Bill and I posted at the same time. Bill and I are in violent agreement that the simple solution here is that you need to buy new batteries.
eherlihy is online now  
Quote Quick Reply Share with Facebook
Sponsored Links
Advertisement
 
post #12 of 19 Old 03-23-2010
Senior Member
 
Join Date: Aug 2006
Location: Arlington, VA
Posts: 1,854
Thanks: 0
Thanked 11 Times in 9 Posts
Rep Power: 11
   
Three guys in "violent agreement".....a pretty scary thought :-)

B.
btrayfors is offline  
Quote Quick Reply Share with Facebook
post #13 of 19 Old 03-23-2010
Telstar 28
 
sailingdog's Avatar
 
Join Date: Mar 2006
Location: New England
Posts: 43,290
Thanks: 0
Thanked 15 Times in 12 Posts
Rep Power: 14
         
Well, in that case, I'd consider the batteries TOAST too...

Quote:
Originally Posted by jjrunning View Post
I did check the electrolyte level and the batteries are full.

Doesn't a hydrometer just test the charge of the battery? What is the difference between testing the electrolyte fluid with a hydrometer and testing the voltage with a multimeter?

Sailingdog

To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.

Telstar 28
New England

You know what the first rule of sailing is? ...Love. You can learn all the math in the 'verse, but you take
a boat to the sea you don't love, she'll shake you off just as sure as the turning of the worlds. Love keeps
her going when she oughta fall down, tells you she's hurting 'fore she keens. Makes her a home.

—Cpt. Mal Reynolds, Serenity (edited)

If you're new to the Sailnet Forums... please read this
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
.

Still—DON'T READ THAT POST AGAIN.
sailingdog is offline  
Quote Quick Reply Share with Facebook
post #14 of 19 Old 03-23-2010
Member
 
Join Date: Jun 2004
Posts: 37
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 0
 
If you unplugged them and they were at 12.8 volts they are being undercharged. 12.9 is a fully charged battery and your charger should push about 13.6 volts to charge minimum, most alternators are in the 14V plus range unless regulated. The battery case will sometimes say the recommended float voltage.

If they were regularly undercharged they are most likely quite sulfated by now. The easiest way to tell sulfation is to fully charge them until they take no more amps then load them up, if the voltage drops off quick and you don't have much capacity as you think it's usually a safe bet. If these are wet cells you can try to do a equalizing charge and convert that hard sulfate crystals back into active material. Rolls (Surrette) batteries has a pretty good instruction guide on equalizing their batteries and it should fit most batteries.

Good luck sir!
arghhh is offline  
Quote Quick Reply Share with Facebook
post #15 of 19 Old 03-23-2010
Telstar 28
 
sailingdog's Avatar
 
Join Date: Mar 2006
Location: New England
Posts: 43,290
Thanks: 0
Thanked 15 Times in 12 Posts
Rep Power: 14
         
Umm... A fully charged 12 VDC battery is 12.6-12.7 VDC, not 12.9... unless it has a surface charge from being charged.

I don't know what brand of batteries or where you got your information, but it's wrong. From the Trojan battery site.





Quote:
Originally Posted by arghhh View Post
If you unplugged them and they were at 12.8 volts they are being undercharged. 12.9 is a fully charged battery and your charger should push about 13.6 volts to charge minimum, most alternators are in the 14V plus range unless regulated. The battery case will sometimes say the recommended float voltage.

If they were regularly undercharged they are most likely quite sulfated by now. The easiest way to tell sulfation is to fully charge them until they take no more amps then load them up, if the voltage drops off quick and you don't have much capacity as you think it's usually a safe bet. If these are wet cells you can try to do a equalizing charge and convert that hard sulfate crystals back into active material. Rolls (Surrette) batteries has a pretty good instruction guide on equalizing their batteries and it should fit most batteries.

Good luck sir!

Sailingdog

To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.

Telstar 28
New England

You know what the first rule of sailing is? ...Love. You can learn all the math in the 'verse, but you take
a boat to the sea you don't love, she'll shake you off just as sure as the turning of the worlds. Love keeps
her going when she oughta fall down, tells you she's hurting 'fore she keens. Makes her a home.

—Cpt. Mal Reynolds, Serenity (edited)

If you're new to the Sailnet Forums... please read this
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
.

Still—DON'T READ THAT POST AGAIN.
sailingdog is offline  
Quote Quick Reply Share with Facebook
post #16 of 19 Old 03-23-2010
Member
 
Join Date: Jun 2004
Posts: 37
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 0
 
Quote:
Originally Posted by sailingdog View Post
Umm... A fully charged 12 VDC battery is 12.6-12.7 VDC, not 12.9... unless it has a surface charge from being charged.

I don't know what brand of batteries or where you got your information, but it's wrong. From the Trojan battery site.
You are indeed correct is it about 12.7 not 12.9 according the the trojan chart referenced. I look a quick peek at my link 20 to see what the voltage of my AGM bank was to get my 12.9. I charged it about a 2 weeks ago and it has been resting ever since. Of course I had to measure it with my fluke to make sure . I wonder if there is something different between wet cells and my AGMs to cause a full charge voltage difference. I have CSB brand VLRA High rate UPS batteries for reference.


Anyway back to topic, seeing 12.8 right off the charger does not sound like the charger is working as it should be.
arghhh is offline  
Quote Quick Reply Share with Facebook
post #17 of 19 Old 03-23-2010
Senior Member
 
Join Date: Aug 2006
Location: Arlington, VA
Posts: 1,854
Thanks: 0
Thanked 11 Times in 9 Posts
Rep Power: 11
   
AGMs and Gels typically both have higher voltages than flooded batteries, not only when fully charged but throughout most of the discharge curve.

Here's a comparison table of Open Circuit Voltages -- OCV (from East Penn):

Well, don't know why this **xx%%##*** Board won't let me attach a small file.


The 100% charged values for flooded, AGM, and gelled are 12.6, 12.80, and 12.85 respectively. "Or higher"
The 75% charge values are 12.4, 12.60, 12.65
The 50% charge values are 12.2, 12.30, 12.35
The 25% charge values are 12.0, 12.0, 12.0

Note that the true OCV can only be determined once the battery has been disconnected from the load -- charge or discharge -- for 24 hours.

Bill

Last edited by btrayfors; 03-23-2010 at 10:31 PM.
btrayfors is offline  
Quote Quick Reply Share with Facebook
post #18 of 19 Old 03-23-2010
Telstar 28
 
sailingdog's Avatar
 
Join Date: Mar 2006
Location: New England
Posts: 43,290
Thanks: 0
Thanked 15 Times in 12 Posts
Rep Power: 14
         
I'd point out that the OP's Stowaway Marine deep cycle batteries are wet cell battteries AFAIK, not gel or AGM.

Sailingdog

To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.

Telstar 28
New England

You know what the first rule of sailing is? ...Love. You can learn all the math in the 'verse, but you take
a boat to the sea you don't love, she'll shake you off just as sure as the turning of the worlds. Love keeps
her going when she oughta fall down, tells you she's hurting 'fore she keens. Makes her a home.

—Cpt. Mal Reynolds, Serenity (edited)

If you're new to the Sailnet Forums... please read this
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
.

Still—DON'T READ THAT POST AGAIN.
sailingdog is offline  
Quote Quick Reply Share with Facebook
post #19 of 19 Old 03-24-2010
Senior Member
 
timebandit's Avatar
 
Join Date: Sep 2002
Posts: 928
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 13
 
Get new batteries.

Any batteries that self descharge below 12 volts in two days are cores.

Rick
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.

Mac 25
Copernicus
Southern California
I am not a prejudice racist sexist bigot. I just hate stupid people.
timebandit is offline  
Quote Quick Reply Share with Facebook
Reply

Quick Reply
Message:
Options

By choosing to post the reply above you agree to the rules you agreed to when joining Sailnet.
Click Here to view those rules.

Register Now



In order to be able to post messages on the SailNet Community forums, you must first register.
Please enter your desired user name, your email address and other required details in the form below.
Please note: After entering 3 characters a list of Usernames already in use will appear and the list will disappear once a valid Username is entered.


User Name:
Password
Please enter a password for your user account. Note that passwords are case-sensitive.

Password:


Confirm Password:
Email Address
Please enter a valid email address for yourself.

Email Address:
OR

Log-in









Human Verification

In order to verify that you are a human and not a spam bot, please enter the answer into the following box below based on the instructions contained in the graphic.




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Show Printable Version Show Printable Version
Email this Page Email this Page



Similar Threads
Thread Thread Starter Forum Replies Last Post
Reconditioned Batteries dryclean Gear & Maintenance 10 03-18-2010 08:28 AM
Battery Bank Design Kevin Jeffrey Gear and Maintenance Articles 0 05-12-2003 08:00 PM
Battery Bank Design Kevin Jeffrey Cruising Articles 0 05-12-2003 08:00 PM
Installing a New Battery Bank Sue & Larry Gear and Maintenance Articles 0 09-26-2002 08:00 PM
Boat Battery Power East Penn Manufr. Gear and Maintenance Articles 0 01-18-1999 07:00 PM

Posting Rules  
You may post new threads
You may post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On
Trackbacks are On
Pingbacks are On
Refbacks are On

 
For the best viewing experience please update your browser to Google Chrome