  #1  
Old 06-29-2012
Junior Member
 
Join Date: Jul 2006
Posts: 24
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 0
xluke is on a distinguished road
Powering AC with genreator, handling surge load

Hello,
I recently got a 2000 watt generator -- a little 2.7hp model. To operate it I simply plug a standard adapter which converts a standard 120v plug into a standard 30amp shore power plug into its 120v and hook my shore power cable into that adapter, and into the shore power socket. It works great, and powers everything BUT the AC. My AC is 16000btu, and draws a modest 4-5 amps under running condition (4-5amps*120v should be around 600 watts, P=IV), however, when the compressor kicks on it draws between 15-30amps. This is no problem on shore power but this surge is beyond the generator's capacity and it cuts out.
I realize I could go to a larger generator, but I do not want the additional weight nor size.
I was wondering if I could run power to the shore power in parallel -- one side of the circuit coming from the 2000 watt generator, and the other coming from a 2000-4000 watt inverter attached to the deep cycles. I theorize that when the AC kicks on, it will draw additional current from the battery to deliver the the necessary amps to kick on the compressor, and then when it drops down to running level amps (4-5amps) I can simply disconnect/switch off the inverter from the batteries, allowing the generator to carry the load on its own for the rest of the time.

Is this feasible? Has anyone experimented with a similar setup?

Thanks!
Reply With Quote Share with Facebook
  #2  
Old 06-29-2012
Classic30's Avatar
Once known as Hartley18
 
Join Date: Aug 2007
Location: Melbourne, Australia
Posts: 4,249
Thanks: 17
Thanked 23 Times in 23 Posts
Rep Power: 8
Classic30 will become famous soon enough Classic30 will become famous soon enough
Re: Powering AC with genreator, handling surge load

Quote:
Originally Posted by xluke View Post
I was wondering if I could run power to the shore power in parallel -- one side of the circuit coming from the 2000 watt generator, and the other coming from a 2000-4000 watt inverter attached to the deep cycles. I theorize that when the AC kicks on, it will draw additional current from the battery to deliver the the necessary amps to kick on the compressor, and then when it drops down to running level amps (4-5amps) I can simply disconnect/switch off the inverter from the batteries, allowing the generator to carry the load on its own for the rest of the time.

Is this feasible?
No, no, NO - absolutely not! You can't practically parallel up to shore power without fitting large and expensive control gear.

The only way you could get your A/C unit to work off of the generator you have will be to install an Inverter big enough to handle the current in-rush of, as you said, 15-30 Amps ie. 30A*120V = 3600 watts, and run that off a battery which you charge with the generator. The A/C would be running off the Inverter full-time. I don't know what a 4kW Inverter would cost, but it wouldn't be cheap - or light - but, by the sounds of it, that's what you'll need.

IMHO you are better advised to get a bigger generator.
__________________
-
"Honestly, I don't know why seamen persist in getting wrecked in some of the outlandish places they do, when they can do it in a nice place like Fiji." -- John Caldwell, "Desperate Voyage"
Reply With Quote Share with Facebook
  #3  
Old 06-29-2012
Senior Member
 
Join Date: Oct 2009
Location: Virginia
Posts: 969
Thanks: 3
Thanked 13 Times in 13 Posts
Rep Power: 5
chuck53 is on a distinguished road
Re: Powering AC with genreator, handling surge load

I've read a number of posts about a "soft starting" AC. I don't know the details but it is some kind of option you can add to the AC unit that makes it pull a lot less amps when starting up. A number of people have it just for your purpose - they have a fairly small generator that works fine except for compressor start up.
__________________
Catalina 34
Reply With Quote Share with Facebook
  #4  
Old 06-29-2012
JimsCAL's Avatar
Senior Member
 
Join Date: May 2007
Location: Glen Cove, NY
Posts: 2,160
Thanks: 0
Thanked 13 Times in 12 Posts
Rep Power: 7
JimsCAL is on a distinguished road
Re: Powering AC with genreator, handling surge load

Hartley is absolutely right about not paralleling two AC sources. To do this you need synchronizing controls so the sine waves are in synch. Without that you will get excessive current and damage things.

And something is wrong with your number for AC capacity or normal current reading. Typical EER of an AC unit is 10. So a 16,000 Btu/hr unit would draw about 1600 watts. That's close to the rating of your generator and will never be able to start it. A 6000 Btu/hr AC unit would be about 600 watts and that would agree with your 4-5 amps when running. Check your numbers.
Reply With Quote Share with Facebook
  #5  
Old 06-29-2012
Senior Member
 
Join Date: Oct 2009
Location: Virginia
Posts: 969
Thanks: 3
Thanked 13 Times in 13 Posts
Rep Power: 5
chuck53 is on a distinguished road
Re: Powering AC with genreator, handling surge load

Quote:
Originally Posted by JimsCAL View Post
Hartley is absolutely right about not paralleling two AC sources. To do this you need synchronizing controls so the sine waves are in synch. Without that you will get excessive current and damage things.

And something is wrong with your number for AC capacity or normal current reading. Typical EER of an AC unit is 10. So a 16,000 Btu/hr unit would draw about 1600 watts. That's close to the rating of your generator and will never be able to start it. A 6000 Btu/hr AC unit would be about 600 watts and that would agree with your 4-5 amps when running. Check your numbers.
I'm betting the 4-5 amps is just the fan running by itself - no compressor.
__________________
Catalina 34
Reply With Quote Share with Facebook
  #6  
Old 06-29-2012
deniseO30's Avatar
Lies about her age
 
Join Date: Nov 2006
Location: Bristol pa
Posts: 5,444
Thanks: 50
Thanked 53 Times in 45 Posts
Rep Power: 9
deniseO30 will become famous soon enough deniseO30 will become famous soon enough
Re: Powering AC with genreator, handling surge load

PO needs to get a real time amp reading on the unit when it starts. The fan most likely runs on less the 2 amps. Depending on which compressor (recip or rotary) will dictate starting amps. if the unit doesn't have a "hard start" accessory. it will need it to lower the starting amps. Do not use the name plate rating for ACTUAL running conditions. I'm assuming the unit is water cooled? That would also make the unit a lower amp draw then a air cooled condenser.
__________________
Denise, Bristol PA, Oday 30. On Tidal Delaware River, Anchor Yacht Club. New Website!
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.

my current "project"!
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
Reply With Quote Share with Facebook
  #7  
Old 06-29-2012
Stu Jackson's Avatar
Senior Member
 
Join Date: Jul 2001
Posts: 716
Thanks: 0
Thanked 2 Times in 2 Posts
Rep Power: 13
Stu Jackson is on a distinguished road
Re: Powering AC with genreator, handling surge load

Quote:
Originally Posted by chuck53 View Post
I've read a number of posts about a "soft starting" AC. I don't know the details but it is some kind of option you can add to the AC unit that makes it pull a lot less amps when starting up. A number of people have it just for your purpose - they have a fairly small generator that works fine except for compressor start up.
That's the way to do it. Never, ever combine two different incoming AC electrical sources. Never.

Google "soft start for boat air conditioning" and you'll find the sources.
__________________
Stu Jackson, C34, 1986, M25 engine, Rocna 10 (22#)
Reply With Quote Share with Facebook
  #8  
Old 06-29-2012
Senior Member
 
Join Date: Feb 2012
Location: New Orleans Louisiana
Posts: 1,472
Thanks: 5
Thanked 22 Times in 21 Posts
Rep Power: 3
Stumble is on a distinguished road
Re: Powering AC with genreator, handling surge load

Depending on which small gen you bought, the Honda and Yamaha can be linked to produce a nominal 4kw from two 2kw gens. But this only works because the control boards can talk to each other and sync up by a cat5 cable.

Trying this with dissimilar sources, as noted above, is both dangerous and a fire hazard.
__________________
Greg Rubin
Attorney
Reply With Quote Share with Facebook
  #9  
Old 06-29-2012
deniseO30's Avatar
Lies about her age
 
Join Date: Nov 2006
Location: Bristol pa
Posts: 5,444
Thanks: 50
Thanked 53 Times in 45 Posts
Rep Power: 9
deniseO30 will become famous soon enough deniseO30 will become famous soon enough
Re: Powering AC with genreator, handling surge load

Back in the day cities in the east like Phila pa. Had and and may still have some "2 phase" service. There used to be 2 phase wired BIG semi hermetic compressors in some old ac units.

Just for conversation, and some interesting reading
http://www.3phasepower.org/2phasesystems.htm
__________________
Denise, Bristol PA, Oday 30. On Tidal Delaware River, Anchor Yacht Club. New Website!
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.

my current "project"!
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.

Last edited by deniseO30; 06-29-2012 at 05:42 PM.
Reply With Quote Share with Facebook
  #10  
Old 06-29-2012
tommays's Avatar
Senior Member
 
Join Date: Sep 2008
Posts: 4,036
Thanks: 1
Thanked 12 Times in 12 Posts
Rep Power: 6
tommays will become famous soon enough
Re: Powering AC with genreator, handling surge load

They still have the two phase and the big machines get special motors which is a PITA
__________________
1970 Cal 29 Sea Fever

To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.

1981 J24 Tangent 2930
Tommays
Northport NY


If a dirty bottom slows you down what do you think it does to your boat
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
Reply With Quote Share with Facebook
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools

 
Posting Rules
You may post new threads
You may post replies
You may post attachments
You may edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Surge currents in Marina del Rey!? dnickers General Discussion (sailing related) 11 03-14-2011 07:08 PM
Storm/Flood Surge, Hows it looking? T37Chef Chesapeake Bay 28 10-04-2010 02:44 AM
Surge and Die Snboard976 Diesel 7 06-27-2010 06:23 PM
Sea Surge theartfuldodger Cruising & Liveaboard Forum 16 02-14-2010 04:09 PM
Surge Protection Question matt2 Electrical Systems 1 03-01-2009 11:36 PM


All times are GMT -4. The time now is 02:50 PM.

Add to My Yahoo!         
Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2014, vBulletin Solutions, Inc.
SEO by vBSEO 3.6.1
(c) Marine.com LLC 2000-2012