  #51  
Old 02-04-2013
Wandersome's Avatar
Wanderer
 
Join Date: Jan 2013
Location: Islamabad Pakistan
Posts: 21
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 0
Wandersome is on a distinguished road
Re: Power Outlet Sizzle - Help Please

When did flipping become code? I like to install them ground down....
Reply With Quote Share with Facebook
  #52  
Old 02-04-2013
Member
 
Join Date: Nov 2012
Posts: 40
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 0
Navigator Wannabe is on a distinguished road
Re: Power Outlet Sizzle - Help Please

So then we agree that there likely was a high resistance, or intermittent contact. At one spot, i.e. in the outlet box, right?

In that case, running everything at at 80% of rated power is not a solution.
Such a sizzle-spot will start a fire at 15 amps, as it did.
Run it at 80%, let it corrode a bit further, and it will start the same fire at 12 amps.
And so on, you can't reduce the load until there is not enough power to start a fire.
The only remedy is getting rid of the (well, all) defective, high resistance, parts and connections. (I think we agree that the wires will corrode at the connection points, right?)
If you notice a problem like this, and just reduce the load on the wiring, you basically are ASKING the fire hazard to come back another time when you are not looking.

Btw, I think sizzle is arcing, not boiling insulation.


Quote:
Originally Posted by BubbleheadMd View Post
I disagree. It isn't always that simple.

The boat is an '85 Catalina. The boat is nearly 30 years old, which offers plenty of time for age and corrosion to introduce extra resistance into an electrical circuit.

My assumption is that the OP is running over 80% of the rating for the circuit, at the end of a long wire run, the wiring or the contacts in the outlet begin to heat up, it melts down, causing the "sizzle" and now the outlet is out of commission.

As I said in my post where you quoted me, running at close to 100% of the circuit's rating continuously, on 30 year old wiring and equipment, is likely to induce extra heat, which would eventually cause a failure.

You make it sound as if electrical components don't at all to break down with age, especially in a marine environment, and that it's safe to run at 100% of a circuit's rating indefinitely. I disagree with that.

The "80% rule" not only applies to vessels, it applies to shore-side installations that aren't even subject to the constant motion and corrosion of the marine environment.

That's cool though. You be you, and I'll be me.
Reply With Quote Share with Facebook
  #53  
Old 02-04-2013
Member
 
Join Date: Nov 2012
Posts: 40
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 0
Navigator Wannabe is on a distinguished road
Re: Power Outlet Sizzle - Help Please

Two legs?

I have never sen a shore power cord with 4 prongs.
Only phase, neutral, and ground.

Quote:
Originally Posted by mad_machine View Post
Yes and No.. 30amps should be two legs.. so he was drawing all that power through ONE leg. It should have definatly tripped the breaker before smoking the outlet
Reply With Quote Share with Facebook
  #54  
Old 02-04-2013
mad_machine's Avatar
Sea Sprite 23 #110 (20)
 
Join Date: Dec 2012
Location: Atlantic City, NJ
Posts: 3,136
Thanks: 5
Thanked 67 Times in 58 Posts
Rep Power: 2
mad_machine is on a distinguished road
Re: Power Outlet Sizzle - Help Please

Quote:
Originally Posted by Navigator Wannabe View Post
Two legs?

I have never sen a shore power cord with 4 prongs.
Only phase, neutral, and ground.
if you read beyond that post.. I mentioned that I was wrong. I was thinking of work... we use 6 panels of 400amp service at the theatre I work at.. so using 30amp service to mean means a gang of three 30amp circuts
__________________
Art Haberland
__________________

In the end all that matters is how fully you loved, how gently you lived, and how gracefully you let go of things that did not belong to you -Buddha

__________________

To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
Reply With Quote Share with Facebook
  #55  
Old 02-04-2013
Junior Member
 
Join Date: Oct 2012
Posts: 3
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 0
Dougtiff is on a distinguished road
Re: Power Outlet Sizzle - Help Please

Install the GFI outlet up stream of all the other outlets, if you read the instructions it will state that it protects 3 or 4 outlets, i forget how many.
Reply With Quote Share with Facebook
  #56  
Old 02-04-2013
Maine Sail's Avatar
Senior Member
 
Join Date: Jan 2003
Location: Maine Coast
Posts: 5,293
Thanks: 10
Thanked 117 Times in 85 Posts
Rep Power: 15
Maine Sail is just really nice Maine Sail is just really nice Maine Sail is just really nice Maine Sail is just really nice
Re: Power Outlet Sizzle - Help Please

Quote:
Originally Posted by Navigator Wannabe View Post
Two legs?

I have never sen a shore power cord with 4 prongs.
Only phase, neutral, and ground.
Plenty of them out there in a 50A 125/250V cord except the fourth "prong" is the metal ring which is Earth ground on a 50A 125V/150V shore cord.. There are also 50A 125V cord sets that are single phase...
__________________
______
-Maine Sail / CS-36T


To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.




© Images In Posts Property of Compass Marine Inc.


Reply With Quote Share with Facebook
  #57  
Old 02-04-2013
Philzy3985's Avatar
Senior Member
 
Join Date: Oct 2012
Location: Redondo Beach
Posts: 174
Thanks: 0
Thanked 6 Times in 6 Posts
Rep Power: 2
Philzy3985 is on a distinguished road
Re: Power Outlet Sizzle - Help Please

I'm learning a good amount from your input and doing some research.

A professional electrician is coming out the day after tomorrow and I'll get my answers and basically fix/replace everything I can afford, highest priority items immediately.

The plugs from my heater, iron, and stereo that morning were all plugged into the power strip. They are all normal and look unaffected The power strip's prongs going into the outlet that sparked are not burnt and they look as usual, the wire appears okay and the power strip still fully works. Of course, the wire (from the outlet to the power strip) was warm, not extremely hot, to the touch when I pulled it out a moment after the sizzle.

Anyways. I'd love for the electrician to test a few things and tell me exactly what went wrong so I can put the mystery to rest.

Thanks again, the wealth of knowledge here is greatly appreciated, as always.
__________________
1985 Catalina 30 Std Rig "A Cenoura"
itsACenoura.tumblr.com
Reply With Quote Share with Facebook
  #58  
Old 02-04-2013
pdqaltair's Avatar
Senior Member
 
Join Date: Nov 2008
Location: Deale, MD
Posts: 2,135
Thanks: 1
Thanked 28 Times in 28 Posts
Rep Power: 6
pdqaltair is on a distinguished road
Re: Power Outlet Sizzle - Help Please

Quote:
Originally Posted by Philzy3985 View Post
Anyways. I'd love for the electrician to test a few things and tell me exactly what went wrong so I can put the mystery to rest.
There is no mystery. The prongs in the female part lost their tension with age and perhaps chronic overheating, the connection became worse, eventually to the point of arcing. This is not at all uncommon in older homes, where replacement of lose plugs is a good idea. This also happens to plugs that are not overheated, only worn due to age or poor construction. However, you supplied the clue about overloading. In this sense, overload does not mean you were over the rated capacity of the circuit, depending on where the heater and iron were set, but you were most likely over the long term practical limit, which is perhaps only 70%, depending on the age and quality of the fittings.
__________________
(when asked how he reached the starting holds on a difficult rock climbing problem that clearly favored taller climbers - he was perhaps 5'5")

"Well, I just climb up to them."

by Joe Brown, English rock climber




To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
Reply With Quote Share with Facebook
  #59  
Old 02-05-2013
Member
 
Join Date: Nov 2012
Posts: 40
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 0
Navigator Wannabe is on a distinguished road
Re: Power Outlet Sizzle - Help Please

Are you being obscene here???





Quote:
Originally Posted by pdqaltair View Post
There is no mystery.

... female part lost their tension with age and perhaps chronic overheating, the connection became worse, ...

This is not at all uncommon in older homes, where replacement of lose plugs is a good idea.

This also happens to plugs that are not overheated, only worn due to age ...

... most likely over the long term practical limit, which is perhaps only 70%, depending on the age and quality of the fittings.
Reply With Quote Share with Facebook
  #60  
Old 02-13-2013
Philzy3985's Avatar
Senior Member
 
Join Date: Oct 2012
Location: Redondo Beach
Posts: 174
Thanks: 0
Thanked 6 Times in 6 Posts
Rep Power: 2
Philzy3985 is on a distinguished road
Re: Power Outlet Sizzle - Help Please

A quick update, for reference sake.

A pro came out from a highly reputable marine service company. He determined that the outlet just got too hot and fried one wire. He cut the wire off and shortened it to the length that was still good, plugged them all back in, and it all works again. He tested the main breaker switch, and pretty much everything else behind the control panel. After talking more, I asked that they come back to replace the shore-power receptacle on the boat-side, and put fuses on the wires for my 'battery select' switch, as recommended previously by the surveyor. He said I should replace my shore power cord, so that's on my list too.

So, nothing apparently massively serious, so that was a relief. I asked all about tracing it and what else could go wrong but the basic answer is "Catalina did the bare minimum throughout the 80s and this is it."

Since then, though, they misplaced my paperwork or something because they haven't called me back to reschedule finishing the other stuff. four 5-star reviews on yelp, so, we'll see how it all goes.

Thanks everyone here
__________________
1985 Catalina 30 Std Rig "A Cenoura"
itsACenoura.tumblr.com
Reply With Quote Share with Facebook
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools

 
Posting Rules
You may post new threads
You may post replies
You may post attachments
You may edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On


Similar Threads
Thread Thread Starter Forum Replies Last Post
12v power outlet in cockpit dougklay Gear & Maintenance 22 09-11-2008 07:19 AM
Batteries Sizzle Like Alka-Seltzer theArchitect Gear & Maintenance 4 07-02-2007 08:42 AM


All times are GMT -4. The time now is 08:23 PM.

Add to My Yahoo!         
Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2014, vBulletin Solutions, Inc.
SEO by vBSEO 3.6.1
(c) Marine.com LLC 2000-2012

The SailNet.com store is owned and operated by a company independent of the SailNet.com forum. You are now leaving the SailNet forum. Click OK to continue or Cancel to return to the SailNet forum.