We have to 2 pair of 6 volt deep cell batteries that are connected in seriers, creating 12 volts. Their model is Deka Promaster GC15/115 min. Any idea how to figure the total amp hours available ?
Yes, but 60% is pretty conservative. Most books say going down to 50% charge is acceptable. This is what the term "deep cycle" batteries refers to. They are claiming they can withstand a certain number of deep cycles. I don't know exactly how deep is deep but I would assume they mean below 50%.To JARCHER - yes that's the battery.
Ok - so if Im following you guys-
1) it's 430 amp hrs available capacity for the 4 batteries (215 x 2 pair) but not good to run batteries below 60% of the 430.
2) safe to assume at 12.6 volts (on meter/approx) the 4 batteries are charged almost 100%?
3) at 12.2 volts (on meter/approx) I assume I have 60% remaining and have used up my safe max of 172 ah (430x40% usage)...and at that point would need to recharge or risk damage to batteries.
4) to add more nausa - if I bought 2 more 6 volt similiar batteries Id go from 430 ah to 645 ah.... times 40% safe max usage for a total of 258 ah to burn before recharging.
Sound correct?