Xantrex Freedom HF 1800 Help Please

I have a Xantrex Freedom HF 1800. I recently acquired a transformer that is changing the 220VAC European shore power to 110VAC. Actual measurement on the 110VAC side is more like 127VAC. Of course it is still 50 cycle rather than 60 cycle. The transformer is rated for 4,000 Watts - more than the 30 Amp shore 110VAC.

My problem is that the unit senses the shore power (the yellow light flashes) but will not switch over to start charging the batteries. I have found no useful information on the Xantrex site.

Any ideas?

CAPT Roger J. Jones USN (ret.)
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


Sailboat Reboot

411 Walnut Street, #9700, Green Cove Springs, FL 32043-3443

Reboot's Agent's Email:
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


Web Site:
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


Blogging:
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


Twitter @Sailboat_Reboot
svzephyr44 is offline  
Quote Quick Reply Share with Facebook
Sponsored Links
Advertisement
 
post #2 of 4 Old 10-19-2012
Bali Hai
 
mgraham49's Avatar
 
Join Date: Jan 2008
Location: Texas
Posts: 50
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 8
 
Send a message via Skype™ to mgraham49
Xantrex Freedom HF 1800 Help Please

If you reach the point that you need professional advice, I have used Tekris Power in New Jersey (I am in Texas) for rebuilding and diagnosing problems. I worked with Chris there and he would literally let me take iPhone pictures of the control panel for my xantrex 2000 and message them to him while we were on the phone to diagnose. Really great people. I finally got tired of the old one and bought a new 3000 from them.
mgraham49 is offline  
Quote Quick Reply Share with Facebook
post #3 of 4 Old 10-21-2012
Member
 
Join Date: Sep 2008
Location: Vancouver, BC
Posts: 63
Thanks: 0
Thanked 1 Time in 1 Post
Rep Power: 7
 
Ask Xantrex if it will work on 50hz. The manual states it will only switch over if the power is within specification and it states 60hz as the input a.c. specification.
KBuckley is offline  
Quote Quick Reply Share with Facebook
post #4 of 4 Old 10-21-2012
Senior Member
 
Join Date: Sep 2010
Posts: 249
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 5
 
Re: Xantrex Freedom HF 1800 Help Please

If you could get the transformer (which is probably an autotransformer) to put out like 105v that would be better if you want to plug in things like motors and transformers which are designed for 125VAC max at 60 cycles. You have to drop the voltage (to be precise after subtracting the resistive voltage loss in the coils from your calculation but you can ignore that) by the same amount that you lower the frequency. So a 125VAC 60 cycle refrigerator would work safely at 104VAC on 50 cycles. The same applies to transformers and any other inductive load.

For a transformer or motor that normally draws 3 amps, you should lower the voltage until it does not draw more than 3 amps when hooking it up to 50 cycles.

Having 127VAC which is slightly above the limit and then having 50 cycles instead of 60 cycles could be a problem.
steel is offline  
Quote Quick Reply Share with Facebook
Reply

Quick Reply
Message:
Options

Register Now



In order to be able to post messages on the SailNet Community forums, you must first register.
Please enter your desired user name, your email address and other required details in the form below.
Please note: After entering 3 characters a list of Usernames already in use will appear and the list will disappear once a valid Username is entered.


User Name:
Password
Please enter a password for your user account. Note that passwords are case-sensitive.

Password:


Confirm Password:
Email Address
Please enter a valid email address for yourself.

Email Address:
OR

Log-in









Human Verification

In order to verify that you are a human and not a spam bot, please enter the answer into the following box below based on the instructions contained in the graphic.




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Show Printable Version Show Printable Version
Email this Page Email this Page



Similar Threads
Thread Thread Starter Forum Replies Last Post
Xantrex sucks - What replaces an Xantrex Echo-Charger? jarcher Gear & Maintenance 20 07-24-2012 09:03 PM
Xantrex/Heart Freedom 25 -- How to connect Water Heater Bene505 Electrical Systems 64 10-25-2010 11:19 AM
xantrex freedom marine 1500 inverter/charger issues ncstatesailor Gear & Maintenance 1 04-09-2010 06:57 PM
I need a Xantrex Freedom remote panel, Link or Standard, Used or ugly OK TommyboySD Gear & Maintenance 0 04-22-2009 06:33 PM
Jrc 1800 Cp PCSSailor Gear & Maintenance 0 01-31-2009 03:08 PM

Posting Rules  
You may post new threads
You may post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On
Trackbacks are On
Pingbacks are On
Refbacks are On

 
For the best viewing experience please update your browser to Google Chrome