AGM batteries

7K views 24 replies 10 participants last post by  kellysails 
#1 ·
I have a few questions I am thinking someone out there knows the answers to. My boat came with three group 27 AGM batteries with two in a house bank and one as a starter battery for my Perkins 4.108. I would like to combine the three current batteries into the house bank and buy an actual starter battery for the diesel.

My house bank currently resides in two typical battery container boxes and if I try to put the third in the same area it would not fit in its own box. Do AGM batteries need to be in boxes or just secured? If they need to be in boxes I will likely fabricate a box that fits all three.

I am thinking of getting a typical lead acid starter battery for the diesel. I'm wondering if I'll have a problem in mixing batteries between the two systems. I never allow both banks to interact and have a separate charging system for both when I'm plugged in to shore. The problem I think might occur when the ACR combines the bank when I'm charging while motoring. Any thoughts on this?

Also, any recommendations on the size of a starter battery I'll need?

Thanks

Scott
 
See less See more
#2 ·
AGMs need to be secured. Doesn't hurt to put them in a box, either.

A group 27 start battery would work. I use a group 31 start battery for my 4-108 just for a bit of extra capacity.

AGMs and flooded batteries have almost identical charging profiles, so you could use a flooded start battery.

Not sure how your ACR is wired. The ideal way these days is to lead ALL charging sources to the house battery bank, then use either a voltage-follower device (e.g., EchoCharge or DuoCharge) or an ACR to maintain the start battery.

BTW, start batteries require very little charging. Starting your 4-108 typically will use 150-175A while cranking, but only for a very few seconds. Typical capacity draw for a diesel start is less than 0.5 amp-hours!! This is replaced in just a couple of minutes.

Bill
 
#3 ·
AGMs need to be secured. Doesn't hurt to put them in a box, either.

A group 27 start battery would work. I use a group 31 start battery for my 4-108 just for a bit of extra capacity.

AGMs and flooded batteries have almost identical charging profiles, so you could use a flooded start battery.

Not sure how your ACR is wired. The ideal way these days is to lead ALL charging sources to the house battery bank, then use either a voltage-follower device (e.g., EchoCharge or DuoCharge) or an ACR to maintain the start battery.

BTW, start batteries require very little charging. Starting your 4-108 typically will use 150-175A while cranking, but only for a very few seconds. Typical capacity draw for a diesel start is less than 0.5 amp-hours!! This is replaced in just a couple of minutes.

Bill
Hey Bill

SO would you use the wet cell charge cycle for both or the agm charge cycle for both?

Brian
 
#4 ·
I used to have the starting battery echo charged off the house bank like Bill mentioned, but with the ACR I installed it acts like an isolator and combiner so that wasnt necessary

Peronally I dont like mixing types of batteries, but because the wets take about the same bulk charge as AGM and its the starter battery whoich woint be discharged much, it may be ok but I am not an expert. Will the AGM be held back by the wet cell charge acceptance?

Dave
 
#5 · (Edited)
The ONLY way that I would consider mixing AGM and Wet-Cell batteries, of different ages, is with the HOUSE bank as AGMs, and the START battery connected via an Echo-Charge. I would verify that the voltage regulator is capable of working with AGMs, and that your alternator is up to the task of charging the house bank. The battery switch would be switched to the start bank to start, and then quickly switched to the house bank at any time when the engine is running.

In general, my learning from the posts in SailNet, and elsewhere, is that one should not mix battery types. YMMV :)

AGMs do not need to be kept in a box, they only need to be secured.

Good article here: http://www.pacificpowerbatteries.com/marinebatts.html
AGM Pro's: better cycling and depth of dischager over the wet or gell batteries. While most wet batteries are supposed to only go to about 50% depth of discharge, the AGM's are able to go to about 20% depth of discharge without harming them PROVIDED that you don't overcharge them at too high a voltage on their return.
...
Wet Lead Acid Battery Con's: Slower to recharge than AGM, require maintenance more often, and don't cycle as deeply as the AGM batteries.
 
#6 · (Edited)
The ONLY way that I would consider mixing AGM and Wet-Cell batteries, of different ages, is with the HOUSE bank as AGMs, and the START battery connected via an Echo-Charge. I would verify that the voltage regulator is capable of working with AGMs, and that your alternator is up to the task of charging the house bank. The battery switch would be switched to the start bank to start, and then quickly switched to the house bank at any time when the engine is running.

In general, my learning from the posts in SailNet, and elsewhere, is that one should not mix battery types. YMMV :)

AGMs do not need to be kept in a box, they only need to be secured.

Good article here: Pacific Power Batteries - About Automotive Batteries

AGM Pro's: better cycling and depth of dischager over the wet or gell batteries. While most wet batteries are supposed to only go to about 50% depth of discharge, the AGM's are able to go to about 20% depth of discharge without harming them PROVIDED that you don't overcharge them at too high a voltage on their return.
...
This is what is so frustrating about the internet, that poor information, is trumpeted as truth..

That data was EXACTLY how AGM batteries marketed and launched themselves into the marine market. Those bogus promises of longer cycle life and more usable capacity than deep cycle flooded batteries was soon ousted as a mistruth in the "real world" where the battery life really matters.. These misleading marketing attempts really bit them in the ARSE because cycle life at 80% DOD SUCKED....

Today nearly every maker of AGM batteries, Lifeline, Deka/East Penn (and all their private labels), Trojan, Rolls etc. etc. all recommend a 50% DOD not 80% DOD.

Odyssey still sells on 80% DOD but they readily admit that at 80% DOD you only get 400 cycles.:eek: (and this in in a laboratory with white glove treatment)

At 80% DOD with a flooded group 31 Rolls 12V battery you get 800 cycles or DOUBLE the life of an Odyssey AGM at 80% DOD. DOUBLE the rated cycles !!!! The Rolls battery also costs less than HALF of what an Odyssey does.

With a Deka/East Penn AGM group 31 12V battery you get 250 cycles to 80% DOD.:eek:

Compare that to a US Battery DCXC group 31 flooded deep cycle battery that sells for about $120.00 and it gives you 675 cycles at 80% DOD!! Bump that up to 50% DOD and you get 1150 cycles yet the Odyssey only gives 700 at 50% and the Deka/East Penn 500 cycles at 50% DOD..

Oh and to even attempt to come close to 400 cycles at 80% DOD with Odyssey batteries you need a minimum of 40% of capacity in charging current. So a 400Ah bank needs a charge source capable of maintaining 160A. If this is an alternator you'd need a cold rating of about 200A to have 160A when hot.... How many boaters can do that or expend all that money just to hope they "might" get 400 cycles when a cheap $120.00 battery will give 675 cycles with no fancy charging system upgrades.....

The fact is that AGM's do not offer longer life or deeper cycling an this has been priven time and time again in the "real world" and also in the lab by the manufacturers.. The manufacturers own data shows shows this, it's where I got the numbers from above.

I find this to be an interesting quote by Trojan Battery. When AGM's first came out the claims were BETTER cycle life than wets as that web site still seems to claim..

Trojan Battery said:
Generally, gel and AGM batteries have about 20% less capacity, cost about two times more, and have a shorter cycle life than comparable flooded lead acid batteries. However, Gel and AGM batteries do not need watering, are safer (no acid spilling out), can be placed in a variety of positions, have a slower self-discharge characteristic, and are more efficient in charging and discharging than flooded batteries (see table below). Gel batteries are more suitable for deep cycling applications whereas AGM batteries are more for light cycling and engine-starting applications.
Disclaimer: Keep in mind that ALL of those numbers are LAB DERIVED where temperature, charge rate and charge/discharge cycles are done very methodically and repeatably. Those numbers are NOT at all indicative of what you'll see in the real world. If you want real world numbers chop 50% right off the top and now you're in the ball park..
 
#8 ·
Brian,

I'd set the charger and any regulator(s) --- for the alternator, wind generator, solar panels, etc. --- to the AGM profile. The EchoCharge will take care of the flooded start battery just fine.

And, if you set it up as I suggested with all charging sources going directly to the house battery bank, with an EchoCharge or DuoCharge connected between the house bank and start battery, then there's no need for switching at all.

IMHO, it's a BAD IDEA to play with the main battery switch while the engine is running, even if it has a field disconnect circuit. Someday, you or one of your crew is going to switch to the wrong position and blow your alternator diodes.

I agree with MainSail's comments about AGMs. Been running some factory supplied numbers myself. My conclusion at this point is that there are very few boats for which AGMs make any sense at all. If you really need a battery with a low self-discharge rate which doesn't require maintenance and which can be installed on its side, then go with gelled batteries.

These have a very long cycle life, provided that you properly set up the charging voltages. Just about any modern charger or regulator has this capability.

Bill
 
#10 ·
Scott, when batteries are combined into a bank it is best if they are all same size form the same production lot. Mixing batteries of different age, or batteries that have been cycled differently and are no longer in the same capacity, is not a good idea. They will equalize across each other and the weakest one will just pull down the others.

So if you have three "identical" batteries but one was used for starting and the other two for house? Don't combine them. Use 'em up, as they are, and then start fresh with one house bank of whatever capacity you want (or can find or afford<G>) and one starting battery of the same chemistry so they can charge together on the same system.

While you are waiting for the current batteries to be used up, take a thorough look at your charging system, and plan to update, modify, improve, that as needed at the same time. Since the "little things" can literally double the life of your batteries, and batteries have gotten damned expensive, any money you spend optimizing the charging system is likely to be very well spent. Even if you optimize that now, and defer the new batteries until these are used up.
 
#11 ·
We did the AGM thing for a while, and then when we left the dock, we couldn't get 3 months out of them. The manufacturer and engineer who installed our electrical system along with Balmar all went over my system and concluded that it must have been a bad batch of batteries. The manufacturer sent us replacement batteries on freight for free. Balmar even replaced our voltage regulator for the alternator. Then after being at anchor for about 6 months, we had problems with the replacement batteries.

We have since went back to wet batteries with no issues.
 
#12 ·
Thanks for all the replies. I do like the lack of maintenance with the AGM batteries but I'm uncertain of how much longer they will last. I would rather go to the flooded style in the future when they die. Is there any way I can determine the potential life left in these batteries?
 
#14 · (Edited)
Scott,

Easiest way to get a reliable estimate of remaining capacity is to find someone with a sophisticated inductance/capacitance tester, like the Midtronics series. These are too costly to buy for your needs (about $600), but they'll tell you the remaining capacity pretty quickly.

Failing that, there's only one reliable way to test remaining capacity, and that's by doing a controlled C/20 load test. This means you fully charge the batteries, then attach a resistive load calculated to be approximately 1/20th the battery capacity, and let it go for upwards of 20 hours or until the voltage drops to 10.5VDC.

A group 27 AGM has between 90-100AH capacity. Say 100AH to make the calculation easy. So, if you hooked up one of these to a load you'd want a 100/20 = 5 amp load. Five amps @ 12 volts = 60 watts, so a 60 watt load would be appropriate to do a load test on one of your group 27 batteries.

As noted above, a halogen car headlamp might do the trick. These tend to be about 55 watts or 4.6 amps....a little less than the target 5 amp load. And, guess what? If your AGM battery were only about 92AH instead of 100AH -- as many are -- then the 4.6 amp load would be right on target :)

Alternatively, you can probably find four 15-watt 12V bulbs at West Marine. Hook all 4 up in parallel and attach to the battery under test. Then, take periodic voltage readings over the next hours until you get to 10.5VDC.

If you only get 10 hours, that means the battery only has 1/2 capacity left.

If you only get 5 hours, that means the battery only has 1/4 capacity left.

When you're done testing each battery, be sure to fully charge it....don't let it sit discharged.

Good luck. Let us know what you find.

Bill
 
#13 ·
You can load test them. Fully cycle them, charge them 100% and let them stand, then put a load test on them. You can buy load testers under $50 for something that small on Amazon (3x higher at the local auto store) or maybe borrow one for free from Autozone or Pep Boys tool rental program. Or take the batteries into a shop and ask them to do a load test, usually free.

You can also load test them by fully charging them, then connecting a load like a headlight and timing it until the voltage drops. Or fully charging the batteries, letting them stand overnight, and then using a good accurate digital multimeter and assuming 12.6 was a new battery, derate them 10% for each 1/10th of a volt they are below that. That's not perfect, because meters aren't dead accurate and 12.6 isn't a universal truth, but it will give you a "1/8-1/4-1/2-3/4" type profile versus the label rating.
 
#15 ·
Maine...is this true?

•The higher charge efficiency of AGMs allows you to recharge with less energy: Flooded cells convert 15-20% of the electrical energy into heat instead of potential power. Gel-cells lose 10-16% but AGMs as little as 4%. The higher charge efficiency of AGMs can contribute to significant savings when it comes to the use of expensive renewable energy sources (wind generators, solar panels, etc.) as your charging system can be 15% smaller (or just charge faster).

I am not arguing with you about the use of AGM. There is a lot of misinformation printed then. I am able to get mine back up to 100% quickly, but eventually I will need to replace them, My 6 volt Lifelines are now 5 years old and going strong. Part of me using them is their inaccessability and that I have two laying on their sides.

This is not correct information then?

Battery Types: Flooded versus AGM and Gel
 
#16 · (Edited)
Dave,

You are using your AGM's for one of their actual "benefits", this is GOOD.. I RARELY see more than hand full of boaters taking advantage of any of the real pluses of AGM's..

Much of that information from that site is correct and much of it is very "dreamy"... For example that article is still in the "fantasy" stages of AGM technology where they sold us on 80% DOD's and suggested you could get away with a smaller bank. That marketing "tune" has changed big time..

This is straight from the Lifeline tech manual.

"For example, if 100 Ah is required on average, select at least a 200Ah battery. This approach will limit the average depth of discharge to 50% and will dramatically extend the life of the battery.

To get the best cycle life, the average depth of discharge should be as low as possible. Concorde (Lifeline) recommends the average depth of discharge be no greater than 50% of the battery's 20 hour rating."


They are not recommending 3:1 bank sizing as that article insinuates, they are suggesting 2:1 bank sizing just as flooded batteries are sized for. I referenced this in the above post and it is 100% backed up by the AGM makers themselves, including Lifeline, which that article seems to tout. The only exception to this that I am aware of is Odyssey who still market at 80% DOD and 400 cycles.

This one element alone throws a HUGE monkey wrench into the entire bank sizing calculations for that site. It would also be better for the math if he had rated the T105's at what Trojan does, which is about 1200 cycles to 50% DOD.. It is right on the T105 Tech Data sheet.

One other thing I find rather odd or perhaps misleading is his use of the West Marine batteries in the cost comparisons. It is NOT a secret that WM slaps a Sea Volt sticker on Deka/East Penn batteries. They are the MOST EXPENSIVE reseller of these batteries or put another way that Sea Volt sticker is VERY expensive.....

Heck the Group 31 12V Deep Cycle was selling for $247.99 in last yeas catalog. That SAME battery can be purchased at Sam's Club for $84.97..

Sams Club = Group 29/31 (Deka DC31) 105Ah Battery $84.97

West Marine = Group 31 (Deka DC31) 105Ah Battery $247.99


Difference = $165.02 per battery !!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!

I honestly wonder how the math would have worked out had he compared the least expensive re-seller of the SAME battery rather than the MOST expensive......????? Inquiring mids are curious...

The SAME batteries can be purchased at NAPA, O'reilly Auto, Sam's Club and many other locations for considerably less than HALF the cost of West Marine. Of course on the flip side, if you use West Marine as your basis for cost analysis, it helps make the Lifeline Battery look better... :D

AGM's charge faster. No secret there and I DO take advantage of this on many installations. Where customers CAN take advantages of the faster charge, and they fully understand that life cycles may not be as good as they suspect, I have no issues installing AGM's and in many cases actually recommend them..

Another big problem is that most boats I go on can't even meet the minimum suggested charge capacity for AGM's, 40% of "C" for Odyssey and 20% of "C" for Lifeline so it makes very little sense to spend huge money on a system we already know will be on the short side of longevity by having a limited charging system.

The other "never talked about" issue is that when AGM's are new they take GOBS of current. New however does not last very long if the batteries do not get back to 100% after every discharge cycle. For mooring sailors this a tough issue. Lifeline specifically notes this in their warranty.

"The limited warranty does not cover discharged batteries, batteries that have been opened, frozen, sulfated batteries due to undercharging, diminishing capacity due to battery age, split open battery cases, transportation, rental, testing, housing, freight or installation costs."

Back in the real world, not warranties worth about as much as the paper they are printed on, I have a 4 year old bank of Lifeline 6V batteries to replace in the next month. They are currently taking just 65-80A in bulk/in-rush and hitting absorption voltage within a few minutes. The alternator, when loaded, goes right up to its 150A cold rating. Customer initially blamed the alternator and regulator and spent HUGE money having the alternator re-built and purchasing a new replacement regulator. Same issue... He calls in the boat yard, they diagnose it as poor wiring and replace it to the tune of $1600.00. OUCH!!! Same problem. Finally I get a call show up, test the batteries, measure internal resistance, fire up the motor and say: "you need new batteries".... "But they are only 4 years old, it can't be the batteries.".... I plug my heat gun into the inverter, fire up the motor and put my Fluke around the alternator output wire. What would you know 150A and the alt and reg are working just fine. Turn off the heat gun and right back to 65A of acceptance..... As it sits now this bank of four 6V batteries takes about 12+ hours to get to a full charge due to the sulfation. So yes when new, how all the marketing is done, they can and do charge faster. However unlike flooded or GEL cells they really don't like to sit at anything less than 100% SOC or they sulfate and performance, including charging performance, suffers and seems to suffer faster than with GEL or flooded LA batts..

From Lifeline:
"For repetitive deep cycling, chargers should have an output current of at least 0.2C (20 Amps for a 100 Ah battery). If the output current is less than this value, the cycle life of the battery may be negatively affected."


Hell beyond the initial 3:1 bank sizing or 80% DOD we were sold on, we were also led to believe early on that AGM batteries did not even sulfate.. Talk about marketing. I can clearly remember the marketing guys telling me "you never need to equalize an AGM battery because they don't suffer from sulfation." SWEET!! So I went out and installed a few banks, based on the "glossy marketing"....... Hmmm guess what? They sulfated..... Doh'........

With AGM's I hear so many people claim they bought them for "high acceptance rates" then they feed a 450Ah bank with an 80A alt that when hot puts out 60-65A or about 14% of capacity or 6% below the minimum suggested by Lifeline.

Heck that same bank in flooded batteries will take the full hot capacity of a 125A alternator or slightly more..

Back in the real world I work in, a customer just last month called me to ask if he really needed to be there for the 8 hours he was going to be equalizing his Lifelines for. Ummmm YES, how else are you going to monitor the battery temperature during this over voltage event....!!!! Makes adding distilled water to some flooded cells seem like cake walk.... 8 hours of 15.5V for a "conditioning charge", but they are sold as "no maintenance". At year two he is already noticing "diminished capacity" hence the conditioning charge. That said AGM batteries are this customers best option due to fitment, containment and because he actually has a 180A alternator. Cost is not an issue for him.

Again, AGM's HAVE NUMEROUS benefits its just that cost and cycle life are not either of them....;)
 
#17 ·
Maine,

Thanks for the explaination

The chart in the link shows the Lifelines at 1000 cycles at 50% discharge.

I have done what was described with a 660 ah bank which rarely goes below the 75% discharge. I do have the availability to get close to the 100% no with the new alternator and shore power master volt charger.

I kaois have been desulfating when neccessary at 15.5, but not for the whole 8 hours...maybe 6 as I watch the temp readings

I porabbly have paid more attention to batteries since I bought these than I do anything else on the boat it seems. My wife says I am obsessed with it.:D

When these finally wear out I proably will go to the gells if I still have Haleakula, as they are really inaccesable.
 
#18 ·
AGM batteries "Depends"

In my case AGM's seem to have done well. When I say in my case, I am talking about going on 7 years with 2 Optima AGM's. I just pulled them and had them checked at Interstate on one of those high dollar testers that Maine Sail recommends. In fact they showed quite a bit above there "rated" capacity. Unfortunately, I don't have a baseline to compare them to since I didn't have them checked when I first bought them.

Since the boat sits on a trailer most of the time and they have been discharged rarely, usually never below 11.0 - 11.5 volts (?) They have also been connected to a fan running 24 hours/365 days a year for the past 5 (?) years. They have been connected to a 20w solar panel with a Morningstar Duo controller (4 stages).

They have never been "equalized" and only occasionally I throw them on a pulse charger over night. I'm not saying that I recommend the way they have been maintained, only listing the facts.

I realize if you are a cruiser and actually get to use your boat regularly and your batteries go through the normal discharge cycles, your mileage will vary.

Although they have held up well, I got them at a ridiculous price from a friend years ago. I would find it hard to pay what they go for now. They are nice because the batteries are hard to get to if I had wet cells it would be a pain.

They will now probably go belly up. :(
 
#19 · (Edited)
Chef & Maine, you guys really make this forum the best, thank you! Yet another interesting topic.

Once the admiral and I finally cast off our lines I was planning to replace all the wet cells with AGM's. I have been following AGM for a number of years and while hearing all sorts of positive remarks, occasionally I would hear about the consistent need of equalizing the batteries. It seemed anytime Lifeline received an issue from a customer their response was, equalize. I did make sure my regulators for my 100amp charger and 210 Balmar supported equalization. But more recently I have been put off by this idea. What am I to do when laying off of Dominica with my AGM's in need of an equalization treatment? I have felt recently that I need to re-examine this approach. This thread pushed me over the edge.

While looking at the Rolls website the other day they noted their AGM's do not need equalization ever. WTF? They note the use of Pure Lead which gets into the new Marketization term of "TPPL" (thin plate pure lead). Is this the resolution to this AGM issue? Or yet another marketing ploy to lead me astray. This is very frustrating trying to get past all the BS.

With a use budget of 200-250 amps per day, (2) D400's and a 10amp solar panel and the above mentioned charger/alternator which way should I go? I was thinking a 600a/h house system. We are not dock marina people, laying on anchor is what we prefer.
 
#22 ·
Chef & Maine, you guys really make this forum the best, thank you! Yet another interesting topic.

Once the admiral and I finally cast off our lines I was planning to replace all the wet cells with AGM's. I have been following AGM for a number of years and while hearing all sorts of positive remarks, occasionally I would hear about the consistent need of equalizing the batteries. It seemed anytime Lifeline received an issue from a customer their response was, equalize. I did make sure my regulators for my 100amp charger and 210 Balmar supported equalization. But more recently I have been put off by this idea. What am I to do when laying off of Dominica with my AGM's in need of an equalization treatment? I have felt recently that I need to re-examine this approach. This thread pushed me over the edge.

While looking at the Rolls website the other day they noted their AGM's do not need equalization ever. WTF? They note the use of Pure Lead which gets into the new Marketization term of "TPPL" (thin plate pure lead). Is this the resolution to this AGM issue? Or yet another marketing ploy to lead me astray. This is very frustrating trying to get past all the BS.

With a use budget of 200-250 amps per day, (2) D400's and a 10amp solar panel and the above mentioned charger/alternator which way should I go? I was thinking a 600a/h house system. We are not dock marina people, laying on anchor is what we prefer.
For me the jury is still out on the new Roll's AGM's. Rolls is not making these like they do their wet cells. They are a Chinese made AGM. I stil think if you go AGM you go Odyssey or Lifeline with Lifeline having a lead due to the ability to equalize them.

That said I think you would be much better off with a GEL battery than an AGM. Provided they are properly charged they will accept more current than flooded batts and are not nearly as finicky about getting back to full. When properly charged they are some of the longest lasting batteries out there.

If you are still considering AGM technology you owe it to yourself to read John Harries multiple article work on AGM's and how they've learned to manage them on a full time cruising boat.

AGM Battery Care / Morgan's Cloud

What John says is all stuff I have been saying for many years. AGM's certainly can work but they are anything but "maintenance free" and require PROPER care to get them to last.... Still as of Jan 2012 he was at 90% of new with only about 400 cycles to 50% and a 180 very shallow cycles all this over 18 months. A battery is considered failed at 80% of new capacity. I will be surprised to see John break much over two years, even with exemplary care ...
 
#20 ·
md, even a nuclear pile loses some capacity over seven years. So if someone tested your Optimas and found them above rated capacity after seven years, I'd say they are in great shape--but the test may have been done wrong, one way or another. Even if you never used them and simply kept them on a float charge...after seven years...most unusual.
 
#24 ·
Kelly..

Batteries are the least taken care of piece of equipment most peoples boats IMHO and it suprising how little the average sailor knows or pays attention to them, unless of course they dont work, they quit after a year or two, or they spend a lot of money on them.

Morgans Cloud is an example of someone who didnt do enough research and also mismatched his system to his actually maintainence so it cost him dearly, which is why I am sure he posted so other wouldnt fall into the same trap. 3 battery banks in 4 years is
operator error.

For our type of sailing and the battery banks inaccesable location the Lifeline 6- 6 Volt AGMS have been a good decision. We can bring them up to 100% as we have a slip in a marina like many other boaters do who post one here and have a three stage charger. After reading extensively and consulting a well qualified marine electrician in our area who knows how we use our boat, we have concluded that this is the way to go for us. We also have a large enough battery bank that one day does not bring us down to the 85% of capacity mark. We also have been equalizing them as necessary. So far we have gotten 4 solid years out of them with no drop off noted. As long as we follow our current treatment of them there is no reason to beleive that I am at about half their life span, with little maintaince as possible but lots of monitoring.

Sailnet has many different types of sailors from weekend to weekend plus cruises, to liveaboards, to cruisers. We all keep our boats differently. On the Chesapeake and in Florida, the majority have shore power and marinas. In LI Sound and New England its mostly moorings. This also leads to different "expert advices" on how to keep your boat as well as what battery systems work best. You have to educate yourself as best as possible using all the experts and figure out what works best in your situation for you boat and how you use it. Taking battery advice from a cruiser when you dont cruise may not be the best advice for you. Taking battery advice from a person who has access to a 3 stage charger every week may not be the best advice for you.

MaineSail always gives great advice and I have followed him reverentially. He has helped educate me in many ways concerninig electrical and electronics. He has also saved me headache and money in making sure that I matched all the componets of my system. He is n ot a big fan of AGMs unless used in the right apllication and has helped guide me in my use of mine

If I was to keep this boat and cruise it I would certainly think about having a solar array to really keep the batteries bank in the 90% charged range all the time even when away from the dock. If I cruised Id probably go to gels and even when this bank goes away may do that, but alwasy will be 6 volters

The more I read the more I am convinced that the way to go no matter what type battery you are using is to make sure you have a large enough bank to start with. The old school reasoning of having a couple of house banks has now given way to the efficiencies in charging, cycling, of the 1 large house bank. The less deeply you discharge it % wise the great number of cycles you get from it.

Figure out you needs and install what works best for you. If you are a cruiser...find some good way of charging the bank and make sure you have a large enough bank. Using an engine/ generator to drive in the last 15% of battery a charge is linited by acceptance is proably not cost effective as say solar would be. If you can manage wet cells...go for it, Desulfating through equalization is the key.

I am not an expert at al and can only speak to what has worked for me in my application
Figure out what yours is and what you need.
 
  • Like
Reactions: mdbee
#25 ·
More great advice, thanks Chef!

Once we cast off our lines our biggest issue will be "very little time in a marina with reliable power". That is the design principal of the solution that I will need. I might be leaning towards Gel at this point but really I have a couple years to mull this over. I will likely change my mind a dozen times between now and then. And I will watch SN like a hawk for more great advice.
 
This is an older thread, you may not receive a response, and could be reviving an old thread. Please consider creating a new thread.