A new thread to Honda Owners claims that a $15 hard start capacitor will do the same thing as a Dometic SmartStart device.
Is this true? If so, how is it done?
Marc
Because they are essentially the same thing and work the same way. The only significant distinction is the behavior one company displays in setting their price.
 
Understanding the Dometic SmartStart

Hello from Dometic Marine - Makers of Cruisair and Marine Air Systems Brand Air Conditioning and Refrigeration Systems.

We've been monitoring this thread and decided to join the forum to lend some expertise and to help everyone out. We have reviewed the forum rules and regulations regarding commercial interests, and we hope that this post in no way offends or violates anything. All we want is for everyone to have the facts. The new SmartStart is a revolutionary new product that is unlike any other soft starter or hard start add-on in the industry. It is very important to understand how it differs so you can make the right choices for your individual situations.

Important information about the dangers of Portable Gasoline Generators
Before we begin, it is important to clearly state that Dometic does not condone the use of portable gasoline generators for any marine application since both the US Coast Guard and the ABYC strongly caution against it. Portable gasoline generators are not properly marinized and they present life-threatening risks and dangers, including carbon monoxide poisoning and risk of explosion since they are typically not ignition protected. For more information, please refer to the USCG bulletins on this topic available online at http://www.uscgboating.org/assets/pdf/recalls/bscscan68a.pdf and http://www.uscgboating.org/assets/pdf/recalls/BSC74.pdf. Also, please refer to the ABYC document TH-22 (http://www.abycinc.org/th-22.pdf) where they discuss the use of portable generators on boats.

Test Setup and Equipment
In order to provide you with the most accurate information, Dometic obtained a Honda EU2000i generator and a Supco SPP6E Super Boost for side-by-side testing with the new Dometic SmartStart. Both the Honda and Supco products are very good, and by no means was this study conducted in order to put down either one. This study is meant to help everyone better understand how the SmartStart is different and where and why it can solve the problems discussed in this thread where other products cannot.

The current surge caused when an air conditioner compressor starts up is very short in duration, typically 150-300 milliseconds. Hand-held clamp-on current meters typically cannot measure this surge accurately because they typically display an averaged reading about once per second. As a result, the reading obtained with a clamp-on meter is always much lower than what has actually occurred. For our SmartStart development which started over one year ago, we at Dometic developed a custom and very specialized piece of test equipment to accurately capture and measure the start surge accurately. This specialized equipment along with an oscilloscope was to carry out the following study. Below is a photo of the test setup which conducted outdoors so we could run the Honda generator. We used a Cruisair model STQ16-R410A Turbo self-contained 16,000 BTU air conditioner for most of the testing.

Image

Outdoor Test Lab Setup

Technical Differences between the Dometic SmartStart and the Supco SPP6E (Class E Super Boost)
The Supco SPP6E Super Boost device consists of a 88-106MFD start capacitor connected in series with an electronically-controlled, solid-state potential relay. Using voltage sensing, it connects the start capacitor in parallel to the air conditioners run capacitor during the start up. As the voltage across the run capacitor (Run winding to Start winding) increases during the start, the device switches out the start capacitor at a preset level or after a timeout period expires. This sequence partially mimics the behavior of a full hard-start kit (start cap with a mechanical start relay) but not exactly. A true potential start relay has its coil connected across the compressor Common and the Start winding. The voltage behavior between these two compressor terminals is a little more predicable during a start-up. As a result, a true start relay can accomplish a more reliable disengagement of the start capacitor. Nevertheless, the Supco Super Boost does provide a good portion of the benefit of a true hard-start kit and reduced cost. Based on our measurements (shown below), the Super Boost provided a startup current surge reduction of about 20-25%.

The new Dometic SmartStart is completely different. The SmartStart uses a microprocessor to provide real-time control of the applied voltage and current to the Start winding and Run winding independently. The voltage applied to the start winding is also shifted in phase by an internal start capacitor. The application of voltage is so precise that each half alternation of the applied AC power is individually handled by the microprocessor. Then, using back EMF detection, the SmartStart determines when the motor's rotor actually begins to rotate. The SmartStart then accelerates the rotor until it has achieved full speed. Then, at a very precise moment when the current waveform passes through zero, the SmartStart seamlessly bypasses its internal control devices with relays to connect the Run winding directly with L2 and disconnecting from the Start winding.

The SmartStart's intelligence then even goes beyond this. Using the information it gathers from each start, it actually "learns" from what happened during one startup to determine what to use on its next startup. So, immediately after installing and using it on for the very first time, the SmartStart may take up to 10 startups for it to optimize itself to the absolute lowest possible starting current. After that, it continues to fine tune its startup behavior from start to start, up or down, depending on age of the compressor, environmental conditions, and voltage.

The result of this microprocessor-controlled automation and recursive learning is the absolutely lowest possible startup current required for each individual compressor and SmartStart combination. For all models of the SmartStart, the average start-up current reduction achieved is 65%.

Test Results
Two sets of tests were run: One on utility power and one on generator power. The Honda EU2000i has an "ECO" switch that allows for economy mode operation. This economy mode of course results in the generator running at a lower throttle setting to save fuel. However, there is a trade-off. When ECO mode is turned ON, the generator cannot respond quite as quickly to rapid changes in load current. Under certain test conditions, the compressor start surge on generator power caused the generator's output voltage to drop drastically and to become erratic when the compressor start faltered, and also caused the generator's maximum output current to be clamped. So, in order to accurately quantify what each hardware configuration would do, accurate start current data was captured using utility power. Later in the generator tests, instantaneous voltage fluctuation was also measured. In the end, both current surge and voltage drop do matter since voltage drop can dramatically and sometimes detrimentally affect other equipment that may be operating on the same generator.

Image

Analysis
The Honda EU2000i is quite a potent little device. Regardless of the start component configuration, it was able to start the 16000 BTU system reliably when the ECO mode was turned off. When the ECO mode was turned on, however, the generator had trouble with the standard configuration and with the Supco SPP6E installed. The Supco Super Boost did help, but the resulting voltage drop to around 67V (46%) was problematic in that it did sometimes reset the digital controls. Other equipment running off the same generator would have also been affected.

The SmartStart made a dramatic difference. With the ECO switch turned on, the generator was able to tolerate the 18 amp start surge with only about a 20% drop in voltage. With the ECO switch turned off, the generator didn't even flinch (i.e. no measurable voltage drop).

Summary
As was cited elsewhere in this thread, the Honda EU2000i can support a 16,000 BTU air conditioner without any added hardware. But as our testing showed, this would only work if the ECO mode was turned off. Adding the Supco SPP6E provides a marginal improvement, but for our specific test with the 16000 BTU system, it could not guarantee a reliable start-up if the generator was operating in ECO mode. Beyond this, if other equipment is already loading the generator (e.g. sea water pump), that will further reduce the available amperage for the compressor start-up. Adding the Dometic SmartStart provides a dramatic improvement, provides a reliable start under almost all conditions, and will allow the generator to be run in ECO mode, which will certainly reduce fuel consumption.

Dometic is very happy to contribute to this forum; however, we cannot guarantee that someone will always have the opportunity to monitor it at all times. We will do our best to return to this thread in the coming days to answer any follow-up questions. In the future, others from Dometic may use this user ID to answer other questions on this forum.

Thank you for your continued interest and support.

Thank you.
M. Giovanetti
Director of Technology
Dometic Marine Corporation
 
Hello from Dometic Marine - Makers of Cruisair and Marine Air Systems Brand Air Conditioning and Refrigeration Systems.

We've been monitoring this thread and decided to join the forum to lend some expertise and to help everyone out. We have reviewed the forum rules and regulations regarding commercial interests, and we hope that this post in no way offends or violates anything. All we want is for everyone to have the facts. The new SmartStart is a revolutionary new product that is unlike any other soft starter or hard start add-on in the industry. It is very important to understand how it differs so you can make the right choices for your individual situations.

Important information about the dangers of Portable Gasoline Generators
Before we begin, it is important to clearly state that Dometic does not condone the use of portable gasoline generators for any marine application since both the US Coast Guard and the ABYC strongly caution against it. Portable gasoline generators are not properly marinized and they present life-threatening risks and dangers, including carbon monoxide poisoning and risk of explosion since they are typically not ignition protected. For more information, please refer to the USCG bulletins on this topic available online at http://www.uscgboating.org/assets/pdf/recalls/bscscan68a.pdf and http://www.uscgboating.org/assets/pdf/recalls/BSC74.pdf. Also, please refer to the ABYC document TH-22 (http://www.abycinc.org/th-22.pdf) where they discuss the use of portable generators on boats.

Test Setup and Equipment
In order to provide you with the most accurate information, Dometic obtained a Honda EU2000i generator and a Supco SPP6E Super Boost for side-by-side testing with the new Dometic SmartStart. Both the Honda and Supco products are very good, and by no means was this study conducted in order to put down either one. This study is meant to help everyone better understand how the SmartStart is different and where and why it can solve the problems discussed in this thread where other products cannot.

The current surge caused when an air conditioner compressor starts up is very short in duration, typically 150-300 milliseconds. Hand-held clamp-on current meters typically cannot measure this surge accurately because they typically display an averaged reading about once per second. As a result, the reading obtained with a clamp-on meter is always much lower than what has actually occurred. For our SmartStart development which started over one year ago, we at Dometic developed a custom and very specialized piece of test equipment to accurately capture and measure the start surge accurately. This specialized equipment along with an oscilloscope was to carry out the following study. Below is a photo of the test setup which conducted outdoors so we could run the Honda generator. We used a Cruisair model STQ16-R410A Turbo self-contained 16,000 BTU air conditioner for most of the testing.

Image

Outdoor Test Lab Setup

Technical Differences between the Dometic SmartStart and the Supco SPP6E (Class E Super Boost)
The Supco SPP6E Super Boost device consists of a 88-106MFD start capacitor connected in series with an electronically-controlled, solid-state potential relay. Using voltage sensing, it connects the start capacitor in parallel to the air conditioners run capacitor during the start up. As the voltage across the run capacitor (Run winding to Start winding) increases during the start, the device switches out the start capacitor at a preset level or after a timeout period expires. This sequence partially mimics the behavior of a full hard-start kit (start cap with a mechanical start relay) but not exactly. A true potential start relay has its coil connected across the compressor Common and the Start winding. The voltage behavior between these two compressor terminals is a little more predicable during a start-up. As a result, a true start relay can accomplish a more reliable disengagement of the start capacitor. Nevertheless, the Supco Super Boost does provide a good portion of the benefit of a true hard-start kit and reduced cost. Based on our measurements (shown below), the Super Boost provided a startup current surge reduction of about 20-25%.

The new Dometic SmartStart is completely different. The SmartStart uses a microprocessor to provide real-time control of the applied voltage and current to the Start winding and Run winding independently. The voltage applied to the start winding is also shifted in phase by an internal start capacitor. The application of voltage is so precise that each half alternation of the applied AC power is individually handled by the microprocessor. Then, using back EMF detection, the SmartStart determines when the motor's rotor actually begins to rotate. The SmartStart then accelerates the rotor until it has achieved full speed. Then, at a very precise moment when the current waveform passes through zero, the SmartStart seamlessly bypasses its internal control devices with relays to connect the Run winding directly with L2 and disconnecting from the Start winding.

The SmartStart's intelligence then even goes beyond this. Using the information it gathers from each start, it actually "learns" from what happened during one startup to determine what to use on its next startup. So, immediately after installing and using it on for the very first time, the SmartStart may take up to 10 startups for it to optimize itself to the absolute lowest possible starting current. After that, it continues to fine tune its startup behavior from start to start, up or down, depending on age of the compressor, environmental conditions, and voltage.

The result of this microprocessor-controlled automation and recursive learning is the absolutely lowest possible startup current required for each individual compressor and SmartStart combination. For all models of the SmartStart, the average start-up current reduction achieved is 65%.

Test Results
Two sets of tests were run: One on utility power and one on generator power. The Honda EU2000i has an "ECO" switch that allows for economy mode operation. This economy mode of course results in the generator running at a lower throttle setting to save fuel. However, there is a trade-off. When ECO mode is turned ON, the generator cannot respond quite as quickly to rapid changes in load current. Under certain test conditions, the compressor start surge on generator power caused the generator's output voltage to drop drastically and to become erratic when the compressor start faltered, and also caused the generator's maximum output current to be clamped. So, in order to accurately quantify what each hardware configuration would do, accurate start current data was captured using utility power. Later in the generator tests, instantaneous voltage fluctuation was also measured. In the end, both current surge and voltage drop do matter since voltage drop can dramatically and sometimes detrimentally affect other equipment that may be operating on the same generator.

Image

Analysis
The Honda EU2000i is quite a potent little device. Regardless of the start component configuration, it was able to start the 16000 BTU system reliably when the ECO mode was turned off. When the ECO mode was turned on, however, the generator had trouble with the standard configuration and with the Supco SPP6E installed. The Supco Super Boost did help, but the resulting voltage drop to around 67V (46%) was problematic in that it did sometimes reset the digital controls. Other equipment running off the same generator would have also been affected.

The SmartStart made a dramatic difference. With the ECO switch turned on, the generator was able to tolerate the 18 amp start surge with only about a 20% drop in voltage. With the ECO switch turned off, the generator didn't even flinch (i.e. no measurable voltage drop).

Summary
As was cited elsewhere in this thread, the Honda EU2000i can support a 16,000 BTU air conditioner without any added hardware. But as our testing showed, this would only work if the ECO mode was turned off. Adding the Supco SPP6E provides a marginal improvement, but for our specific test with the 16000 BTU system, it could not guarantee a reliable start-up if the generator was operating in ECO mode. Beyond this, if other equipment is already loading the generator (e.g. sea water pump), that will further reduce the available amperage for the compressor start-up. Adding the Dometic SmartStart provides a dramatic improvement, provides a reliable start under almost all conditions, and will allow the generator to be run in ECO mode, which will certainly reduce fuel consumption.

Dometic is very happy to contribute to this forum; however, we cannot guarantee that someone will always have the opportunity to monitor it at all times. We will do our best to return to this thread in the coming days to answer any follow-up questions. In the future, others from Dometic may use this user ID to answer other questions on this forum.

Thank you for your continued interest and support.

Thank you.
M. Giovanetti
Director of Technology
Dometic Marine Corporation
That was a nice writeup. As long as you do not "push" your products here, I have no problem with you participating.

Brian
 
Thanks for the information Dometic. I'd point out that most users of the small gasoline powered generators are at little risk for explosion, since most use them on deck or on the swim platform, not inside the cabin. The carbon monoxide is a risk, but that is true of all ICE equipment.
 
Giovanetti, it's indeed a nice write-up, and clever product idea. I'm a natural prospect for its use, and will be even more delighted if works on my EU2000i plus your VTD12K I have on my boat. It's supposedely even less power hungry than the STQ series.
 
The Smart-Start is not really new, similar systems have been around for RVs for a while, but it sounds like the dometic unit is a lot more sophisticated.

Having said that I doubt you need one. I've heard of lots of people running 16,000 BTU a/c from the Honda 2000 and I run my 7,000 BTU unit from an EU1000i with no problem - no smartstart and in eco mode

Go for the Honda and get the Smart-Start if you need it (they do work).
 
Anything new with the smartstart? anyone install it yet? My honda EB3000c has a hard time starting my 16,000 unit. It usually takes a few tries. Is it for use only with Dometic air? I know, it's a little cold right now but it gets miserably hot during the summer in se texas.
 
Giovanetti, can the SmartStart be used with AC units from other manufacturers?

Thanks for an informative write-up,
Jim
 
It Works!

After reading lots of info on the SmartStart, but finding no real life consumer results, I was skeptical about spending the money on the device.

We had a Marine Airrr 16k BTU a/c and was not able to get the Honda to run it with eco on or off, so we used a 9,000 btu portable unit while on the hook in 100 degree temps. The Honda would run the portable unit, but only with eco off.

I tried the Supco device on the boat unit and measured a 5 amp reduction in start surge, but that was not enough to get the Honda to start the a/c.

We replaced our boat unit with a Mermaid 16,5000 btu unit and took the plunge purchasing a SmartStart, which I am here to tell you was the best investment I've probably ever made for my boat. The SmartStart reliably starts my a/c every single try with ECO on!! It is amazing!

My dad now has a SmartStart on order to repeat my success.

Here's a blog post on the subject if anyone wants to read.

New Temps in the Air; cabin air that is… « s/v Monomoy's blog
 
dometic smartstart

any new info on the smartstart? havent heard any new information lately. I sent email to dometic to ask if it works with ocean breeze ac's but no reply. anyone know? how could I get wiring schematic?
 
any new info on the smartstart? havent heard any new information lately. I sent email to dometic to ask if it works with ocean breeze ac's but no reply. anyone know? how could I get wiring schematic?
Giovanetti, can the SmartStart be used with AC units from other manufacturers
(Please accept our apologies for not responding until now. We apparently missed the e-mail alert for this thread back in February.)

The SmartStart will work with A/Cs from other manufacturers. There are some exceptions, however, even with some Dometic Marine equipment from before 2000 (older Cruisair and Marine Air Systems units).

First, you must remember to choose the right SmartStart model. There are 3 different ones, depending on the voltage of your compressor and its BTU capacity.

Second, the SmartStart will work with pretty much any rotary or scroll compressor that is a permanent split capacitor motor (i.e. has a run cap).

Third, SmartStarts work with most reciprocating compressors, but there are some older models of these compressors (pre-2000) on which the SmartStart will not work optimally. It has to do with how the compressor motor windings were designed and the target start capacitor for these motors. Many of these older compressors require start capacitors that are much smaller than the run capacitors. Modern compressors require start capacitor values that are closer to and often exceed the size of the run capacitors. SmartStarts were designed to work with the present-day compressors, as best as could be done, given the thousands of compressor models that are out there.

So, whether or not a SmartStart will work on your non-Dometic/Cruisair/Marine Air A/C system will be a function your system's compressor model.

If you have a question, post your system's compressor manufacturer and model # here or send me a private message, and I can research it for you. (Note, the compressor manufacturer and its model # should be visible on a label on the side of the actual compressor, providing that the A/C system manufacturer didn't paint over it; the manufacturer of the entire A/C system and its model # are not required.) Admittedly, there are some wiring modifications that can be done to resolve the start-to-run capacitor size ratio issue that some older reciprocating compressors have. I can advise on those depending on what you have. There are no guarantees that all compressors can be made to work with the SmartStart, however, so please be understanding of that for your particular case.

A basic wiring diagram is available on the second page of the SmartStart's spec sheet, available online at: http://dometic.com/cbcde79f-6594-4d01-b60c-2ab7e153c982.fodoc

Thank you for your continued interest and support.

Thank you.
M. Giovanetti
Director of Technology
Dometic Marine Corporation
 
Thank you for your quick reply. I will pm you or post the compressor model after I go to the boat this weekend. The unit is an Ocean Breeze, model OB16CH. 16,700 BTU, draws 11.25 amps, QU288 thermostat. I believe it is a 2007 model.
 
It does NOT work

Dometic
I have read your report which states that the Cruisair 16000 btu with Smart Start installed, will run on a Honda 2000 generator.
My new Cruisair 16000 btu (split unit) was installed on my 31' sailboat June 2010 and as the salesman/installer also said that if I installed a Smart Start I would be able to run the A/C on a 2000 Honda generator, I did install the Smart Start ($500).
I also then purchased a Honda 2000 ($1100)
I have tried many times but have not been able to start the Cruisair. I have tried with the fan and water pump already running (pump on a different circuit) but to no avail. After reading your glowing report I tried again last week. Still unable to start the Cruisair, but blew the thermostat in the process.
I wasted $ 1,600.-

If I want the Cruisair to operate when at anchor, it appears I must buy another Honda 2000 companion for another $1,100.- and run both generators.
With two Honda's operating I would not have needed the Smart Start.
You need to rewrite your report so other people do not make the same mistake I did.
I am located in Key Largo.
 