Quote:
Originally Posted by eherlihy View Post
DO NOT confuse the AC Ground (aka neutral or white wire) with the GroundING (aka green wire).

The Ground should go to whatever AC load that you are connecting the AC to. The GroundING wire should connect to your vessel's bonding circuit. And, if your smart, you should have some form of galvanic isolation device for the vessel.
The white wire is Neutral, not to be confused with the ground. Neutral has never been called ground.
DotDun is offline  
Sponsored Links
Advertisement
 
post #12 of 18 Old 03-14-2017
Learning the HARD way...
 
eherlihy's Avatar
 
Join Date: Jan 2007
Location: Boston / Ft Myers Area
Posts: 6,775
Thanks: 391
Thanked 293 Times in 288 Posts
Rep Power: 13
 
Re: Galvanic Isolator

Quote:
Originally Posted by DotDun View Post
The white wire is Neutral, not to be confused with the ground. Neutral has never been called ground.
Not to ABYC. According to ABYC AC neutral IS called the "Grounded Conductor"

Quote:
11.4 DEFINITIONS

For the purposes of this standard, the following definitions apply.

11.4.1 AC grounded conductor - a current carrying conductor that is intentionally maintained at ground potential.

NOTE: This may be referred to as the neutral (white) conductor in AC electrical systems.


To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.

USCG Licensed OUPV Captain, ASA 101/103/104/105/106/114/118 Instructor - Also certified in Marine Electrical Systems


To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.

Last edited by eherlihy; 03-14-2017 at 09:32 PM.
eherlihy is online now  
post #13 of 18 Old 03-14-2017
Member
 
Join Date: Dec 2003
Posts: 51
Thanks: 0
Thanked 2 Times in 2 Posts
Rep Power: 16
 
Re: Galvanic Isolator

Quote:
Originally Posted by misfits View Post
I can't wrap my head around this for the life of me.
Why would you connect an AC ground that under the right circumstances could back feed line voltage to a DC buss. What am I missing here?

Bob
Can you explain what circumstances that might happen?
DotDun is offline  
 
post #14 of 18 Old 03-14-2017
Member
 
Join Date: Dec 2003
Posts: 51
Thanks: 0
Thanked 2 Times in 2 Posts
Rep Power: 16
 
Re: Galvanic Isolator

Quote:
Originally Posted by eherlihy View Post
Not to ABYC.
Here is your post:

Quote:
Originally Posted by eherlihy View Post
DO NOT confuse the AC Ground (aka neutral or white wire) with the GroundING (aka green wire).

The Ground should go to whatever AC load that you are connecting the AC to. The GroundING wire should connect to your vessel's bonding circuit. And, if your smart, you should have some form of galvanic isolation device for the vessel.
Difference: You called it AC Ground, ABYC calls it the AC Grounded Conductor

Your omission of "ed" changed the description of the conductor significantly.
DotDun is offline  
post #15 of 18 Old 03-15-2017
Senior Member
 
misfits's Avatar
 
Join Date: Dec 2011
Location: NH
Posts: 659
Thanks: 2
Thanked 11 Times in 11 Posts
Rep Power: 8
 
Re: Galvanic Isolator

Quote:
Originally Posted by DotDun View Post
Can you explain what circumstances that might happen?
One thing I know for certain, electricity doesn't care what color the wire is....

On my boat the "shore" inlet is within 10' of the panel so the additional main breaker is not required.
If there ever was a short to ground (green wire) within this 10' & I landed the ground to the DC negative buss as some illustrations show, would that not put line voltage to the DC - buss?
Keep in mind my DC system is free floating, not grounded to anything but the negative terminal on the battery.

Maybe I'm overthinking this but I do not want to create a condition that could hurt anyone. Sounds like I need to have this discussion with a knowledgeable marine electrician.

Thanks,
Bob

I'm not happy unless I'm complaining about something.
I'm having a very good day!
misfits is offline  
post #16 of 18 Old 03-15-2017
Senior Member
 
mitiempo's Avatar
 
Join Date: Sep 2008
Location: Victoria B.C. Canada
Posts: 7,853
Thanks: 0
Thanked 113 Times in 104 Posts
Rep Power: 13
   
Re: Galvanic Isolator

Quote:
Originally Posted by misfits View Post
Seeing how I'm in the process of re-wiring the whole boat I've been wondering where to terminate the AC ground. The old AC ground landed at the ICE which was connected to the thru hull bonding system & lightening bonded system, both of which terminate at a single keel bolt. I no longer have an ICE, but an electric drive.

My DC system is free floating, not grounded to anything but the - terminal on the battery.
Question on the table, where do I land the AC ground?
Is your drive shaft electrically connected to the motor from DC negative?

An AC short is most likely to come from a dual voltage device - charger or inverter. Without the alternative path to earth the AC/DC connection provides in such a case the DC system would likely become AC hot.

Brian
Living aboard in Victoria Harbour
mitiempo is online now  
post #17 of 18 Old 03-15-2017
Member
 
Join Date: Dec 2003
Posts: 51
Thanks: 0
Thanked 2 Times in 2 Posts
Rep Power: 16
 
Re: Galvanic Isolator

Quote:
Originally Posted by misfits View Post
One thing I know for certain, electricity doesn't care what color the wire is....

On my boat the "shore" inlet is within 10' of the panel so the additional main breaker is not required.
If there ever was a short to ground (green wire) within this 10' & I landed the ground to the DC negative buss as some illustrations show, would that not put line voltage to the DC - buss?
Keep in mind my DC system is free floating, not grounded to anything but the negative terminal on the battery.

Maybe I'm overthinking this but I do not want to create a condition that could hurt anyone. Sounds like I need to have this discussion with a knowledgeable marine electrician.

Thanks,
Bob
Power from a source is looking for a return path back to the source.

A short from hot to ground in the 10' inside your boat would trip the breaker in the shorepower pedestal.
DotDun is offline  
post #18 of 18 Old 03-16-2017
Senior Member
 
misfits's Avatar
 
Join Date: Dec 2011
Location: NH
Posts: 659
Thanks: 2
Thanked 11 Times in 11 Posts
Rep Power: 8
 
Re: Galvanic Isolator

Quote:
Originally Posted by mitiempo View Post
Is your drive shaft electrically connected to the motor from DC negative?

An AC short is most likely to come from a dual voltage device - charger or inverter. Without the alternative path to earth the AC/DC connection provides in such a case the DC system would likely become AC hot.
The prop shaft is isolated from the motor. From what I've read this is typical for EP installations so the seawater doesn't become an electrolyte & suck the life out of your batteries or do other not so good things with underwater metals on your boat. That's why the DC buss is free floating. The zinc on the prop shaft only protects the wheel because of dissimilar metal issues.

I have no intent of renting a slip so marina "shore" power is off the table. If solar can't provide enough juice to keep the battery bank full I'll power the boat/charger(s) with a small Honda generator if needed.

That's all I know.

Bob

I'm not happy unless I'm complaining about something.
I'm having a very good day!
misfits is offline  
Reply

Quick Reply
Message:
Options

By choosing to post the reply above you agree to the rules you agreed to when joining Sailnet.
Click Here to view those rules.

Register Now



In order to be able to post messages on the SailNet Community forums, you must first register.
Please enter your desired user name, your email address and other required details in the form below.
Please note: After entering 3 characters a list of Usernames already in use will appear and the list will disappear once a valid Username is entered.


User Name:
Password
Please enter a password for your user account. Note that passwords are case-sensitive.

Password:


Confirm Password:
Email Address
Please enter a valid email address for yourself.

Email Address:
OR

Log-in











Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Show Printable Version Show Printable Version
Email this Page Email this Page



Similar Threads
Thread Thread Starter Forum Replies Last Post
Galvanic Isolator wmjr Pacific Seacraft 13 01-16-2014 11:12 AM
How to make your own Galvanic Isolator for under $20 yandina Gear & Maintenance 14 12-13-2012 11:14 AM
Wiring a galvanic isolator Minnewaska Gear & Maintenance 6 05-22-2011 05:25 AM
Galvanic Isolator Question Allanbc Electrical Systems 9 03-16-2011 06:51 AM
Galvanic isolator Minnewaska Gear & Maintenance 1 09-14-2010 11:57 AM

Posting Rules  
You may post new threads
You may post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On
Trackbacks are On
Pingbacks are On
Refbacks are On

 
For the best viewing experience please update your browser to Google Chrome