to switch over to the cool mode and set it for about 60 degrees. It will take a few minutes but you'll be able to see the ice melt off the coils. Once it does go back to the heat mode and you'll be fine. Keep an eye on it periodically and do a defrost when the coils start to become blocked. One tell tale sign is the heat output will drop off.
Mike
PS we have our new 43 October Moon at Glenn's as well. We're over on the pump out dock on the Winter's side of things.
MJBrown is offline  
Quote Quick Reply Share with Facebook
post #3 of 6 Old 04-15-2009
Senior Member
 
Join Date: Dec 2007
Posts: 201
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 8
 
One other thing to try is slowing down the fan speed, if you have the ability to control the fan manually. This might prolong the icing cycle. You may also supplement the reverse cycle heat with a plug in ceramic heater, especially when plugged into shore power.
jason3317 is offline  
Quote Quick Reply Share with Facebook
post #4 of 6 Old 04-20-2009 Thread Starter
Member
 
BigMoe's Avatar
 
Join Date: Oct 2006
Posts: 40
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 0
 
Talking Found the problem with Air Conditioner/Heaters freezing up!

Hello Fellow Sailors:
I isolated the problem with the help of an air conditioning repair person supplied by my boat dealer, Winters Sailing. Both of my units, on my new Beneteau, had globs of Silicone jammed in the "Condensing Coil". The repair person tried his best to unclog the units but to no avail. I hooked up an air compressor to a 1/8" stiff poly propeline line about 6 foot long. I slowly and carefully fed it into the condensing coil through the water intake line until I hit the clog. I then gave it about 100 PSI and kept moving it in and out until the silicone broke up and it went through the system. I suspect the silicone was used on the clear rubber intake hose somewhere between the intake and the units.

Heat Finally!

Thanks to everyone who helped me.

Big Moe
BigMoe is offline  
Quote Quick Reply Share with Facebook
post #5 of 6 Old 05-13-2009
Junior Member
 
Join Date: Apr 2009
Posts: 3
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 0
 
Cooling

Ok, so you guys are trying to heat up, while I am trying to cool down!

I recently bought a Beneteau 473. I live in the Middle East (Dubai) and to be understated, it is getting hot....and this is just the start. Temperatures over the next few months will climb to 120F, or 48c. Not really a problem while sailing, as you get used to it, but as you can imagine even thinking about going down below or having a nice dinner in the cabin while moored is out of the question.

I have been checking the web and I am looking to install air conditioning for when we are moored in the marina.

Any advice on manufacturers, size or cost? I really do not want to get into a lot of installation since it is only will be used when at the dock, when we are at the boat, which is only on the weekends, at best.

Is portable the way to go? I have shore power and it seems that this may be the simplest, but storage may be an issue, unless we leave the units on the dock with the guys.

Any advice is welcome.

Regards

Jimb
jbad is offline  
Quote Quick Reply Share with Facebook
post #6 of 6 Old 05-13-2009
moderate?
 
camaraderie's Avatar
 
Join Date: May 2002
Location: East Coast
Posts: 13,877
Thanks: 0
Thanked 3 Times in 3 Posts
Rep Power: 16
     
jbad...a 473 is completely unsuitable for portable. Indeed...you will need somewhere over 20,000 Btu's and probably 2 units to keep the boat cool.
I would suggest a 16k unit for the main cabin and a 6k unit for the master stateroom.
You will need through hulls for the installation so will need to pull the boat.
The work is not at all hard and if you are reasonably handy, you can do it yourself. Lots of good companies...Marine Airr makes a fine product and offers good support among others.
This will not be cheap...but portable will be a waste of money in my opinion.

No longer posting. Reach me by PM!
camaraderie is offline  
Quote Quick Reply Share with Facebook
Reply

Quick Reply
Message:
Options

Register Now



In order to be able to post messages on the SailNet Community forums, you must first register.
Please enter your desired user name, your email address and other required details in the form below.
Please note: After entering 3 characters a list of Usernames already in use will appear and the list will disappear once a valid Username is entered.


User Name:
Password
Please enter a password for your user account. Note that passwords are case-sensitive.

Password:


Confirm Password:
Email Address
Please enter a valid email address for yourself.

Email Address:
OR

Log-in









Human Verification

In order to verify that you are a human and not a spam bot, please enter the answer into the following box below based on the instructions contained in the graphic.




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Show Printable Version Show Printable Version
Email this Page Email this Page



Similar Threads
Thread Thread Starter Forum Replies Last Post
Waeco cold machine charging TahitiDave Gear & Maintenance 3 03-19-2006 07:52 AM
Steering System Spring Checkup Tom Wood Gear and Maintenance Articles 0 04-26-2004 08:00 PM
Checking the Wheel Steering System Will Keene Gear and Maintenance Articles 0 07-31-2002 08:00 PM
Sailing with E-Mail Kathy Barron Seamanship Articles 0 09-04-2000 08:00 PM
Sailing with E-Mail Kathy Barron Gear and Maintenance Articles 0 09-04-2000 08:00 PM

Posting Rules  
You may post new threads
You may post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On
Trackbacks are On
Pingbacks are On
Refbacks are On

 
For the best viewing experience please update your browser to Google Chrome