One issue is that by only going down to 80% capacity, you're actually going to be wasting a lot of the capacity of the bank. If that is your plan, you're probably better off not combining the various different batteries, and using either the AGM pair or the wetcell pair as the house bank and running it down to the 50% mark instead--or using both pairs as two different house banks and alternating between them.
Having the 95 AH battery in the mix is pretty stupid IMHO.
Mixing the AGM with the wetcell is also a bad idea, since the AGMs have a much higher current acceptance rate when in bulk charging mode than the wet cells do.
Also, if you combine all the batteries for a bank size of over 500 amp-hours, the charger you have is woefully undersized to deal with it.