Battery Chargers in Parallel

I've been looking at 60A Victron Centaur Battery Chargers. Since the price of larger chargers goes up exponentially I was wondering if connecting two in parallel is an issue? I've read the available documentation from the Victron site but it doesn't address parallel connection. In principal for a dumb charger it seems plausible, but for a Smart Charger that senses and adjusts voltage I'm concerned it would create conflict. I guess the same might be true of an alternator and AC powered charger.
Missingyou is offline  
Sponsored Links
Advertisement
 
post #2 of 15 Old 09-10-2015
Senior Member
 
Join Date: Sep 2014
Location: Northeast U.S
Posts: 2,389
Thanks: 5
Thanked 85 Times in 82 Posts
Rep Power: 6
 
Re: Battery Chargers in Parallel

Quote:
Originally Posted by Missingyou View Post
I've been looking at 60A Victron Centaur Battery Chargers. Since the price of larger chargers goes up exponentially I was wondering if connecting two in parallel is an issue? I've read the available documentation from the Victron site but it doesn't address parallel connection. In principal for a dumb charger it seems plausible, but for a Smart Charger that senses and adjusts voltage I'm concerned it would create conflict. I guess the same might be true of an alternator and AC powered charger.
I recently tried to add an additional basic 48 volt power supply in parallel with my three stage charger just to add a few more amps into the charging/power mix. The power supply sensed the charger voltage and did not provide any additional amps. Perhaps adding a diode on the power supply output might isolate the power supply output enough but, I have not yet tried it. Sophisticated battery chargers might fight each other even more IMO.

Mike
Currently: Heading to warm waters over the winter on a variety of boats.

To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
mbianka is online now  
post #3 of 15 Old 09-10-2015
Super Moderator
 
Maine Sail's Avatar
 
Join Date: Jan 2003
Location: Maine Coast
Posts: 6,721
Thanks: 32
Thanked 363 Times in 283 Posts
Rep Power: 10
       
Re: Battery Chargers in Parallel

Quote:
Originally Posted by Missingyou View Post
I've been looking at 60A Victron Centaur Battery Chargers. Since the price of larger chargers goes up exponentially I was wondering if connecting two in parallel is an issue? I've read the available documentation from the Victron site but it doesn't address parallel connection. In principal for a dumb charger it seems plausible, but for a Smart Charger that senses and adjusts voltage I'm concerned it would create conflict. I guess the same might be true of an alternator and AC powered charger.
If you want a 100A-120A charger then you are far better off to invest in a good quality inverter / charger such as a Magnum, Outback or a Victron.

I am not a fan of the Centaur for a number of reasons.

*This is a dip switch charger with very few voltages to choose from. Even their cheap MPPT controllers allow me to custom program it for accurate battery voltage. The Centaur does not and you get what you get with the dip switch options..

I like to think of dip-switch chargers as dip-sh!t chargers. It is so easy today to build a good charger yet companies bone you with 1960's technology then call it "smart"...

Batteries do much better when charged with the correct voltages, in line with manufacturer recommendations. Always look for a charger that allows custom programming or more options than just a few. Also always look for a charger with on battery automated temp compensation..

*This charger does not offer temp compensation other than internal based on the chargers environment not the batteries environment.. This is NOT "smart"..

*For what you are not getting in a so called "smart charger" they are rather pricey and DUMB.


A better value would be the ProMariner ProNautic P 1260 or the Sterling ProCharge Ultra 1260.. Two chargers can run in parallel without issue IN BULK. Once one charger reaches absorption they can begin to ping-pong until one finally takes over and finishes the absorption cycle.

For the price of two 60A chargers a good inverter / charger makes more sense.....

______
-Maine Sail / CS-36T


To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.




Images In Posts Property of Compass Marine Inc.


Maine Sail is offline  
 
post #4 of 15 Old 09-10-2015
Senior Member
 
Join Date: Mar 2006
Location: Edmonton, Alberta
Posts: 180
Thanks: 0
Thanked 8 Times in 7 Posts
Rep Power: 15
 
Re: Battery Chargers in Parallel

Since Mainsail posted I'm hoping we could expand on this..

I know many boats that run multiple MPPT chargers from solar panels. How would this be different?

Just wondering!
travellerw is offline  
post #5 of 15 Old 09-10-2015 Thread Starter
Senior Member
 
Missingyou's Avatar
 
Join Date: Aug 2013
Location: Philadelphia
Posts: 152
Thanks: 13
Thanked 6 Times in 5 Posts
Rep Power: 7
 
Re: Battery Chargers in Parallel

Quote:
Originally Posted by Maine Sail View Post
If you want a 100A-120A charger then you are far better off to invest in a good quality inverter / charger such as a Magnum, Outback or a Victron.
I already have a Mastervolt Inverter, but I could always sell it on ebay, it should get a good price. It's location is more ideally suited anyway. The Magnum 125A looks very promising and I could ditch my poorly located Dipswitch 60A Cristec which is baking underneath of my aft starboard birth.

Quote:
Originally Posted by Maine Sail View Post
A better value would be the ProMariner ProNautic P 1260 or the Sterling ProCharge Ultra 1260.. Two chargers can run in parallel without issue IN BULK. Once one charger reaches absorption they can begin to ping-pong until one finally takes over and finishes the absorption cycle.

For the price of two 60A chargers a good inverter / charger makes more sense.....
Should have done more research on Chargers though, I did not think the ProMariner/Sterlings were so affordable. They are definitely a better option should I decide to keep my existing inverter.

Thanks Main Sail.

What would really put these Inverter/Chargers over the top is an input for Solar Panels, say 600W. How cool would that be? Truly all in one.

Last edited by Missingyou; 09-10-2015 at 02:56 PM. Reason: spelling/grammar
Missingyou is offline  
post #6 of 15 Old 09-13-2015
Once known as Hartley18
 
Classic30's Avatar
 
Join Date: Aug 2007
Location: Melbourne, Australia
Posts: 5,179
Thanks: 52
Thanked 85 Times in 85 Posts
Rep Power: 14
   
Dock
Re: Battery Chargers in Parallel

Quote:
Originally Posted by travellerw View Post
Since Mainsail posted I'm hoping we could expand on this..

I know many boats that run multiple MPPT chargers from solar panels. How would this be different?

Just wondering!
The difference is in how the batteries are hooked up. eg. I use a pair of MPPT chargers on my boat powered from one solar panel - one charger for the Start battery and one charger for House bank.

If the OP had multiple banks (or even multiple batteries within one bank) it is certainly possible to run more than one charger.. he just wouldn't be connecting them in parallel 'tis all.

-
A bad day on a boat beats a good day in the office

Last edited by Classic30; 09-13-2015 at 07:24 PM.
Classic30 is offline  
post #7 of 15 Old 09-13-2015
Super Moderator
 
Maine Sail's Avatar
 
Join Date: Jan 2003
Location: Maine Coast
Posts: 6,721
Thanks: 32
Thanked 363 Times in 283 Posts
Rep Power: 10
       
Re: Battery Chargers in Parallel

Quote:
Originally Posted by travellerw View Post
Since Mainsail posted I'm hoping we could expand on this..

I know many boats that run multiple MPPT chargers from solar panels. How would this be different?

Just wondering!
It really is no different at all. Both chargers will supply full current during bulk charging. Once the charge sources have brought the bank to the absorption/limiting voltage the charger with the highest voltage will finish the charge. In early absorption there may be a little game of ping pong going on as one charge source drops off and the remaining one perhaps can't maintain the limiting voltage. Eventually the batteries get to the point where only one charger is needed and it finishes the job..

The subject gets much deeper and a bit more complex when we have solar, wind, hydro, shore chargers and alternators, but two or more charge sources can easily be used and it is done every day...

______
-Maine Sail / CS-36T


To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.




Images In Posts Property of Compass Marine Inc.


Maine Sail is offline  
post #8 of 15 Old 09-13-2015
Senior Member
 
Join Date: Mar 2006
Location: Edmonton, Alberta
Posts: 180
Thanks: 0
Thanked 8 Times in 7 Posts
Rep Power: 15
 
Re: Battery Chargers in Parallel

Quote:
Originally Posted by Classic30 View Post
The difference is in how the batteries are hooked up. eg. I use a pair of MPPT chargers on my boat powered from one solar panel - one charger for the Start battery and one charger for House bank.

If the OP had multiple banks (or even multiple batteries within one bank) it is certainly possible to run more than one charger.. he just wouldn't be connecting them in parallel 'tis all.
Hhhmm I may have not been clear..

I have read about multiple cruisers that have 2 or 3 solar panels with 2 or 3 MPPT controllers (in parallel) charging a house bank. One controller per solar panel.

I'm wondering how this works. Wouldn't the charge controllers interfere with each other?
travellerw is offline  
post #9 of 15 Old 09-13-2015
Senior Member
 
Join Date: Mar 2006
Location: Edmonton, Alberta
Posts: 180
Thanks: 0
Thanked 8 Times in 7 Posts
Rep Power: 15
 
Re: Battery Chargers in Parallel

A quick google answered my question..

In case anyone else is wondering!
Parallel Charging Using Multiple Controllers With Separate PV Arrays Morningstar Corporation
travellerw is offline  
post #10 of 15 Old 09-13-2015
Once known as Hartley18
 
Classic30's Avatar
 
Join Date: Aug 2007
Location: Melbourne, Australia
Posts: 5,179
Thanks: 52
Thanked 85 Times in 85 Posts
Rep Power: 14
   
Dock
Re: Battery Chargers in Parallel

Quote:
Originally Posted by travellerw View Post
Hhhmm I may have not been clear..

I have read about multiple cruisers that have 2 or 3 solar panels with 2 or 3 MPPT controllers (in parallel) charging a house bank. One controller per solar panel.

I'm wondering how this works. Wouldn't the charge controllers interfere with each other?
Yes, you answered it.. but as the article states, the controllers are still not technically wired in parallel (both input and output). One key point is they must be identical units (same make/model down to the same switch settings) and must be designed for parallel operation (not just any old controller off the shelf).

For this reason it's generally not a good idea to do this on a boat, because failure of one unit in some foreign port someplace with no identical replacement available could mean you have to replace the entire charging system to get going again - an expensive proposition that kinda defeats the purpose. ..and besides, it really isn't necessary to do it this way when other alternatives exist for boat-sized loads.

-
A bad day on a boat beats a good day in the office

Last edited by Classic30; 09-13-2015 at 09:39 PM.
Classic30 is offline  
Reply

Quick Reply
Message:
Options

By choosing to post the reply above you agree to the rules you agreed to when joining Sailnet.
Click Here to view those rules.

Register Now



In order to be able to post messages on the SailNet Community forums, you must first register.
Please enter your desired user name, your email address and other required details in the form below.
Please note: After entering 3 characters a list of Usernames already in use will appear and the list will disappear once a valid Username is entered.


User Name:
Password
Please enter a password for your user account. Note that passwords are case-sensitive.

Password:


Confirm Password:
Email Address
Please enter a valid email address for yourself.

Email Address:
OR

Log-in











Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 



Similar Threads
Thread Thread Starter Forum Replies Last Post
Battery Bank Parallel or Series Rogre Electrical Systems 33 05-12-2018 03:41 PM
Series / Parallel Battery Jumper Sizing itsjustgher Electrical Systems 4 06-04-2013 08:52 PM
Battery Chargers willysail Gear & Maintenance 7 03-07-2012 04:55 AM
Battery Chargers for Multiple Battery Banks btrayfors Electrical Systems 5 11-15-2009 11:57 AM
Battery chargers wchevron Gear & Maintenance 13 05-09-2008 09:19 PM

Posting Rules  
You may post new threads
You may post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On
Trackbacks are On
Pingbacks are On
Refbacks are On

 
For the best viewing experience please update your browser to Google Chrome