Hydronic Heater Install

Hello all -

I am about 75% complete on my ESPAR hydronic system installation in my (new to me) Catalina 310. We cruise here in the PNW, and being cold can really be a drag. Plus, it keeps the Admiral happy and willing to go with me.

I will be into this project for less than $2,000 (pro's want something like $6,000), and countless crawls into the port stern cavity. Believe me, I understand the labor cost factor at this point, but I really enjoy projects like this. I also am a tool guy - think "Tim Taylor" without [most of] the grunts - and this turned out to be a GREAT way to familiarize myself with the boat's innards.

I have a couple questions for the forum:

1) The Raymarine fluxgate compass is going to be within 12-18" of the stern fan heater (the fan will be furthest away), and the spiral vent hose to the cabin will go right over the top of it. The vent hose is like mylar with a stainless steel spiral wires (4" diameter). The manual for the compass says stay away from LARGE metal objects and wiring.

Any major concerns or recommendations from you knowledgeable folks out there? Moving it is nearly impossible, but I will listen to knowledgeable advice.

2) I have been taking lots of digital pictures and keeping good records of the install process. I have also recorded good sources for the bits and pieces at the best prices I could find. Is there any interest in me posting this information here?

If so...

3) What would be the best way? Serial posts? Other?

Thanks for your help.
jonfreeman is offline  
Sponsored Links
Advertisement
 
post #2 of 18 Old 03-19-2009
Super Moderator
 
Maine Sail's Avatar
 
Join Date: Jan 2003
Location: Maine Coast
Posts: 6,665
Thanks: 31
Thanked 356 Times in 276 Posts
Rep Power: 10
       
Quote:
Originally Posted by jonfreeman View Post
1) The Raymarine fluxgate compass is going to be within 12-18" of the stern fan heater (the fan will be furthest away), and the spiral vent hose to the cabin will go right over the top of it. The vent hose is like mylar with a stainless steel spiral wires (4" diameter). The manual for the compass says stay away from LARGE metal objects and wiring.

Any major concerns or recommendations from you knowledgeable folks out there? Moving it is nearly impossible, but I will listen to knowledgeable advice.
.
I owned a 310 and installed the flux gate under the sink and as close to the center line as possible (behind the waste basket). You want one as low and as close to the center of the boat as possible. Use a boy scout compass to make sure you get no interference.

Personally I would not install it in the stern...

______
-Maine Sail / CS-36T


To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.




Images In Posts Property of Compass Marine Inc.


Maine Sail is offline  
post #3 of 18 Old 03-19-2009
Bender of Nails
 
Join Date: Jan 2009
Location: West Coast BC
Posts: 66
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 11
 
Like MaineSail said, I'm sorta questioning the compass' location myself.

That said, I've installed a bunch of both the Airtronic and Hydronic Espars. They are a great little heater, that's for sure - a hydronic would be my first choice as well.

A couple quick suggestions...first, they don't like to share a fuel pickup. It doesn't take much draw to starve them.
Second, too many false starts in a row and the computer will lock the unit. An airlock in the coolant circuit will do that too. The bleeder is a slotted screw on top of the unit (it isn't marked and I can't read German, lol)
Third, allow for a ridiculous amount of combustion airflow - it's used to cool the unit as well as burn the fuel.
The unit will stink at first at might even give a little smoke inside the compartment. It's a pretty distinctive smell - it's the lagging (fibrous insulation) you wrapped around the exhaust. It's normal and it'll go away after a bit.

Finally, the pump needs to be near the unit so prime it to within a few inches of the pump. A valve at the tank will make your life a little easier here - you can close it after you've primed the line. The pump is a solenoid driving a diaphragm, so using it to prime by feeding it 12V constant will burn it out. If you make up a pigtail with spade connectors on the pump end and leave the end of the power wire bare, barely touching it to a 12V source will give you an intermittent connection that works like a charm. Wow, that was tougher to explain than to actually do it...

Oh, and the condensate drain coming off the exhaust elbow will get VERY hot in use - be sure it's in free air. I still have the scar on my elbow...

I can't think of anything else at this point that might make your installation go easier but if you have any questions, fire away.

"Verbosity leads to unclear inarticulate things"
~Dan Quayle
Deadeye is offline  
 
post #4 of 18 Old 03-20-2009 Thread Starter
Junior Member
 
Join Date: Dec 2006
Location: Washington State
Posts: 16
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 0
 
The compass was installed there by the PO (or the Broker, can't tell). I will investigate moving it, as you guys suggest. If I'm lucky (usually am), the wire will have lots of excess still...

I figured the boiler unit might stink for awhile. Having one of the fan heaters in the same cavity with the boiler is going to be interesting. I think I will buy the back end fitting for the fan, and pull outside air using the vent system, via a "Y" tube. Otherwise, the fan will pull the smell into the cabin.
jonfreeman is offline  
post #5 of 18 Old 03-20-2009 Thread Starter
Junior Member
 
Join Date: Dec 2006
Location: Washington State
Posts: 16
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 0
 
OOPS - BTW - Thanks Deadeye MUCH for the other hints. These were things I hadn't thought about.
jonfreeman is offline  
post #6 of 18 Old 03-20-2009
Junior Member
 
Join Date: Feb 2009
Posts: 2
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 0
 
Espar Hydronic: My worst buy for a boat. I purchased from Ocean Options. When I started having problems they told me that Maint. on such a unit would run about $1000.00 a year! The computer will shut down after too many failed starts and can't be restarted without an additional computer. Good Luck.
aluminun is offline  
post #7 of 18 Old 03-20-2009
██▓▓▒▒░░▒▒▓▓██
 
Join Date: Apr 2006
Posts: 13,645
Thanks: 11
Thanked 253 Times in 248 Posts
Rep Power: 15
   
jon, if you don' t move the fluxgate...Fire it all up, have someone watch the compass while you move the ducting over the fluxgate. If the compass reading changes--which I suspect it will--then the simplest solution is probably to cut out 2-3 feet of the ducting where it runs over the fluxgate, and splice in a piece of non-magnetic ducting instead.

You can get clothes dryer duct made from 'waffled' aluminum with no metal wires. Or all plastic, or even a piece of thinwall PVC plumbing pipe will do just fine. Whatever is on hand at your hardware store and fits the location, this is not a critical material as long as it won't collapse or burn.

You can also take a plain hand-compass to the hardware store (and use it for the ducting you have on the boat) and if the needle swings when you hold it next to the duct's wire...no good, the fluxgate will be affected too.
hellosailor is offline  
post #8 of 18 Old 03-20-2009
Senior Member
 
Join Date: May 2004
Location: Long Is.
Posts: 329
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 16
 
And watch out for that fan motor. I had very erratic behaviour from my autopilot until I figured out that things went screwy when a fresh water pump on the other side of a bulkhead came on. Moved the fluxgate and things settled down. A fan motor is very different from a water pump, but check it out anyway.
gc1111 is offline  
post #9 of 18 Old 03-23-2009 Thread Starter
Junior Member
 
Join Date: Dec 2006
Location: Washington State
Posts: 16
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 0
 
Well - I am a HAPPY camper. Finished the Espar installation over the weekend after a couple long and satisfying days. Fired it up yesterday. Had to bleed it several times, and restart a few times, but after about an hour, it started and stayed on. DEADEYE - smoke and smell counsel was dead on. Stunk for a bit, and then... heat, GLORIOUS HEAT!. And quickly too. I'd say within 5 minutes the cabin was heating very nicely. We (Admiral and I) ran it for about an hour, while I checked for leaks, and generally was full of myself. My wife was actually impressed. All in all, a big win.

As in all projects, I made several quick trips to West Marine and the hardware store, as I neared completion. The final frustration on the final task (cutting the diesel pickup tube) was having the hacksaw blade break. Admiral to the rescue! Called her up (pretty frustrated, I was), and she went to True Value, and purchased one package of every kind blade they carried (She is SO good). Anyway, all is well, and I have plenty of pictures and data to share, if anyone needs it. Regards!
jonfreeman is offline  
post #10 of 18 Old 03-23-2009
Bender of Nails
 
Join Date: Jan 2009
Location: West Coast BC
Posts: 66
Thanks: 0
Thanked 0 Times in 0 Posts
Rep Power: 11
 
Glad it went so well. They are a pretty efficient unit. One thing concerns me a bit though...in the event of an exhaust leak at the burner, will exhaust (and CO) be drawn into the cabin by the bus heater ? I think CO poisoning is cumulative. Either way, now that you're heating the cabin through combustion, a 12V CO monitor might be a good investment.

To answer your original question, I think a thread would be useful. I'll see if I can dig up some of my install photos as well.

Sorry you had crappy luck aluminun. Good point though - if it doesn't start, find out why before restarting it. I'm not sure how one could spend a thou a year to keep one running, but that's JMHO.

"Verbosity leads to unclear inarticulate things"
~Dan Quayle
Deadeye is offline  
Reply

Quick Reply
Message:
Options

By choosing to post the reply above you agree to the rules you agreed to when joining Sailnet.
Click Here to view those rules.

Register Now



In order to be able to post messages on the SailNet Community forums, you must first register.
Please enter your desired user name, your email address and other required details in the form below.
Please note: After entering 3 characters a list of Usernames already in use will appear and the list will disappear once a valid Username is entered.


User Name:
Password
Please enter a password for your user account. Note that passwords are case-sensitive.

Password:


Confirm Password:
Email Address
Please enter a valid email address for yourself.

Email Address:
OR

Log-in











Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Show Printable Version Show Printable Version
Email this Page Email this Page



Similar Threads
Thread Thread Starter Forum Replies Last Post
Boat hydronic heater PROHEAT - XL- 900 edwmama General Discussion (sailing related) 0 12-01-2012 02:35 AM
DIY hydronic heat? miatapaul Gear & Maintenance 1 09-03-2012 02:46 AM
How long can you idle a diesel for the hydronic heat? chrisncate General Discussion (sailing related) 27 12-08-2010 09:13 PM
Hydronic Heating - ProHeat X45?? BELLATRIX1965 Gear & Maintenance 1 09-27-2010 11:03 PM
C400 Batt install and Inv/CHg install Cruisingdad Catalina 1 08-01-2007 01:02 PM

Posting Rules  
You may post new threads
You may post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On
Trackbacks are On
Pingbacks are On
Refbacks are On

 
For the best viewing experience please update your browser to Google Chrome