Fried Shore Power

Dearest Sailheads,

My shore power deck connection is fried. See pic.

Can anyone tell me how this could have happened? Shouldn't the dockside or onboard circuit breaker have tripped before the connection melted down?

It's 30 amp and 125 v and has been plugged into shore power for about half of the 5 years it's been installed.

Thanks in advance!

Ed
Attached Thumbnails
IMG_8109.jpeg  
Ed Kinney is offline  
Sponsored Links
Advertisement
 
post #2 of 10 Old 02-06-2019
Senior Member
 
misfits's Avatar
 
Join Date: Dec 2011
Location: NH
Posts: 659
Thanks: 2
Thanked 11 Times in 11 Posts
Rep Power: 8
 
Re: Fried Shore Power

Lucky you didn't lose the boat or worse!
ottos likes this.
misfits is offline  
post #3 of 10 Old 02-06-2019
Senior Member
 
SchockT's Avatar
 
Join Date: May 2012
Location: North Vancouver, BC
Posts: 1,815
Thanks: 1
Thanked 39 Times in 36 Posts
Rep Power: 8
 
Re: Fried Shore Power

That kind of overheating is usually caused by loose or corroded connections, corroded plug prongs etc. If you look at your shore power cord you will probably see signs of overheating where the prongs enter the plastic plug.

The breaker isnt necessarily going to trip unless the amp draw exceeds the rating of the breaker, or the wire shorts to ground. Overheating can happen without drawing excessive current.

Sent from my SM-G960W using Tapatalk

2011 Jeanneau 39i Azura
SchockT is online now  
 
post #4 of 10 Old 02-06-2019
Senior Member
 
SanderO's Avatar
 
Join Date: Jul 2007
Location: Northport, NY
Posts: 2,968
Thanks: 2
Thanked 79 Times in 79 Posts
Rep Power: 0
 
Re: Fried Shore Power

It's a good idea to clean your prongs with a wire bruish, and spray socket and plug with something like DeOxit which lubricates and protects electrical connections.

pay attention... someone's life depends on it
SanderO is online now  
post #5 of 10 Old 02-06-2019
Senior Member
 
Join Date: Oct 2011
Location: Nanaimo B.C.
Posts: 4,427
Thanks: 5
Thanked 135 Times in 134 Posts
Rep Power: 8
 
Re: Fried Shore Power

Consider yourself lucky, Probably bunged the end of the cord too. Happens frequently. Replace both units with the best most expensive new fangeled gizmos available. Dang the expense, there's a lot at stake. Somebody will clue you as to brand name.
Capt Len is online now  
post #6 of 10 Old 02-06-2019
Senior Member
 
Bleemus's Avatar
 
Join Date: Oct 2015
Location: Fl
Posts: 1,368
Thanks: 29
Thanked 51 Times in 51 Posts
Rep Power: 4
 
Re: Fried Shore Power

Your shore power plug is based on ancient, but accepted, technology. They fail often and are a leading cause of boat fires. You are lucky your whole boat didn't burn. Switching to a Smartplug would fix it.

Keth

Boat Vinyl Lettering and Graphics
Bleemus is offline  
The Following User Says Thank You to Bleemus For This Useful Post:
Maine Sail (02-07-2019)
post #7 of 10 Old 02-07-2019
Senior Member
 
Join Date: Dec 2018
Posts: 215
Thanks: 4
Thanked 9 Times in 9 Posts
Rep Power: 0
 
Re: Fried Shore Power

Quote:
Originally Posted by Ed Kinney View Post
Dearest Sailheads,

My shore power deck connection is fried. See pic.

Can anyone tell me how this could have happened? Shouldn't the dockside or onboard circuit breaker have tripped before the connection melted down?

It's 30 amp and 125 v and has been plugged into shore power for about half of the 5 years it's been installed.

Thanks in advance!

Ed

How it could have happened? One of the conductors (prolly the ungrounded by the look of it) developed an "intermittent" connection, which then began to arc and create carbon, which continued to increase the "closed" circuit connection impedance. Eventually, the impedance and resultant voltage drop became high enough that for the load current, sufficient electrical energy was converted to heat, to melt and burn the plastic.

Why the breaker didn't trip? The total circuit impedance was low enough that the current through the high impedance connection, was lower than the breaker rating. In your case, the breaker would not trip if 30 A was sustained forever. However, if 50 Vac was dropped at the high impedance shore power connection, that's 1500 W, certainly way more than enough to melt plastic. Under normal circumstances the voltage drop across a shore power connection should be less than 1 Vac.

It is wise to check cords and connectors after every use for signs of discolouration. At first sign, investigate, as just a slight discolouration may be due to actual burning on the other side.

Also investigate any case of low AC Panel voltage reading. If it is normally 120 Vac, and today it is 108 Vac, ensure it is not because of a bad connection.

Shore power connectors have an ALF (Average Life Expectancy) of about 15 years, and cords about 5.

Last edited by boatsurgeon; 02-07-2019 at 01:48 AM.
boatsurgeon is offline  
post #8 of 10 Old 02-07-2019
Sailor
 
Join Date: Jul 2014
Posts: 228
Thanks: 0
Thanked 8 Times in 8 Posts
Rep Power: 5
 
Re: Fried Shore Power

The wire that shorted out(black) is very green with corrosion i would bet the receptacle either leaked between the hull or it is in a high condensation area. Was this marine grade tinned wire?
ottos likes this.
Jim_W is online now  
post #9 of 10 Old 02-07-2019
Seņor Member
 
ottos's Avatar
 
Join Date: Aug 2008
Location: OC NJ
Posts: 557
Thanks: 6
Thanked 11 Times in 11 Posts
Rep Power: 11
 
Re: Fried Shore Power

See Maine Sail's write up on shore power connections here.

Then if you aren't subject to nightmares look for his "Hall of Fail" article on the same site.
RegisteredUser likes this.
ottos is online now  
post #10 of 10 Old 02-09-2019 Thread Starter
Avast, ye scurvy dogs!
 
Join Date: Sep 2016
Posts: 28
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 0
 
Re: Fried Shore Power

Great stuff, folks. I really appreciate it. I'll add one more item to the "Inspect Regularly" list.

Thanks!

Ed
Ed Kinney is offline  
Reply

Quick Reply
Message:
Options

By choosing to post the reply above you agree to the rules you agreed to when joining Sailnet.
Click Here to view those rules.

Register Now



In order to be able to post messages on the SailNet Community forums, you must first register.
Please enter your desired user name, your email address and other required details in the form below.
Please note: After entering 3 characters a list of Usernames already in use will appear and the list will disappear once a valid Username is entered.


User Name:
Password
Please enter a password for your user account. Note that passwords are case-sensitive.

Password:


Confirm Password:
Email Address
Please enter a valid email address for yourself.

Email Address:
OR

Log-in











Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Show Printable Version Show Printable Version
Email this Page Email this Page



Similar Threads
Thread Thread Starter Forum Replies Last Post
Solar power instead of shore power Ajax_MD Chesapeake Bay 50 07-10-2017 11:47 PM
Shore power - Reverse Polarity and no power at GFCI outlets tatracy Electrical Systems 17 05-20-2014 10:58 PM
Hooking 110 power cord to shore power? dvuyxx Electrical Systems 16 06-02-2012 09:35 AM
shore power with out shore power marcusn Gear & Maintenance 33 06-20-2008 03:55 PM
Fried out Voltage Regulator scurvy Gear & Maintenance 28 09-23-2007 07:53 PM

Posting Rules  
You may post new threads
You may post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On
Trackbacks are On
Pingbacks are On
Refbacks are On

 
For the best viewing experience please update your browser to Google Chrome